So, if I have an outbuilding, wired into my main panel in my house,
that outbuilding should not have a ground rod on *its* panel, but I
should instead extend a ground from my house to the outbuilding?

Allan

Fmiser <[EMAIL PROTECTED]> writes:

> It seems than at Mon, 17 Dec 2007 11:56:47 -0600, R wrote:
>
>> Should the generator itself be grounded? I can't help thinking
>> that there should be a connection from the generator frame to
>> a good ground. I have considered driving a ground rod in and
>> either keeping a ground wire on it all of the time or setting
>> up something that would permit a quick ground connection at
>> either end.
>
> Yes.
>
> Or no.
>
> There should be one and only one place were ground and neutral
> are bonded together. This is usually done at the first load
> center (circuit breaker panel). This is also the usual place for
> the wire from the ground rod to also be bonded to the panel
> ground.
>
> If you are connecting a generator through this breaker panel,
> don't add another ground rod.
>
> If, however, you are running extension cords from the generator
> to each of the appliances, then it would be a really good idea
> to bond the generator neutral to generator ground and a ground
> rod.
>
> The reason is that earth is not a very good conductor, thus if there
> is a lightning strike there will be a voltage difference (possibly
> thousands of volts) between the ground rods. And and that difference
> will cause current flow in your wires.
>
>
> --           Philip
>
> _______________________________________
> http://www.okiebenz.com
> For new parts see official list sponsor: http://www.buymbparts.com/
> For used parts email [EMAIL PROTECTED]
>
> To Unsubscribe or change delivery options go to:
> http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
>

-- 