> On Jun 28, 2019, at 10:51 AM, Travis Mack, SET, CFPS, CWBSP, RME-G
> <[email protected]> wrote:
>
> Better ammo: Chap 5 – Light Hazard. Annex says unused attics are light
> hazard. So, an attic used for storage would not be unused, nor light hazard.
>
>
> Page 6 of 28 of the tyco data sheet says light hazard. Seems like the AHJ
> missed the target on this one.
>
> <image002.jpg> <http://www.mfpdesign.com/>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> MFP Design, LLC
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> [email protected] <mailto:[email protected]>
> www.mfpdesign.com <http://www.mfpdesign.com/>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
> “The bitterness of poor quality remains long after the sweetness of low price
> is forgotten.”
>
>
> From: Sprinklerforum <[email protected]
> <mailto:[email protected]>> On Behalf Of
> Fpdcdesign
> Sent: Friday, June 28, 2019 10:49 AM
> To: Sprinklerforum <[email protected]
> <mailto:[email protected]>>
> Subject: Re: Attic sprinklers
>
> I agree with you, but I have an AHJ who is allowing a church to store in an
> attic protected by Viking Attic Sprinklers (The occupancy was not part of the
> original plan). Looking for some ammo and was hoping I could find something
> specific in the literature.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-553-3553 (fax)
> 860-608-4559 (cell)
>
>
>
>> On Jun 28, 2019 at 1:46 PM, <RME-G Travis Mack <mailto:[email protected]>>
>> wrote:
>>
>> Based on talks I have had with Globe and Tyco reps on this issue, I think
>> you are in a losing battle. These are specially listed for attic fire
>> loads. These are not for any pitched roof that fits the slope requirements.
>>
>> <image003.jpg> <http://www.mfpdesign.com/>
>> Travis Mack, CFPS, CWBSP, RME-G, SET
>> MFP Design, LLC
>> 3356 E Vallejo Ct
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> [email protected] <mailto:[email protected]>
>> www.mfpdesign.com <http://www.mfpdesign.com/>
>>
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>> LinkedIn: https://www.linkedin.com/in/travismack
>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>>
>> “The bitterness of poor quality remains long after the sweetness of low
>> price is forgotten.”
>>
>>
>> From: Sprinklerforum <[email protected]
>> <mailto:[email protected]>> On Behalf Of
>> Fpdcdesign
>> Sent: Friday, June 28, 2019 10:44 AM
>> To: Sprinklerforum <[email protected]
>> <mailto:[email protected]>>
>> Subject: Re: Attic sprinklers
>>
>> I have looked in both the Viking and Tyco literature and it just says
>> “attic”. No reference to anything beyond that.
>>
>> The dictionary definition of attic makes no reference to what is in the
>> space.
>>
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860-535-2080 (ofc)
>> 860-553-3553 (fax)
>> 860-608-4559 (cell)
>>
>>
>>
>>
>>> On Jun 28, 2019 at 1:40 PM, <Steve Leyton
>>> <mailto:[email protected]>> wrote:
>>>
>>> Or a Viking rep …
>>>
>>> From: Sprinklerforum [mailto:[email protected]
>>> <mailto:[email protected]>] On Behalf Of
>>> Travis Mack, SET, CFPS, CWBSP, RME-G
>>> Sent: Friday, June 28, 2019 10:39 AM
>>> To: [email protected]
>>> <mailto:[email protected]>
>>> Subject: RE: Attic sprinklers
>>>
>>> Yes. If occupied, I would say it is not an attic any longer. If there is
>>> no ceiling, it is not a concealed space. These are specially listed
>>> concealed space sprinklers. A call to Tyco technical services would clear
>>> it up for you if that is not enough.
>>>
>>> <image007.jpg> <http://www.mfpdesign.com/>
>>> Travis Mack, CFPS, CWBSP, RME-G, SET
>>> MFP Design, LLC
>>> 3356 E Vallejo Ct
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> [email protected] <mailto:[email protected]>
>>> www.mfpdesign.com <http://www.mfpdesign.com/>
>>>
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>>> LinkedIn: https://www.linkedin.com/in/travismack
>>> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>>>
>>> “The bitterness of poor quality remains long after the sweetness of low
>>> price is forgotten.”
>>>
>>>
>>> From: Sprinklerforum <[email protected]
>>> <mailto:[email protected]>> On Behalf Of
>>> [email protected] <mailto:[email protected]>
>>> Sent: Friday, June 28, 2019 10:37 AM
>>> To: [email protected]
>>> <mailto:[email protected]>
>>> Subject: RE: Attic sprinklers
>>>
>>> If it’s ‘occupied’, is it still considered an attic?
>>>
>>> Cliff Whitfield, SET
>>> President
>>>
>>> Fire Design, Inc.
>>> 184 Comfort Place
>>> Burnsville, NC 28714
>>> Ph: 828-284-4772
>>>
>>> <image008.jpg>
>>>
>>> From: Sprinklerforum <[email protected]
>>> <mailto:[email protected]>> On Behalf Of
>>> Fpdcdesign
>>> Sent: Friday, June 28, 2019 1:34 PM
>>> To: Sprinklerforum <[email protected]
>>> <mailto:[email protected]>>
>>> Subject: Attic sprinklers
>>>
>>> Where in NFPA 13 or in their listings are attic sprinklers restricted to
>>> unoccupied attic spaces?
>>>
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> 860-535-2080 (ofc)
>>> 860-553-3553 (fax)
>>> 860-608-4559 (cell)
>>>
>>> <image009.jpg>
>>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
>>>
>>> Virus-free. www.avast.com
>>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
>>>
>>> _______________________________________________ Sprinklerforum mailing list
>>> [email protected]
>>> <mailto:[email protected]>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>> _______________________________________________ Sprinklerforum mailing list
>> [email protected]
>> <mailto:[email protected]>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org