I believe the 65% requirement is a basis for the fire pump to be listed, not 
for field testing.

Performance test results is to be compared to two items:

  *   Downstream system demand
  *   95% of Rated / Acceptance Test Performance (Your 78%); 74.1%.

Look first at the Amperage / RPM and adjust your results accordingly.
Compare to previous tests to see if you identify a trend.



Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Fpdcdesign <[email protected]>
Sent: Wednesday, October 15, 2025 2:50 PM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Pump requirement at 150% flow

I received and was asked to comment on a test report from a pump that failed. 
The pump is an electric 1000 gpm at 100 psi unit. One of the curious things on 
the report is that they are looking for 78% of rated pressure at 150% rated 
flow. NFPA

I received and was asked to comment on a test report from a pump that failed. 
The pump is an electric 1000 gpm at 100 psi unit.

One of the curious things on the report is that they are looking for 78% of 
rated pressure at 150% rated flow. NFPA 20 calls for 65%. Before I shoot my 
mouth off, is there any justification for this?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT