What it boils down to is not the VFD but something in the DC or low 
voltage circuits. I don't have a modbus problem but rather a sserial 
problem.

Thanks

On 1/4/2016 3:00 PM, Rafael wrote:
>    When nothing else works, it's wise to go back to the beginning. After
> so many suggestions, recommendations, and disagreements we have not
> solved this problem since last year.
>
> While grounding could be a major issue, it's not necessarily so in this
> case. As long as there is star wired ground. Besides ground loops don't
> always add up, sometimes they subtract too. Of course, we are not at the
> broken system so troubleshooting is obviously difficult.
>
> On 12/26/2015 07:16 AM, John Thornton wrote:
>> I just checked the ground to housing on the VFD filter, VFD, computer,
>> and the smaller filter and they are all internally connected to ground.
>> The VFD is controlled via modbus so I don't know how to check that cable
>> (which is just a phone cable with a phone jack on one end and a DB9 on
>> the other end to connect to the computers serial port, it's a Automation
>> Direct cable not home made.
>>
>> Is injection to the mains coming back to the machine somehow?
>>
>> JT
> Troubleshooting was mostly focused on ground and wiring so far. Modbus
> is where the (noisy) action is so it's the most obvious place to start
> troubleshooting.
>
> Not being familiar with modbus I decided to do some reading on it.
> https://en.wikipedia.org/wiki/Modbus
> https://en.wikipedia.org/wiki/RS-232
>
> If I understand it correctly, there are 3 physical means to carry
> modbus: RS-232, RS-485, and ethernet. RS stands for Recommended
> Standard, which never became a real standard as far as I'm concerned.
> I've seen RS-232 implementations for mainframe and PC computer
> peripherals and ham radio ranging from ±25V to ±12V and what's most
> common today, ±5V.
>
> RS-232 is relatively immune to noise, for speeds we are dealing with
> here, as long as one side of shielded cable is grounded. We used to have
> cable runs between mainframe computers and terminals in other buildings
> with (to a degree) different ground and no major issues.
>
> After some search, I ended up reading this document, Modbus For Field
> Technicians:
> http://www.modbusbacnet.com/includes/pdf/MODBUS_2010Nov12.pdf
> see pages 29 and numerous pages dedicated to RS-485 issues.
>
> I am assuming that your implementation is based on either RS-232 or
> RS-485. At this point it might be worthwhile to look into VFD "black
> box" to see how exactly it connects to the outside world.
>
> Time to check:
> - (HW) drivers, ICs, transistors, local caps, voltages [1],
> - configuration (parity, etc.),
> - use RS-232 breakbox and check signals quality with scope
> - try different RS-232 port on PC or replace it if necessary.
> - any related jumpers, if any
>
> [1] optical connection protects you from different voltage levels but
> that was not your first try I think so the port on PC side could be
> damaged if the VFD side uses 12V for example. It depends on how old the
> VFD is.
>
> Unknown:
> - was VFD/modbus fully functional before rewiring BP?
> - What says the VFD maintenance manual?
> - Can you run standalone tests on VFD?
>
> How about replacing the DC motors with large resistors and run the
> tests? One by one or all. Are those brushless motors? What's the noise
> around motor wires with a motor or with a resistor?
>


------------------------------------------------------------------------------