If it's a 13D system then:
13D 8.3.8    Sprinklers shall not be required in closets in garages and
exterior closets (regardless of size) located on exterior balconies,
exterior breezeways/corridors, or accessed from outdoors where the closet
does not have doors or unprotected penetrations directly
into the dwelling unit.

Is the building classified as an R-3 occupancy? The '13' reference on the
code analysis page might be a mistake if it is but you can always give the
architect a call to see if that's the case. Otherwise I agree - this layout
looks a little odd for a 13D but it is what it is unless the local
ammendments have anything to add to the situation.




<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Fri, Feb 9, 2018 at 12:15 PM, Paul Cetani <pa...@norcalfire.com> wrote:

> This is pretty cut and dry here in Nor Cal. We have to sprinkler garages
> for most of our homes due to local AHJ requirements. 😊
>
> Even if you sprinkler the garage, still seems like 13D to me.
>
>
>
> *Paul B. Cetani*
>
> *Exec. Vice President*
>
>
>
> Nor Cal Fire, Inc.
>
> *16840 Joleen Way, Bldg A*
>
> *Morgan Hill, CA 95037*
>
> *T 408-776-1580 <(408)%20776-1580>*
>
> *F 408-776-1590 <(408)%20776-1590>*
>
> *pa...@norcalfire.com <pa...@norcalfire.com>*
>
> *www.norcalfire.com <http://www.norcalfire.com/>*
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *John Irwin
> *Sent:* Friday, February 09, 2018 11:08 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Abuse of 13D?
>
>
>
> Ok someone help me make an argument that this is not a 13D installation.
> This is the garage level of a two family home. However, the units are
> stacked on top of each other. Both units share a single lead-in (also
> shared with domestic). 13D 2010 is pretty clear that garages are not
> sprinklered. Code analysis page references NFPA 13 and not 13D. Sprinkler
> “engineered” page calls for 13D and shows no floor control on the garage
> level. (I think at a minimum the storage rooms need sprinklers as the
> garage exception is just for the garage)
>
>
>
> What say you smart people?
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to