The filter is 115/250v  so it could go on the upstream side of the 
control transformer. I'm not understanding the ground part. I thought 
all grounds go to a common point? Drawing tomorrow...

JT

On 12/25/2015 5:05 PM, Bertho Stultiens wrote:
> On 12/25/2015 11:51 PM, John Thornton wrote:
> [snip]
>> So from the distribution blocks the
>> 240v goes to the VFD filter and the control transformer. I have a second
>> filter for the 120v side, should that go just after the control transformer?
> Could you make a (quick and dirty) drawing?
>
> The mains filter should normally be on the primary side, not the
> secondary. A mains filter is to prevent injection back into the grid.
>
> If I understand you correctly, you want to do following:
>
>
> [240V mains]--+--[vfd filter]--[VFD controller]--[spindle]
>                |
>                +--[mains filter]--[ctl transformer]--[control]
>
> The interesting part in now how earth is connected in the "VFD
> controller" and the "control". If the GND of both are connected to earth
> (internally), then you will create a loop and all hell may break loose.
>


------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to