Yeah but … that’s a red herring regarding the question on the table.   The 
spray pattern and droplet size are different from a conventional sprinkler.  
These are designed to cool the compartments more than wet burning fuel, so 
applying an attic sprinkler to any space with people or stuff in it is outside 
of its listing.   An attic is an attic and as Travis noted, the standard says 
that UNUSED attics are light hazard.   If there’s any doubt about what a word 
means in the standard that isn’t fully defined, we go to Merriam Webster’s 
Collegiate Dictionary, 11th edition which states, “ a room or a space 
immediately below the roof of a building.”    So that’s not a space between 
floors, only the one below the roof (which has pitches and creases and so 
forth, hence the unique design and discharge patterns of attic sprinklers) but 
it has to be unused, otherwise it’s an occupied compartment.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Friday, June 28, 2019 10:52 AM
To: [email protected]
Subject: RE: Attic sprinklers

Better ammo:  Chap 5 – Light Hazard.  Annex says unused attics are light 
hazard.  So, an attic used for storage would not be unused, nor light hazard.

Page 6 of 28 of the tyco data sheet says light hazard.  Seems like the AHJ 
missed the target on this one.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum <[email protected]> On Behalf 
Of Fpdcdesign
Sent: Friday, June 28, 2019 10:49 AM
To: Sprinklerforum <[email protected]>
Subject: Re: Attic sprinklers

I agree with you, but I have an AHJ who is allowing a church to store in an 
attic protected by Viking Attic Sprinklers (The occupancy was not part of the 
original plan). Looking for some ammo and was hoping I could find something 
specific in the literature.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)


On Jun 28, 2019 at 1:46 PM, <RME-G Travis Mack<mailto:[email protected]>> 
wrote:
Based on talks I have had with Globe and Tyco reps on this issue, I think you 
are in a losing battle.  These are specially listed for attic fire loads.  
These are not for any pitched roof that fits the slope requirements.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Fpdcdesign
Sent: Friday, June 28, 2019 10:44 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Re: Attic sprinklers

I have looked in both the Viking and Tyco literature and it just says “attic”. 
No reference to anything beyond that.

The dictionary definition of attic makes no reference to what is in the space.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



On Jun 28, 2019 at 1:40 PM, <Steve Leyton<mailto:[email protected]>> 
wrote:
Or a Viking rep …

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Friday, June 28, 2019 10:39 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Attic sprinklers

Yes.  If occupied, I would say it is not an attic any longer.  If there is no 
ceiling, it is not a concealed space.  These are specially listed concealed 
space sprinklers.  A call to Tyco technical services would clear it up for you 
if that is not enough.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of [email protected]<mailto:[email protected]>
Sent: Friday, June 28, 2019 10:37 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Attic sprinklers

If it’s ‘occupied’, is it still considered an attic?

Cliff Whitfield, SET
President

Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772

[Description: New FDI Logo-4.jpg]

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Fpdcdesign
Sent: Friday, June 28, 2019 1:34 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Attic sprinklers

Where in NFPA 13 or in their listings are attic sprinklers restricted to 
unoccupied attic spaces?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)

[Image removed by 
sender.]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>

_______________________________________________ Sprinklerforum mailing list 
[email protected]<mailto:[email protected]>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list 
[email protected]<mailto:[email protected]>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to