Add a separate, dedicated, AND CLEARLY LABELED foam FDC feeding ONLY the 
helipad appurtenances.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
[email protected]  \  burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
*Registered in: MN, PA, & TX
**NICET IV - Water-Based Systems Layout

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Colin Carew (Cambridge)
Sent: Thursday, February 09, 2017 4:10 PM
To: [email protected]
Subject: RE: Foam - FDC

Thanks Craig ,

So there  wouldn't be an issue having the fire dept hooking up and injecting 
foam into all  the wet pipe standpipes and other wet zones and the foam zone .  
(we are taking about 10,000 sprinkler heads)



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: February-09-17 5:03 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Foam - FDC

I read through your situation a couple of times and think I understand what 
you've got.

The FDC is on the building where the foam system equipment (concentrate tank, 
water supply, proportioner, etc.) are located which supplies a series of foam 
monitors around the helipad.

We had a fuel depot with an NFPA 11 foam system for the internal floating roof 
tanks.  There is no fixed water supply and the system is manual.  The FD rolls 
up, and pressurizes the system via their apparatus via a local hydrant.  The 
foam tote is good for about 7 minutes of foam, system requires 55 minutes of 
foam.  So once the tote runs out and the foam truck has already arrived, things 
are switched over to the foam truck who connects to the FDCs on the manifold 
and they pump the foam-water mix to the fuel tanks.  This flows through the 
proportioners.  I contacted the foam manufacturer to see if pumping the mixture 
through the proportioners would have any effect on the quality of the foam 
mixture and they said, it was not an issue.  There is a sign posted telling the 
FD at what pressure to run their pump to insure proper function of the system.

So to answer your question,  there are cautions that need to be addressed such 
as the flow and pressure rate if the source was a fire apparatus versus the 
normal water source, the foam concentration and foam types would have to 
naturally be identified which shouldn't be an issue.

Our situation was coordinated with the local FD which I would suggest getting 
on board if this were to be considered an option.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Colin Carew (Cambridge)
Sent: Thursday, February 09, 2017 4:47 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Foam - FDC [EXTERNAL]

I was just asked this question by the fire dept at a project where we designed 
a helipad foam system .

"A question has come up regarding the new helipad at the MRH.  We know there is 
a foam system installed that should provide approx. 10 minutes of foam mixture 
to the helipad upon activation of the system.  If foam is required for a longer 
period of time or if for some reason foam isn't being produced in the discharge 
from the monitors the question was asked would it be possible to supply a 
foam/water solution into the FDC on the building?  I realize this would 
probably not produce very nice foam but I would just like to know if there is 
any reason why a person could not attempt this if they felt it was required?  "


My  first response would be no , based on NFPA 16 2011  6.2.5 alone ,  any one 
else ran into this situation or offer any comments ?

Thanks  !


Colin Carew