From: [email protected] <[email protected]>
Sent: Wednesday, January 15, 2025 9:56 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
<[email protected]>
Subject: [Sprinklerforum] Re: 13D generator requirements
Neither NFPA 13D nor IRC P2904 requires a pump to meet NFPA 20 requirements or
listing (other than the same electrical UL listing for every electric
appliance). As noted, there could be a local amendment related to care
facilities; however, until we get into NFPA 13R and/or NFPA 13 applications, no
such requirement exists.
[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Bob Caputo, CFPS
President
American Fire Sprinkler Association
c: 760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org<http://firesprinkler.org/>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org/>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png]
<https://twitter.com/afsa/status/1039528345367732224>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
<https://www.instagram.com/firesprinklerorg/>
From: [email protected] <[email protected]>
Sent: Wednesday, January 15, 2025 7:20 AM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]>
Subject: [Sprinklerforum] Re: 13D generator requirements
Todd,
A good question for local Fire Chief and or AHJ.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638
[email protected]<mailto:[email protected]>
________________________________
From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Wednesday, January 15, 2025 7:45 AM
To: Sprinklerforum
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] 13D generator requirements
I am working on a group home, which by all of the Code analysis, requires a
standard 13D system. They propose to install a pump and tank system. Would a
back up power supply be required for this? I have never been asked about it but
can’t find much that addresses it.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054> (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]