Steve,

 

Luckily this is one of the more reasonable AHJ’s. Yes this a 4 story
building  that is type  I-A and V-A  construction. Thank you, always nice to
have one of the big dogs confirm my thoughts.  

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, July 31, 2017 2:26 PM
To: [email protected]
Subject: RE: non combustible/limited combustible space 

 

Rocci:

We see this condition in SoCal a lot and while I can’t speak for your AHJ’s
up there (a pit full of vipers), we treat this condition as non-combustible
down here and just about everyone on the enforcer side agrees.  If I’m
understanding correctly, you have a Type 5A building (please confirm,
impacts my opinion) that I’m assuming is four stories if it’s both rated and
sprinklered per 13.  If not 4 stories then they’re taking sprinklers for
something else like area per floor.   Anyway, the frame is plywood sheathing
over stick framing with lightweight concrete topping.  The underside is
enveloped with two layers of gyp to create a one-hour floor-ceiling
assembly.  Then the ceiling drops – where they occur – are non-combustible.
You thus have one-hour capsules around each guest room and the corridor.
Presuming all that, I agree that sprinkler protection is not required above
the ceiling, so long as all combustibles are encapsulated and the
floor-ceiling envelope is taped/mudded/fire sealed to maintain a one-hour
fire rating.   

 

Steve L.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Monday, July 31, 2017 1:57 PM
To: [email protected]
Subject: non combustible/limited combustible space 

 

We have a hotel we are working on and we have limited space in the corridors
(surprise surprise)  so I am trying to not sprinkle the concealed space in
the corridor. Situation is a concrete deck with min. ½” plywood sheathing
below it  followed by 2x8 wood joists with (2) layers of 5/8” type X gyp.
The ceiling below is 1 5/8” metal joists with 1 layer of 5/8” type X  gyp ,
attached directly to ceiling  joists. ( We have roughly 12” from bottom of
(2) layers of gyp to top of ceiling framing.)  Because the 2x8 are covered
with 2 layers of 5/8” gyp can I consider this space non/limited combustible
per 8.15.1.2.2? (BTW the architect is calling this out as a 1 hour rated
assembly.) 

 

Thank you

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to