What if we just designed everything for flammable liquid storage, that
would be the ticket right?

I'm getting ready to start answering the 'what ifs' with my own which is
"What if the architect put the occupancy information on the cover page and
the building owner actually followed that? Oh you think they may do
something else down the road, well what if you had the power to inspect
buildings for compliance? Sounds like your issue is with the building owner
and architect; I can only go by what they put on the plans."

After typing that out I realize that's way too long to actually use as a
pat comeback...

Ben

On Wed, Aug 8, 2018 at 4:14 PM Ron Greenman <[email protected]> wrote:

> What if evil tribbles steal the doors for their dilithium crystal mine
> slave camps? What if someone parks a nuclear missile submarine in hallway?
> What if the garage is built on a secret gateway to the Forbidden Zone and
> the Keymaster and the Gatekeeper open the doors at the same time? I love
> what ifs.
>
> On Wed, Aug 8, 2018 at 1:05 PM Steve Leyton <[email protected]>
> wrote:
>
>> PS:  I’m assuming that if the corridor is rated that the doors have to be
>> rated and equipped with self-closers.   So we can’t program sprinklers for
>> every eventuality that entails aberrant actions by occupants.
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *MFP
>> Design, LLC
>> *Sent:* Wednesday, August 08, 2018 1:02 PM
>>
>>
>> *To:* [email protected]
>> *Subject:* RE: NFPA 13R - Garages - CPVC
>>
>>
>>
>> *Your description of accessible by more than one dwelling unit is exactly
>> the way I view it.  But, I got shot down by the AHJ.  Their response was:
>> “What if some one propped open a door?”  *
>>
>>
>>
>> [image: MFP_logo_F]
>>
>> Travis Mack, SET
>>
>> MFP Design, LLC
>>
>> 3356 E Vallejo Ct
>>
>> Gilbert, AZ 85298
>>
>> 480-505-9271
>>
>> fax: 866-430-6107
>>
>> email:[email protected]
>>
>>
>>
>> http://www.mfpdesign.com
>> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
>>
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>>
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>>
>> LinkedIn: https://www.linkedin.com/in/travismack
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>>
>>
>>
>> *“**The bitterness of poor quality remains long after the sweetness of
>> low price is forgotten.**”*
>>
>>
>>
>> *From:* Sprinklerforum <[email protected]> *On
>> Behalf Of *Steve Leyton
>> *Sent:* Wednesday, August 8, 2018 1:00 PM
>> *To:* [email protected]
>> *Subject:* RE: NFPA 13R - Garages - CPVC
>>
>>
>>
>> 13.   My point is only to reinforce the intent of the standard(s) and
>> also that the manufacturers will warrant the application.
>>
>>
>>
>> The word that’s in Travis’s way here is “private”.  But from a fire
>> hazard perspective, the garages are still private in scale if I understand
>> correctly.   IMHO, I think the concept of accessible to others besides just
>> those in a single dwelling unit implies a larger communal space where more
>> hazardous loads and uses could occur.  Individual unit garages that have a
>> corridor between them and the unit aren’t going to be measurably more
>> hazardous.   I think it’s the intent of the book and the listing to allow
>> the CPVC.
>>
>>
>>
>> SL
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *Ben Young
>> *Sent:* Wednesday, August 08, 2018 12:49 PM
>> *To:* [email protected]
>> *Subject:* Re: NFPA 13R - Garages - CPVC
>>
>>
>>
>> Just to be clear Steve, was the that proposal for NFPA 13R or for 13 and
>> 13R?
>>
>>
>>
>> On Wed, Aug 8, 2018 at 2:05 PM Steve Leyton <[email protected]>
>> wrote:
>>
>> For the 2019 edition, I proposed and the committee accepted the following
>> 2nd draft comment, creating a new subsection:
>>
>>
>>
>> “*16.3.9.6.2* Where nonmetallic pipe installed in accordance with
>> 16.3.9.6 supplies sprinklers in private garage within a dwelling unit not
>> exceeding 1,000 sq. ft. in area, it shall be permitted to be protected from
>> the garage compartment by not less than the same wall or ceiling sheathing
>> that is required by the applicable building code.”
>>
>>
>>
>> This is NOT the condition Travis described but it does speak to the
>> extent of the listing and the willingness by the manufacturer to warrant
>> the product in OH compartments up to 1,000 sq. ft.   My intent was to
>> clarify that it’s NOT the intent of the standard or the product listing
>> limitations to require steel piping in small parking garages in R2
>> occupancies protected by NFPA 13, which is how it went down.  We are seeing
>> AHJs in the southwest requiring double layers of Type ‘X’ and other fairly
>> extreme measure.  One jurisdiction (City of San Diego) has flat-out
>> mandated steel pipe in the those applications.   Going forward, I hope this
>> expands the application for CPVC to at least homogenize the bill of
>> materials in attached residential projects.
>>
>>
>>
>> Travis – you could probably push through an all-CPVC piping plan by
>> bringing in BlazeMaster or Spears to support your design.
>>
>>
>>
>> SML
>>
>>
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *Fire
>> Design
>> *Sent:* Wednesday, August 08, 2018 10:51 AM
>> *To:* [email protected]; [email protected]
>> *Subject:* Re: NFPA 13R - Garages - CPVC
>>
>>
>>
>> I would agree with CPVC because of the  manufacturer listing. However, if
>> you were using a manufacturer that did not have that verbiage and you were
>> back to your interpretation of 13R I think you are wrong in applying the
>> aggregate for the 400 sq. ft. rule. 13R specifically calls out "rooms" and
>> not 'areas'. I personally think it's completely within the scope of 13R to
>> have a 300 sq. ft. storage room next to a 150 sq. ft. mop closet and be
>> able to use CPVC to feed each room because individually they're less than
>> 400 sq. ft. Now, perhaps in the rare event you have a large run of such
>> rooms next to each other it may be better to have your line out in the
>> corridor or something and poke a head into each room in lieu of running the
>> line directly over the run of OH rooms but that is still just a matter of
>> preference in my opinion. I think the main thing to be concerned about is
>> being able to provide the correct water density since the piping above is
>> not going to be compromised if the sprinkler activates and controls the
>> fire when it should.
>>
>>
>>
>>
>>
>> [image: Image removed by sender.]
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>>
>> Virus-free. www.avast.com
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
>>
>>
>>
>> On Wed, Aug 8, 2018 at 9:05 AM, Bob <[email protected]> wrote:
>>
>> Travis,
>>
>> Based on the product listing, CPVC is appropriate.
>>
>>
>>
>> Thank you,
>>
>>
>>
>> Bob Knight, CET III
>>
>> 208-318-3057
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *MFP
>> Design, LLC
>> *Sent:* Wednesday, August 08, 2018 9:57 AM
>> *To:* [email protected]
>> *Subject:* NFPA 13R - Garages - CPVC
>>
>>
>>
>> Good morning forum members.  I would like to get your take on the concept
>> below.
>>
>>
>>
>> We have a building that meets all criteria to be protected per NFPA 13R
>> (2013 edition).  These buildings have garages and dwelling units on the
>> lower floor separated from the dwelling units by a common corridor.  As
>> such, these garages are not a separate building, but are accessible by more
>> than one dwelling unit.  This requires designing the garages per 7.2 –
>> Areas outside the dwelling unit.
>>
>>
>>
>> Since garages are typically OH1, it is the intent to calculate these
>> spaces with a density of 0.15.  The spaces are ≤ 500 sq ft, so 7.2.2.1
>> allows us to limit the number of calculated sprinklers to all in a
>> compartment to a maximum of 4.  We are using QR sprinklers in these garages.
>>
>>
>>
>> Now, here is where the wrinkle comes.  Are we permitted to use CPVC above
>> the ceiling in these areas?  The ceiling is double layered gyp board.  NFPA
>> 13R 5.2.2.2 states pipe or tube listed for light hazard shall be permitted
>> where the room does not exceed 400 sq ft.  I was always informed that you
>> must consider the aggregate area for determining this 400 sq ft.  Some of
>> these garages are just over 400 sq ft.  Others are ±300 sq ft.  However,
>> there are multiple garages side by side, so the aggregate is well over 400
>> sq ft.  In this section, I would state that CPVC would not be an option
>> above the garages.
>>
>>
>>
>> But, the listing of CPVC has a section for garages.  It states that CPVC
>> is permitted provided that:
>>
>>    - Minimum protection of 3/8” gypsum
>>    - Listed sprinklers ≤225°F utilized
>>    - System shall be installed per NFPA 13R
>>    - CPVC pipe / fittings to be installed per manufacturer’s criteria.
>>
>>
>>
>> I am proposing that the piping be steel due to 5.2.2.2 but the builder is
>> wanting CPVC and is stating it is possible by the CPVC listing noted
>> above.  The issue is that we have floor joists closely spaced and you can’t
>> get steel going perpendicular to the floor joists up in the floor joist
>> space.  So, the builder will have to build a soffit where we run
>> perpendicular to the floor joists.  We can be up in the joist space running
>> parallel.
>>
>>
>>
>> So, CPVC or steel?  What is the forum consensus?
>>
>>
>>
>> [image: MFP_logo_F]
>>
>> Travis Mack, SET
>>
>> MFP Design, LLC
>>
>> 3356 E Vallejo Ct
>>
>> Gilbert, AZ 85298
>>
>> 480-505-9271
>>
>> fax: 866-430-6107
>>
>> email:[email protected]
>>
>>
>>
>> http://www.mfpdesign.com
>> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
>>
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>>
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>>
>> LinkedIn: https://www.linkedin.com/in/travismack
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>>
>>
>>
>> *“**The bitterness of poor quality remains long after the sweetness of
>> low price is forgotten.”*
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> --
>>
>>
>> Benjamin Young
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> --
> Sent from Gmail Mobile
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 

Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to