Just to be clear Steve, was the that proposal for NFPA 13R or for 13 and
13R?

On Wed, Aug 8, 2018 at 2:05 PM Steve Leyton <[email protected]>
wrote:

> For the 2019 edition, I proposed and the committee accepted the following 2
> nd draft comment, creating a new subsection:
>
>
>
> “*16.3.9.6.2* Where nonmetallic pipe installed in accordance with
> 16.3.9.6 supplies sprinklers in private garage within a dwelling unit not
> exceeding 1,000 sq. ft. in area, it shall be permitted to be protected from
> the garage compartment by not less than the same wall or ceiling sheathing
> that is required by the applicable building code.”
>
>
>
> This is NOT the condition Travis described but it does speak to the extent
> of the listing and the willingness by the manufacturer to warrant the
> product in OH compartments up to 1,000 sq. ft.   My intent was to clarify
> that it’s NOT the intent of the standard or the product listing limitations
> to require steel piping in small parking garages in R2 occupancies
> protected by NFPA 13, which is how it went down.  We are seeing AHJs in the
> southwest requiring double layers of Type ‘X’ and other fairly extreme
> measure.  One jurisdiction (City of San Diego) has flat-out mandated steel
> pipe in the those applications.   Going forward, I hope this expands the
> application for CPVC to at least homogenize the bill of materials in
> attached residential projects.
>
>
>
> Travis – you could probably push through an all-CPVC piping plan by
> bringing in BlazeMaster or Spears to support your design.
>
>
>
> SML
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Fire Design
> *Sent:* Wednesday, August 08, 2018 10:51 AM
> *To:* [email protected]; [email protected]
> *Subject:* Re: NFPA 13R - Garages - CPVC
>
>
>
> I would agree with CPVC because of the  manufacturer listing. However, if
> you were using a manufacturer that did not have that verbiage and you were
> back to your interpretation of 13R I think you are wrong in applying the
> aggregate for the 400 sq. ft. rule. 13R specifically calls out "rooms" and
> not 'areas'. I personally think it's completely within the scope of 13R to
> have a 300 sq. ft. storage room next to a 150 sq. ft. mop closet and be
> able to use CPVC to feed each room because individually they're less than
> 400 sq. ft. Now, perhaps in the rare event you have a large run of such
> rooms next to each other it may be better to have your line out in the
> corridor or something and poke a head into each room in lieu of running the
> line directly over the run of OH rooms but that is still just a matter of
> preference in my opinion. I think the main thing to be concerned about is
> being able to provide the correct water density since the piping above is
> not going to be compromised if the sprinkler activates and controls the
> fire when it should.
>
>
>
>
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
>
> Virus-free. www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
>
>
>
> On Wed, Aug 8, 2018 at 9:05 AM, Bob <[email protected]> wrote:
>
> Travis,
>
> Based on the product listing, CPVC is appropriate.
>
>
>
> Thank you,
>
>
>
> Bob Knight, CET III
>
> 208-318-3057
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *MFP
> Design, LLC
> *Sent:* Wednesday, August 08, 2018 9:57 AM
> *To:* [email protected]
> *Subject:* NFPA 13R - Garages - CPVC
>
>
>
> Good morning forum members.  I would like to get your take on the concept
> below.
>
>
>
> We have a building that meets all criteria to be protected per NFPA 13R
> (2013 edition).  These buildings have garages and dwelling units on the
> lower floor separated from the dwelling units by a common corridor.  As
> such, these garages are not a separate building, but are accessible by more
> than one dwelling unit.  This requires designing the garages per 7.2 –
> Areas outside the dwelling unit.
>
>
>
> Since garages are typically OH1, it is the intent to calculate these
> spaces with a density of 0.15.  The spaces are ≤ 500 sq ft, so 7.2.2.1
> allows us to limit the number of calculated sprinklers to all in a
> compartment to a maximum of 4.  We are using QR sprinklers in these garages.
>
>
>
> Now, here is where the wrinkle comes.  Are we permitted to use CPVC above
> the ceiling in these areas?  The ceiling is double layered gyp board.  NFPA
> 13R 5.2.2.2 states pipe or tube listed for light hazard shall be permitted
> where the room does not exceed 400 sq ft.  I was always informed that you
> must consider the aggregate area for determining this 400 sq ft.  Some of
> these garages are just over 400 sq ft.  Others are ±300 sq ft.  However,
> there are multiple garages side by side, so the aggregate is well over 400
> sq ft.  In this section, I would state that CPVC would not be an option
> above the garages.
>
>
>
> But, the listing of CPVC has a section for garages.  It states that CPVC
> is permitted provided that:
>
>    - Minimum protection of 3/8” gypsum
>    - Listed sprinklers ≤225°F utilized
>    - System shall be installed per NFPA 13R
>    - CPVC pipe / fittings to be installed per manufacturer’s criteria.
>
>
>
> I am proposing that the piping be steel due to 5.2.2.2 but the builder is
> wanting CPVC and is stating it is possible by the CPVC listing noted
> above.  The issue is that we have floor joists closely spaced and you can’t
> get steel going perpendicular to the floor joists up in the floor joist
> space.  So, the builder will have to build a soffit where we run
> perpendicular to the floor joists.  We can be up in the joist space running
> parallel.
>
>
>
> So, CPVC or steel?  What is the forum consensus?
>
>
>
> [image: MFP_logo_F]
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.”*
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 

Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to