I'm not sure the reference to 8.3.8 would apply.
First, John mentioned he was working with the 2010 edition of 13D. That
edition doesn't contain this language.
Second, if John were working with the '16 edition then 8.3.8 would not
apply in my opinion as the "storage areas" are not exterior, and are
only accessed from inside a portion of the dwelling unit.
just my thoughts,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 02/09/2018 11:56 AM, Fire Design wrote:
If it's a 13D system then:
13D 8.3.8 Sprinklers shall not be required in closets in garages
and exterior closets (regardless of size) located on exterior balconies,
exterior breezeways/corridors, or accessed from outdoors where the
closet does not have doors or unprotected penetrations directly
into the dwelling unit.
Is the building classified as an R-3 occupancy? The '13' reference on
the code analysis page might be a mistake if it is but you can always
give the architect a call to see if that's the case. Otherwise I agree
- this layout looks a little odd for a 13D but it is what it is unless
the local ammendments have anything to add to the situation.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free. www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
On Fri, Feb 9, 2018 at 12:15 PM, Paul Cetani <pa...@norcalfire.com
<mailto:pa...@norcalfire.com>> wrote:
This is pretty cut and dry here in Nor Cal. We have to sprinkler
garages for most of our homes due to local AHJ requirements. 😊
Even if you sprinkler the garage, still seems like 13D to me.
*/Paul B. Cetani/*
*Exec. Vice President*
**
Nor Cal Fire, Inc.
*16840 Joleen Way, Bldg A*
*Morgan Hill, CA 95037***
*T 408-776-1580 <tel:%28408%29%20776-1580>*
*F 408-776-1590 <tel:%28408%29%20776-1590>*
_pa...@norcalfire.com <mailto:pa...@norcalfire.com>_
_www.norcalfire.com <http://www.norcalfire.com/>_
*From:* Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org>] *On
Behalf Of *John Irwin
*Sent:* Friday, February 09, 2018 11:08 AM
*To:* sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org>
*Subject:* Abuse of 13D?
Ok someone help me make an argument that this is not a 13D
installation. This is the garage level of a two family home.
However, the units are stacked on top of each other. Both units
share a single lead-in (also shared with domestic). 13D 2010 is
pretty clear that garages are not sprinklered. Code analysis page
references NFPA 13 and not 13D. Sprinkler “engineered” page calls
for 13D and shows no floor control on the garage level. (I think
at a minimum the storage rooms need sprinklers as the garage
exception is just for the garage)
What say you smart people?
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org