I’m trying to figure out if I need another isolation valve or if I can save 
about 50’-60’ of piping. 

 

The sprinkler system if feed from a combination standpipe in the stair well 
that runs all 12 floors.

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of AKS-Gmail-IMAP
Sent: Tuesday, May 01, 2018 9:14 AM
To: [email protected]
Subject: Re: Secondary Standpipe on Upper Levels

 

The reason behind these questions is because the situation does not smell right 
and we are trying to envision how this thing works within the building code. 

 

When you enter an egress stairwell you are supposed to be entering a structure 
that basically guarantees a safe path to street level safety out of the next 
doorway. The implications for this extends into how the enclosure for this path 
is isolated from the building structure itself and all MEP systems. That 
stairwell egress path typically commands the highest enclosure protection of 
anything else in the building. How that super protected egress path is 
traversing half the building on the 10th floor of a 12 story high-rise is a 
head scratcher in many ways. 

 

In the very least that passage is functionally part of the lower stairwells. If 
it actually connects to both the lower stairwells, providing an exiting choice 
at the 10th floor, then you have the question as to whether or not one or both 
of the lower standpipes should supply that upper stairwell standpipe. It sounds 
like it is not the same situation as having one of the stairwells being a 
straight shot all the way up to the 12th floor.

 

By the way, what supplies the floor level sprinkler systems?

 

Allan Seidel

St. Louis                               





On May 1, 2018, at 10:09 AM, Jerry Van Kolken <[email protected]> wrote:

 

Correct, it will be a second stair for the upper level until you get to the 
first full floor at level 10. Then your be roughly in the middle of the floor 
and would travel to either end of the building to the full set of stairs down 
to the ground floor. 

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, April 30, 2018 8:25 PM
To: [email protected]
Subject: Re: Secondary Standpipe on Upper Levels

 

So it's an offset stair, correct? In other words, it doesn't just go from an 
upper floor down 3 levels to a lobby, it stays in an exit passageway and you go 
horizontally on the transfer floor to a different stairwell for the rest of the 
trip down to exit discharge, is that right?

 

 

Steve

 

 

-------- Original message --------

From: Jerry Van Kolken <[email protected]> 

Date: 4/30/18 5:39 PM (GMT-08:00) 

To: [email protected] 

Subject: Re: Secondary Standpipe on Upper Levels 

 

The building loses half of the floor on the upper levels, so it’s a second 
stair for the top levels. And the ahj is calling it a required exit

Jerry Van Kolken


On Apr 30, 2018, at 16:01, Steve Leyton <[email protected]> wrote:

Why is there a “partial stairwell”?    Is it classified as required exit stair 
or a convenience stair?    

 

Steve L.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Monday, April 30, 2018 3:04 PM
To: [email protected]
Subject: Secondary Standpipe on Upper Levels 

 

I have a 12 story project with a partial stairwell on the top 3 floors. The AHJ 
is requiring a standpipe at this partial stairwell. My question is to I need to 
run another vertical feed from the pump on the first floor, or can I do a 
horizontal feed off the standpipe in the opposite stairwell on the upper level?

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________