One ground for one service drop.

The NEC and other standards dictate that there be one
ground point common to a drop.  Multiple grounds
create real havoc within the system, not to mention
the potential (no pun intended) for some serious
damage in a fault or lightning situation.

Dan (with 20 years in the generator business)



 
--- dave walton <[EMAIL PROTECTED]> wrote:

> Would that not "invite" the lightening strike on
> your outbuilding to
> enter your house rather than be dissipated at the
> point of impact?
> The path of least resistance is your house.
> Is that a good thing?
> 
> -Dave Walton
> 
> 
> On Dec 17, 2007 4:44 PM, Allan Streib
> <[EMAIL PROTECTED]> wrote:
> > So, if I have an outbuilding, wired into my main
> panel in my house,
> > that outbuilding should not have a ground rod on
> *its* panel, but I
> > should instead extend a ground from my house to
> the outbuilding?
> >
> > Allan
> >
> >
> > Fmiser <[EMAIL PROTECTED]> writes:
> >
> > > It seems than at Mon, 17 Dec 2007 11:56:47
> -0600, R wrote:
> > >
> > >> Should the generator itself be grounded? I
> can't help thinking
> > >> that there should be a connection from the
> generator frame to
> > >> a good ground. I have considered driving a
> ground rod in and
> > >> either keeping a ground wire on it all of the
> time or setting
> > >> up something that would permit a quick ground
> connection at
> > >> either end.
> > >
> > > Yes.
> > >
> > > Or no.
> > >
> > > There should be one and only one place were
> ground and neutral
> > > are bonded together. This is usually done at the
> first load
> > > center (circuit breaker panel). This is also the
> usual place for
> > > the wire from the ground rod to also be bonded
> to the panel
> > > ground.
> > >
> > > If you are connecting a generator through this
> breaker panel,
> > > don't add another ground rod.
> > >
> > > If, however, you are running extension cords
> from the generator
> > > to each of the appliances, then it would be a
> really good idea
> > > to bond the generator neutral to generator
> ground and a ground
> > > rod.
> > >
> > > The reason is that earth is not a very good
> conductor, thus if there
> > > is a lightning strike there will be a voltage
> difference (possibly
> > > thousands of volts) between the ground rods. And
> and that difference
> > > will cause current flow in your wires.
> > >
> > >
> > > --           Philip
> > >
> > > _______________________________________
> > > http://www.okiebenz.com
> > > For new parts see official list sponsor:
> http://www.buymbparts.com/
> > > For used parts email [EMAIL PROTECTED]
> > >
> > > To Unsubscribe or change delivery options go to:
> > >
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> > >
> >
> > --
> > 1983 300D
> > 1966 230
> >
> >
> > _______________________________________
> > http://www.okiebenz.com
> > For new parts see official list sponsor:
> http://www.buymbparts.com/
> > For used parts email [EMAIL PROTECTED]
> >
> > To Unsubscribe or change delivery options go to:
> >
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> >
> 
> _______________________________________
> http://www.okiebenz.com
> For new parts see official list sponsor:
> http://www.buymbparts.com/
> For used parts email [EMAIL PROTECTED]
> 
> To Unsubscribe or change delivery options go to:
>
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> 



      
____________________________________________________________________________________
Never miss a thing.  Make Yahoo your home page. 
http://www.yahoo.com/r/hs

_______________________________________
http://www.okiebenz.com
For new parts see official list sponsor: http://www.buymbparts.com/
For used parts email [EMAIL PROTECTED]

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com

Reply via email to