65% of rated pressure at 150% of rated flow is the lowest pressure a pump can 
produce and qualify as a listed fire pump. Manufacturer’s regularly produce 
pumps with a flatter curve than that threshold. 78% is likely the pressure that 
particular pump and impeller produce at 150% flow. Get the factory test curve 
from the manufacturer by providing them with the pump serial number.

Regards,
Mark
Mark. R. Mannex, PE  /  MANNEX ENGINEERING  /  425-331-9129

From: Steve Leyton <[email protected]>
Sent: Wednesday, October 15, 2025 1:09 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Pump requirement at 150% flow

Does anyone have the original factory bench test curve (or the OEM spec from 
the time of installation) for comparison?

Steve

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Wednesday, October 15, 2025 12:50 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Pump requirement at 150% flow

I received and was asked to comment on a test report from a pump that failed. 
The pump is an electric 1000 gpm at 100 psi unit.

One of the curious things on the report is that they are looking for 78% of 
rated pressure at 150% rated flow. NFPA 20 calls for 65%. Before I shoot my 
mouth off, is there any justification for this?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to