Neither NFPA 13D nor IRC P2904 requires a pump to meet NFPA 20 requirements or 
listing (other than the same electrical UL listing for every electric 
appliance). As noted, there could be a local amendment related to care 
facilities; however, until we get into NFPA 13R and/or NFPA 13 applications, no 
such requirement exists.







 [https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]

Bob Caputo, CFPS

President

American Fire Sprinkler Association

c:     760-908-7753

p:

214-349-5965 ext124

w:

firesprinkler.org<http://firesprinkler.org/>

[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org/>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://twitter.com/afsa/status/1039528345367732224>   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>  
 
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 <https://www.instagram.com/firesprinklerorg/>





From: [email protected] <[email protected]>
Sent: Wednesday, January 15, 2025 7:20 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: 13D generator requirements



Todd,



A good question for local Fire Chief and or AHJ.







Regards,

G. Tim Stone



G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services



   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638

             [email protected]<mailto:[email protected]>





________________________________

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Wednesday, January 15, 2025 7:45 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] 13D generator requirements



I am working on a group home, which by all of the Code analysis, requires a 
standard 13D system. They propose to install a pump and tank system. Would a 
back up power supply be required for this? I have never been asked about it but 
can’t find much that addresses it.



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080<tel:860-535-2080> (ofc)

860-554-7054<tel:860-554-7054>  (fax)

860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to