I agree with you, but I have an AHJ who is allowing a church to store in an 
attic protected by Viking Attic Sprinklers (The occupancy was not part of the 
original plan). Looking for some ammo and was hoping I could find something 
specific in the literature.   
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  

  
  
>   
> On Jun 28, 2019 at 1:46 PM,  <RME-G Travis Mack (mailto:[email protected])> 
>  wrote:
>   
>   
>           
>   
>
>  Based on talks I have had with Globe and Tyco reps on this issue, I think 
> you are in a losing battle.    These are specially listed for attic fire 
> loads.    These are not for any pitched roof that fits the slope requirements.
>
>   
>
>     
>
>   
>   
>
>   (http://www.mfpdesign.com/)
>
>   
>
>  Travis Mack, CFPS, CWBSP, RME-G, SET
>
>   
>
>  MFP Design, LLC
>
>   
>
>  3356 E Vallejo Ct
>
>   
>
>  Gilbert, AZ 85298
>
>   
>
>  480-505-9271
>
>   
>
>  fax: 866-430-6107
>
>   
>
>  [email protected] (mailto:[email protected])
>
>   
>
>  www.mfpdesign.com
>
>   
>
>     
>
>   
>
>  Send large files to us via:     https://www.hightail.com/u/MFPDesign 
> (https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0)
>      
>
>   
>
>  LinkedIn:     https://www.linkedin.com/in/travismack 
> (https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0)
>
>   
>
>   
>
>   
>
> “The bitterness of poor quality remains long after the sweetness of low price 
> is forgotten.”
>
>   
>
>   
>
>   
>   
>
>     
>
>   
>   
>   
>
> From:  Sprinklerforum  <[email protected]>   On 
> Behalf Of  Fpdcdesign
>   Sent:  Friday, June 28, 2019 10:44 AM
>   To:  Sprinklerforum  <[email protected]>
>   Subject:  Re: Attic sprinklers
>
>   
>   
>   
>
>   
>
>   
>   
>
> I have looked in both the Viking and Tyco literature and it just says 
> “attic”. No reference to anything beyond that.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> The dictionary definition of attic makes no reference to what is in the 
> space.   
>
>   
>   
>   
>   
>
>
>  Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (ofc)
>
>   
>   
>   
>
> 860-553-3553 (fax)
>
>   
>   
>   
>
> 860-608-4559 (cell)
>
>   
>   
>   
>   
>   
>   
>
>
>   
>   
>
>
>   
> >   
> >   
> >
> > On Jun 28, 2019 at 1:40 PM,  <Steve Leyton 
> > (mailto:[email protected])>  wrote:
> >
> >   
> >   
> >   
> >
> > Or a Viking rep …
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Sprinklerforum 
> > [mailto:[email protected]]  On Behalf Of  
> > Travis Mack, SET, CFPS, CWBSP, RME-G
> >   Sent:  Friday, June 28, 2019 10:39 AM
> >   To:   [email protected] 
> > (mailto:[email protected])
> >   Subject:  RE: Attic sprinklers
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> >  Yes.    If occupied, I would say it is not an attic any longer.    If 
> > there is no ceiling, it is not a concealed space.    These are specially 
> > listed concealed space sprinklers.    A call to Tyco technical services 
> > would clear it up for you if that is not enough.
> >
> >   
> >
> >     
> >
> >   
> >   
> >
> >   (http://www.mfpdesign.com/)
> >
> >   
> >
> >  Travis Mack, CFPS, CWBSP, RME-G, SET
> >
> >   
> >
> >  MFP Design, LLC
> >
> >   
> >
> >  3356 E Vallejo Ct
> >
> >   
> >
> >  Gilbert, AZ 85298
> >
> >   
> >
> >  480-505-9271
> >
> >   
> >
> >  fax: 866-430-6107
> >
> >   
> >
> >  [email protected] (mailto:[email protected])
> >
> >   
> >
> >   www.mfpdesign.com (http://www.mfpdesign.com)
> >
> >   
> >
> >     
> >
> >   
> >
> >  Send large files to us via:     https://www.hightail.com/u/MFPDesign 
> > (https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0)
> >      
> >
> >   
> >
> >  LinkedIn:     https://www.linkedin.com/in/travismack 
> > (https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0)
> >
> >   
> >
> >   
> >
> >   
> >
> > “The bitterness of poor quality remains long after the sweetness of low 
> > price is forgotten.”
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> >     
> >
> >   
> >   
> >   
> >
> > From:  Sprinklerforum  <[email protected] 
> > (mailto:[email protected])>   On Behalf Of   
> > [email protected] (mailto:[email protected])
> >   Sent:  Friday, June 28, 2019 10:37 AM
> >   To:   [email protected] 
> > (mailto:[email protected])
> >   Subject:  RE: Attic sprinklers
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> > If it’s ‘occupied’, is it still considered an attic?
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> > Cliff Whitfield, SET
> >
> >   
> >
> > President
> >
> >   
> >
> >   
> >
> >   
> >
> > Fire Design, Inc.
> >
> >   
> >
> > 184 Comfort Place
> >
> >   
> >
> > Burnsville, NC 28714
> >
> >   
> >
> > Ph: 828-284-4772
> >
> >   
> >
> >   
> >
> >   
> >
> >
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:  Sprinklerforum  <[email protected] 
> > (mailto:[email protected])>   On Behalf Of  
> > Fpdcdesign
> >   Sent:  Friday, June 28, 2019 1:34 PM
> >   To:  Sprinklerforum  <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  Attic sprinklers
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >
> > Where in NFPA 13 or in their listings are attic sprinklers restricted to 
> > unoccupied attic spaces?   
> >
> >   
> >   
> >   
> >   
> >
> >
> >  Todd G Williams, PE
> >
> >   
> >   
> >
> > Fire Protection Design/Consulting
> >
> >   
> >   
> >   
> >
> > Stonington, CT
> >
> >   
> >   
> >   
> >
> > 860-535-2080 (ofc)
> >
> >   
> >   
> >   
> >
> > 860-553-3553 (fax)
> >
> >   
> >   
> >   
> >
> > 860-608-4559 (cell)
> >
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >
> >
> >
> >   
> >   
> >   
> >
> >  Virus-free.  www.avast.com 
> > (https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link)
> >    
> >
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >
> >  _______________________________________________ Sprinklerforum mailing 
> > list  [email protected] 
> > (mailto:[email protected])    
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> >   
> >   
>   
>   
>   
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to