Steve, Yes, the fire pump data plate.
Tom Wellen Procon Consulting On Wed, Oct 15, 2025 at 3:09 PM Steve Leyton <[email protected]> wrote: > Does anyone have the original factory bench test curve (or the OEM spec > from the time of installation) for comparison? > > > > Steve > > > > *From:* Fpdcdesign <[email protected]> > *Sent:* Wednesday, October 15, 2025 12:50 PM > *To:* Sprinklerforum <[email protected]> > *Subject:* [Sprinklerforum] Pump requirement at 150% flow > > > > I received and was asked to comment on a test report from a pump that > failed. The pump is an electric 1000 gpm at 100 psi unit. > > > > One of the curious things on the report is that they are looking for 78% > of rated pressure at 150% rated flow. NFPA 20 calls for 65%. Before I shoot > my mouth off, is there any justification for this? > > > > Todd G Williams, PE > > Fire Protection Design/Consulting > > Stonington, CT > > 860-535-2080 (ofc) > > 860-554-7054 (fax) > > 860-608-4559 (cell) > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected] >