Todd,

I feel your pain. Fire pump test reports have turned into frustration for
me.

A pump fail is when the fire pump is unable to supply the system demand(s).

The report should show the actual performance test results, certified
manufacturer curve, and the adjusted curves one one graph. Most pump
reports I see don't provide this necessary information. If they provided
all 3 curves on the graph, that will answer any questions. Something sounds
wrong with the information provided to you.

A 5% drop is not a fire pump failure. An investigation should be completed
to figure out why the pump test results have degraded. An increase at 150%
is suspect and question their results.

Tom Wellen
Procon Consulting



On Wed, Oct 15, 2025 at 2:51 PM Fpdcdesign <[email protected]> wrote:

> I received and was asked to comment on a test report from a pump that
> failed. The pump is an electric 1000 gpm at 100 psi unit.
>
> One of the curious things on the report is that they are looking for 78%
> of rated pressure at 150% rated flow. NFPA 20 calls for 65%. Before I shoot
> my mouth off, is there any justification for this?
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to