Thanks Bob,  that’s the detail!

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Monday, July 31, 2017 2:29 PM
To: [email protected]
Subject: RE: non combustible/limited combustible space 

 

Rocci,

It sounds like your situation looks something like this:



If this is the case then you have a situation similar to 8.15.1.2.5 and
sprinklers should be able to be omitted.

 

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Monday, July 31, 2017 2:57 PM
To: [email protected]
Subject: non combustible/limited combustible space 

 

We have a hotel we are working on and we have limited space in the corridors
(surprise surprise)  so I am trying to not sprinkle the concealed space in
the corridor. Situation is a concrete deck with min. ½” plywood sheathing
below it  followed by 2x8 wood joists with (2) layers of 5/8” type X gyp.
The ceiling below is 1 5/8” metal joists with 1 layer of 5/8” type X  gyp ,
attached directly to ceiling  joists. ( We have roughly 12” from bottom of
(2) layers of gyp to top of ceiling framing.)  Because the 2x8 are covered
with 2 layers of 5/8” gyp can I consider this space non/limited combustible
per 8.15.1.2.2? (BTW the architect is calling this out as a 1 hour rated
assembly.) 

 

Thank you

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org