Absolutely, in this case the answer is no based on 11.2.3.1.4 (4)(d).

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, July 31, 2017 5:02 PM
To: Bob; Sprinklerforum
Subject: Re: non combustible/limited combustible space

 

Don't forget to ask yourself if the design area needs to be increased to 3000 
sqft. 


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)






On Jul 31, 2017 at 6:09 PM, <Bob <mailto:[email protected]> > wrote:

A picture is worth a thousand words.  Thanks sprinklerfourm for allowing 
attachments.  They are a huge help.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, July 31, 2017 3:37 PM
To: [email protected]; [email protected]
Subject: RE: non combustible/limited combustible space 

 

That’s what I pictured when I wrote my ramble.


SL

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Monday, July 31, 2017 2:29 PM
To: [email protected]
Subject: RE: non combustible/limited combustible space 

 

Rocci,

It sounds like your situation looks something like this:



If this is the case then you have a situation similar to 8.15.1.2.5 and 
sprinklers should be able to be omitted.

 

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Rocci Cetani 3
Sent: Monday, July 31, 2017 2:57 PM
To: [email protected]
Subject: non combustible/limited combustible space 

 

We have a hotel we are working on and we have limited space in the corridors 
(surprise surprise)  so I am trying to not sprinkle the concealed space in the 
corridor. Situation is a concrete deck with min. ½” plywood sheathing below it  
followed by 2x8 wood joists with (2) layers of 5/8” type X gyp. The ceiling 
below is 1 5/8” metal joists with 1 layer of 5/8” type X  gyp , attached 
directly to ceiling  joists. ( We have roughly 12” from bottom of (2) layers of 
gyp to top of ceiling framing.)  Because the 2x8 are covered with 2 layers of 
5/8” gyp can I consider this space non/limited combustible per 8.15.1.2.2? (BTW 
the architect is calling this out as a 1 hour rated assembly.) 

 

Thank you

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information 

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

 

_______________________________________________ Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to