Ken, your first point - yes, but on your second point, the closets don't
have to be exterior - I'm referencing the first exemption 'closets in
garages' and not the second 'closets on exterior balconies.' I think the
point is that if you don't have to sprinkler garages then you likewise
wouldn't sprinkler closets in garages since the closet is 'in the garage.'


<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Fri, Feb 9, 2018 at 1:18 PM, Parsley Consulting <
parsleyconsult...@cox.net> wrote:

> I'm not sure the reference to 8.3.8 would apply.
>
> First, John mentioned he was working with the 2010 edition of 13D. That
> edition doesn't contain this language.
>
> Second, if John were working with the '16 edition then 8.3.8 would not
> apply in my opinion as the "storage areas" are not exterior, and are only
> accessed from inside a portion of the dwelling unit.
>
> just my thoughts,
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 <(760)%20745-6181> Visit the website
> <http://www.parsleyconsulting.com/> *
> On 02/09/2018 11:56 AM, Fire Design wrote:
>
> If it's a 13D system then:
> 13D 8.3.8    Sprinklers shall not be required in closets in garages and
> exterior closets (regardless of size) located on exterior balconies,
> exterior breezeways/corridors, or accessed from outdoors where the closet
> does not have doors or unprotected penetrations directly
> into the dwelling unit.
>
> Is the building classified as an R-3 occupancy? The '13' reference on the
> code analysis page might be a mistake if it is but you can always give the
> architect a call to see if that's the case. Otherwise I agree - this layout
> looks a little odd for a 13D but it is what it is unless the local
> ammendments have anything to add to the situation.
>
>
>
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>  Virus-free.
> www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
>
> On Fri, Feb 9, 2018 at 12:15 PM, Paul Cetani <pa...@norcalfire.com> wrote:
>
>> This is pretty cut and dry here in Nor Cal. We have to sprinkler garages
>> for most of our homes due to local AHJ requirements. 😊
>>
>> Even if you sprinkler the garage, still seems like 13D to me.
>>
>>
>>
>> *Paul B. Cetani*
>>
>> *Exec. Vice President*
>>
>>
>>
>> Nor Cal Fire, Inc.
>>
>> *16840 Joleen Way, Bldg A*
>>
>> *Morgan Hill, CA 95037*
>>
>> *T 408-776-1580 <%28408%29%20776-1580>*
>>
>> *F 408-776-1590 <%28408%29%20776-1590>*
>>
>> *pa...@norcalfire.com <pa...@norcalfire.com>*
>>
>> *www.norcalfire.com <http://www.norcalfire.com/>*
>>
>>
>>
>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>> @lists.firesprinkler.org] *On Behalf Of *John Irwin
>> *Sent:* Friday, February 09, 2018 11:08 AM
>> *To:* sprinklerforum@lists.firesprinkler.org
>> *Subject:* Abuse of 13D?
>>
>>
>>
>> Ok someone help me make an argument that this is not a 13D installation.
>> This is the garage level of a two family home. However, the units are
>> stacked on top of each other. Both units share a single lead-in (also
>> shared with domestic). 13D 2010 is pretty clear that garages are not
>> sprinklered. Code analysis page references NFPA 13 and not 13D. Sprinkler
>> “engineered” page calls for 13D and shows no floor control on the garage
>> level. (I think at a minimum the storage rooms need sprinklers as the
>> garage exception is just for the garage)
>>
>>
>>
>> What say you smart people?
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>>
>
>
> _______________________________________________
> Sprinklerforum mailing 
> listSprinklerforum@lists.firesprinkler.orghttp://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to