Travis,

Based on the product listing, CPVC is appropriate.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Wednesday, August 08, 2018 9:57 AM
To: [email protected]
Subject: NFPA 13R - Garages - CPVC

 

Good morning forum members.  I would like to get your take on the concept below.

 

We have a building that meets all criteria to be protected per NFPA 13R (2013 
edition).  These buildings have garages and dwelling units on the lower floor 
separated from the dwelling units by a common corridor.  As such, these garages 
are not a separate building, but are accessible by more than one dwelling unit. 
 This requires designing the garages per 7.2 – Areas outside the dwelling unit.

 

Since garages are typically OH1, it is the intent to calculate these spaces 
with a density of 0.15.  The spaces are ≤ 500 sq ft, so 7.2.2.1 allows us to 
limit the number of calculated sprinklers to all in a compartment to a maximum 
of 4.  We are using QR sprinklers in these garages.

 

Now, here is where the wrinkle comes.  Are we permitted to use CPVC above the 
ceiling in these areas?  The ceiling is double layered gyp board.  NFPA 13R 
5.2.2.2 states pipe or tube listed for light hazard shall be permitted where 
the room does not exceed 400 sq ft.  I was always informed that you must 
consider the aggregate area for determining this 400 sq ft.  Some of these 
garages are just over 400 sq ft.  Others are ±300 sq ft.  However, there are 
multiple garages side by side, so the aggregate is well over 400 sq ft.  In 
this section, I would state that CPVC would not be an option above the garages.

 

But, the listing of CPVC has a section for garages.  It states that CPVC is 
permitted provided that:

*       Minimum protection of 3/8” gypsum
*       Listed sprinklers ≤225°F utilized
*       System shall be installed per NFPA 13R
*       CPVC pipe / fittings to be installed per manufacturer’s criteria.

 

I am proposing that the piping be steel due to 5.2.2.2 but the builder is 
wanting CPVC and is stating it is possible by the CPVC listing noted above.  
The issue is that we have floor joists closely spaced and you can’t get steel 
going perpendicular to the floor joists up in the floor joist space.  So, the 
builder will have to build a soffit where we run perpendicular to the floor 
joists.  We can be up in the joist space running parallel.

 

So, CPVC or steel?  What is the forum consensus?

 

MFP_logo_F

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to