I found this on amazon

http://www.amazon.com/UT-211-Port-powered-Mini-size-PhotoElectric-Isolator/dp/B00GI9GS58/ref=sr_1_3?ie=UTF8&qid=1451156759&sr=8-3&keywords=serial+isolator

Not sure how I might isolate the VFD from the chassis at this moment. 
Well I could machine some delrin standoffs... I have a machine shop.

I will need the control transformer to get power for the monitor or just 
plug the monitor into the wall outlet and power the PC with 240v?

JT

On 12/26/2015 12:51 PM, Bertho Stultiens wrote:
> On 12/26/2015 07:36 PM, John Thornton wrote:
>> You misunderstand, all those components are internally grounded I did
>> not ground any of them. I just showed that the shell on each component
>> is bonded to the ground connection on each device.
> Ok, now the real question is whether you can see the difference wrt. to
> my drawing.
>
> The trick is that there should never ever be two or more paths for the
> current to flow, even if it is just an earth connection (or GND for that
> matter).
>
> The isolation barrier I drew is the low-to-high-power separation. It
> should be kept physically separated everywhere until you join the power
> and earth connections at the power supply input.
>
> The real problem I see is the connection of the VFD controller to the
> computer's serial port. Apparently, the computer and the VFD controller
> both have the GND connected internally to earth.
>
> I am pretty sure that the computer's GND is connected to the earth
> (chassis) of the computer (most PCs have).
>
> The VFD controller probably has the same connection, where the modbus
> serial port's GND is connected to the VFD controller's earth (chassis).
>
> If so, then you need to break that loop by electrically isolating the
> serial port.
>


------------------------------------------------------------------------------