Actually, I stand corrected.  I just pulled out some
of my old NEC manuals, and since a generator is
considered a power source in it's own right, it has to
be grounded separately. (head slap - I knew this, it's
been 10 years since I've done it)

In systems up to 400A 3 phase the neutrals can be
combined.  Above that you may separate the neutrals if
they are isolated between the two systems (power
sources.)


Dan


--- dave walton <[EMAIL PROTECTED]> wrote:

> Lightening is nothing if not unpredictable.
> Would you settle for a frame ground at the remote
> generator site that
> is not connected to neutral?
> 
> -Dave Walton
> 
> On Dec 17, 2007 4:58 PM, LWB250 <[EMAIL PROTECTED]>
> wrote:
> > One ground for one service drop.
> >
> > The NEC and other standards dictate that there be
> one
> > ground point common to a drop.  Multiple grounds
> > create real havoc within the system, not to
> mention
> > the potential (no pun intended) for some serious
> > damage in a fault or lightning situation.
> >
> > Dan (with 20 years in the generator business)
> >
> >
> >
> >
> >
> > --- dave walton <[EMAIL PROTECTED]> wrote:
> >
> > > Would that not "invite" the lightening strike on
> > > your outbuilding to
> > > enter your house rather than be dissipated at
> the
> > > point of impact?
> > > The path of least resistance is your house.
> > > Is that a good thing?
> > >
> > > -Dave Walton
> > >
> > >
> > > On Dec 17, 2007 4:44 PM, Allan Streib
> > > <[EMAIL PROTECTED]> wrote:
> > > > So, if I have an outbuilding, wired into my
> main
> > > panel in my house,
> > > > that outbuilding should not have a ground rod
> on
> > > *its* panel, but I
> > > > should instead extend a ground from my house
> to
> > > the outbuilding?
> > > >
> > > > Allan
> > > >
> > > >
> > > > Fmiser <[EMAIL PROTECTED]> writes:
> > > >
> > > > > It seems than at Mon, 17 Dec 2007 11:56:47
> > > -0600, R wrote:
> > > > >
> > > > >> Should the generator itself be grounded? I
> > > can't help thinking
> > > > >> that there should be a connection from the
> > > generator frame to
> > > > >> a good ground. I have considered driving a
> > > ground rod in and
> > > > >> either keeping a ground wire on it all of
> the
> > > time or setting
> > > > >> up something that would permit a quick
> ground
> > > connection at
> > > > >> either end.
> > > > >
> > > > > Yes.
> > > > >
> > > > > Or no.
> > > > >
> > > > > There should be one and only one place were
> > > ground and neutral
> > > > > are bonded together. This is usually done at
> the
> > > first load
> > > > > center (circuit breaker panel). This is also
> the
> > > usual place for
> > > > > the wire from the ground rod to also be
> bonded
> > > to the panel
> > > > > ground.
> > > > >
> > > > > If you are connecting a generator through
> this
> > > breaker panel,
> > > > > don't add another ground rod.
> > > > >
> > > > > If, however, you are running extension cords
> > > from the generator
> > > > > to each of the appliances, then it would be
> a
> > > really good idea
> > > > > to bond the generator neutral to generator
> > > ground and a ground
> > > > > rod.
> > > > >
> > > > > The reason is that earth is not a very good
> > > conductor, thus if there
> > > > > is a lightning strike there will be a
> voltage
> > > difference (possibly
> > > > > thousands of volts) between the ground rods.
> And
> > > and that difference
> > > > > will cause current flow in your wires.
> > > > >
> > > > >
> > > > > --           Philip
> > > > >
> > > > > _______________________________________
> > > > > http://www.okiebenz.com
> > > > > For new parts see official list sponsor:
> > > http://www.buymbparts.com/
> > > > > For used parts email [EMAIL PROTECTED]
> > > > >
> > > > > To Unsubscribe or change delivery options go
> to:
> > > > >
> > >
> >
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> > > > >
> > > >
> > > > --
> > > > 1983 300D
> > > > 1966 230
> > > >
> > > >
> > > > _______________________________________
> > > > http://www.okiebenz.com
> > > > For new parts see official list sponsor:
> > > http://www.buymbparts.com/
> > > > For used parts email [EMAIL PROTECTED]
> > > >
> > > > To Unsubscribe or change delivery options go
> to:
> > > >
> > >
> >
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> > > >
> > >
> > > _______________________________________
> > > http://www.okiebenz.com
> > > For new parts see official list sponsor:
> > > http://www.buymbparts.com/
> > > For used parts email [EMAIL PROTECTED]
> > >
> > > To Unsubscribe or change delivery options go to:
> > >
> >
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> > >
> >
> >
> >
> >      
>
____________________________________________________________________________________
> > Never miss a thing.  Make Yahoo your home page.
> > http://www.yahoo.com/r/hs
> >
> >
> > _______________________________________
> > http://www.okiebenz.com
> > For new parts see official list sponsor:
> http://www.buymbparts.com/
> > For used parts email [EMAIL PROTECTED]
> >
> > To Unsubscribe or change delivery options go to:
> >
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> >
> 
> _______________________________________
> http://www.okiebenz.com
> For new parts see official list sponsor:
> http://www.buymbparts.com/
> For used parts email [EMAIL PROTECTED]
> 
> To Unsubscribe or change delivery options go to:
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> 



      
____________________________________________________________________________________
Never miss a thing.  Make Yahoo your home page. 
http://www.yahoo.com/r/hs

_______________________________________