Your ammo is the word, “unused”.  It’s very simple …

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Fpdcdesign
Sent: Friday, June 28, 2019 10:49 AM
To: Sprinklerforum
Subject: Re: Attic sprinklers

I agree with you, but I have an AHJ who is allowing a church to store in an 
attic protected by Viking Attic Sprinklers (The occupancy was not part of the 
original plan). Looking for some ammo and was hoping I could find something 
specific in the literature.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



On Jun 28, 2019 at 1:46 PM, <RME-G Travis Mack<mailto:[email protected]>> 
wrote:
Based on talks I have had with Globe and Tyco reps on this issue, I think you 
are in a losing battle.  These are specially listed for attic fire loads.  
These are not for any pitched roof that fits the slope requirements.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum <[email protected]> On Behalf 
Of Fpdcdesign
Sent: Friday, June 28, 2019 10:44 AM
To: Sprinklerforum <[email protected]>
Subject: Re: Attic sprinklers

I have looked in both the Viking and Tyco literature and it just says “attic”. 
No reference to anything beyond that.

The dictionary definition of attic makes no reference to what is in the space.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)




On Jun 28, 2019 at 1:40 PM, <Steve Leyton<mailto:[email protected]>> 
wrote:
Or a Viking rep …

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Friday, June 28, 2019 10:39 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Attic sprinklers

Yes.  If occupied, I would say it is not an attic any longer.  If there is no 
ceiling, it is not a concealed space.  These are specially listed concealed 
space sprinklers.  A call to Tyco technical services would clear it up for you 
if that is not enough.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of [email protected]<mailto:[email protected]>
Sent: Friday, June 28, 2019 10:37 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Attic sprinklers

If it’s ‘occupied’, is it still considered an attic?

Cliff Whitfield, SET
President

Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772

[Description: New FDI Logo-4.jpg]

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Fpdcdesign
Sent: Friday, June 28, 2019 1:34 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Attic sprinklers

Where in NFPA 13 or in their listings are attic sprinklers restricted to 
unoccupied attic spaces?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)

[Image removed by 
sender.]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>

_______________________________________________ Sprinklerforum mailing list 
[email protected]<mailto:[email protected]>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to