Yeah the EVSE's GFCI is required to self-test, so that self test can trip
an upstream GFCI.  Which means every time you try to charge you get a
nuisance trip.

If you must install a GFCI on your 14-50 because of your local AHJ, try to
obtain a 30ma unit not a 6ma.

Best thing to do is hardwire it so the upstream GFCI is not required.

On Fri, Apr 12, 2024 at 10:35 AM Mark Hanson <markehans...@gmail.com> wrote:

> Thanks Phil etc
> Sometimes the code doesn’t explain why there’s certain rules that appear
> arbitrary (like the 12” cord rule).  The larger units are limited to 6’.
> Presumably the GFCI trip current (inside a EVSE) is higher (not sure how
> much) than the 6ma (if using a GFCI panel breaker).  A large chassis like a
> car and with an internal switching supply-charger has EMI X (line to line)
> and Y caps (line to ground for common mode RF) that will most likely leak
> close to 6ma.  Luckily inspector 13 (here) hasn’t enforced the panel GFCI
> breaker requirement (since 2020) on 14/50s used for EV charging.
> Best regards Mark
> Sent from my iPhone
>
> On Apr 12, 2024, at 12:46 PM, (-Phil-) <p...@ingineerix.com> wrote:
>
> 
> Yes, the 12" restriction is because all EVSEs are required to have
> integral GFCI protection, but of course this will do no good for wiring
> "before" the EVSE, so they mandate this cable is as short as possible.
> EVSEs are used in mechanically hostile environments, so it's likely that a
> certain percentage of EVSEs will get mechanical damage to the insulation on
> their cords.   If that cord was before the integral GFCI, there would be no
> protection, in addition, the cable from the EVSE to the car is electrically
> dead until the handshake from the car is completed, so the likelihood of
> getting shocked or electrocuted is much lower.   Not so with the cable from
> the wall to the EVSE itself.
>
> On Fri, Apr 12, 2024 at 8:05 AM Tom Keenan via EV <ev@lists.evdl.org>
> wrote:
>
>> NEC article 625.17 has a mention that the input cord length shall not
>> exceed 12” if the personnel protection system (GFI?) is located in the EVSE
>> enclosure.
>> That appears to be an ‘out’ for needing a GFI breaker?  Just speculation.
>> Tom Keenan
>>
>> > On Apr 12, 2024, at 7:14 AM, Mark Hanson via EV <ev@lists.evdl.org>
>> wrote:
>> >
>> > Hi folks
>> > When reading the 2020 NEC for a master electrician exam, I noticed
>> 210.8(B) says that 50A and below must now have a GFCI breaker at the panel
>> that Tesla etc says will cause nuisance trips (see article). 625.54 in the
>> EV section further states “All receptacles for EV charging shall have GFCI
>> protection.  The article states that hardwired EVSE gets around this
>> requirement since the GFCI is contained but I don’t see that in the code
>> book.  Anyway I have not installed GFCI protection on EVSE circuits and
>> don’t know of electricians here that have since it causes nuisance trips.
>> The code looks like using a 60A breaker is a loophole to get around this
>> requirement as the Tesla EVSE installation manual recommends (and the fact
>> that Teslas can draw up to 48A instead if the typical 30A others use).
>> > Say does anyone know why there’s a 12” cord limit on portable EVSE?
>> That seems silly unless they’re afraid it might lay on the floor in a water
>> puddle.
>> > Best regards Mark
>> > https://www.seahurst.com/nema-14-50/
>> >
>> > Sent from my iPhone
>> > _______________________________________________
>> > Address messages to ev@lists.evdl.org
>> > No other addresses in TO and CC fields
>> > HELP: http://www.evdl.org/help/
>> >
>>
>> _______________________________________________
>> Address messages to ev@lists.evdl.org
>> No other addresses in TO and CC fields
>> HELP: http://www.evdl.org/help/
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20240412/de595de8/attachment.htm>
_______________________________________________
Address messages to ev@lists.evdl.org
No other addresses in TO and CC fields
HELP: http://www.evdl.org/help/

Reply via email to