If it's a 13D system then: 13D 8.3.8 Sprinklers shall not be required in closets in garages and exterior closets (regardless of size) located on exterior balconies, exterior breezeways/corridors, or accessed from outdoors where the closet does not have doors or unprotected penetrations directly into the dwelling unit.
Is the building classified as an R-3 occupancy? The '13' reference on the code analysis page might be a mistake if it is but you can always give the architect a call to see if that's the case. Otherwise I agree - this layout looks a little odd for a 13D but it is what it is unless the local ammendments have anything to add to the situation. <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon> Virus-free. www.avast.com <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2> On Fri, Feb 9, 2018 at 12:15 PM, Paul Cetani <pa...@norcalfire.com> wrote: > This is pretty cut and dry here in Nor Cal. We have to sprinkler garages > for most of our homes due to local AHJ requirements. 😊 > > Even if you sprinkler the garage, still seems like 13D to me. > > > > *Paul B. Cetani* > > *Exec. Vice President* > > > > Nor Cal Fire, Inc. > > *16840 Joleen Way, Bldg A* > > *Morgan Hill, CA 95037* > > *T 408-776-1580 <(408)%20776-1580>* > > *F 408-776-1590 <(408)%20776-1590>* > > *pa...@norcalfire.com <pa...@norcalfire.com>* > > *www.norcalfire.com <http://www.norcalfire.com/>* > > > > *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] *On Behalf Of *John Irwin > *Sent:* Friday, February 09, 2018 11:08 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* Abuse of 13D? > > > > Ok someone help me make an argument that this is not a 13D installation. > This is the garage level of a two family home. However, the units are > stacked on top of each other. Both units share a single lead-in (also > shared with domestic). 13D 2010 is pretty clear that garages are not > sprinklered. Code analysis page references NFPA 13 and not 13D. Sprinkler > “engineered” page calls for 13D and shows no floor control on the garage > level. (I think at a minimum the storage rooms need sprinklers as the > garage exception is just for the garage) > > > > What say you smart people? > > > > > > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org