Lightening is nothing if not unpredictable.
Would you settle for a frame ground at the remote generator site that
is not connected to neutral?

-Dave Walton

On Dec 17, 2007 4:58 PM, LWB250 <[EMAIL PROTECTED]> wrote:
> One ground for one service drop.
>
> The NEC and other standards dictate that there be one
> ground point common to a drop.  Multiple grounds
> create real havoc within the system, not to mention
> the potential (no pun intended) for some serious
> damage in a fault or lightning situation.
>
> Dan (with 20 years in the generator business)
>
>
>
>
>
> --- dave walton <[EMAIL PROTECTED]> wrote:
>
> > Would that not "invite" the lightening strike on
> > your outbuilding to
> > enter your house rather than be dissipated at the
> > point of impact?
> > The path of least resistance is your house.
> > Is that a good thing?
> >
> > -Dave Walton
> >
> >
> > On Dec 17, 2007 4:44 PM, Allan Streib
> > <[EMAIL PROTECTED]> wrote:
> > > So, if I have an outbuilding, wired into my main
> > panel in my house,
> > > that outbuilding should not have a ground rod on
> > *its* panel, but I
> > > should instead extend a ground from my house to
> > the outbuilding?
> > >
> > > Allan
> > >
> > >
> > > Fmiser <[EMAIL PROTECTED]> writes:
> > >
> > > > It seems than at Mon, 17 Dec 2007 11:56:47
> > -0600, R wrote:
> > > >
> > > >> Should the generator itself be grounded? I
> > can't help thinking
> > > >> that there should be a connection from the
> > generator frame to
> > > >> a good ground. I have considered driving a
> > ground rod in and
> > > >> either keeping a ground wire on it all of the
> > time or setting
> > > >> up something that would permit a quick ground
> > connection at
> > > >> either end.
> > > >
> > > > Yes.
> > > >
> > > > Or no.
> > > >
> > > > There should be one and only one place were
> > ground and neutral
> > > > are bonded together. This is usually done at the
> > first load
> > > > center (circuit breaker panel). This is also the
> > usual place for
> > > > the wire from the ground rod to also be bonded
> > to the panel
> > > > ground.
> > > >
> > > > If you are connecting a generator through this
> > breaker panel,
> > > > don't add another ground rod.
> > > >
> > > > If, however, you are running extension cords
> > from the generator
> > > > to each of the appliances, then it would be a
> > really good idea
> > > > to bond the generator neutral to generator
> > ground and a ground
> > > > rod.
> > > >
> > > > The reason is that earth is not a very good
> > conductor, thus if there
> > > > is a lightning strike there will be a voltage
> > difference (possibly
> > > > thousands of volts) between the ground rods. And
> > and that difference
> > > > will cause current flow in your wires.
> > > >
> > > >
> > > > --           Philip
> > > >
> > > > _______________________________________
> > > > http://www.okiebenz.com
> > > > For new parts see official list sponsor:
> > http://www.buymbparts.com/
> > > > For used parts email [EMAIL PROTECTED]
> > > >
> > > > To Unsubscribe or change delivery options go to:
> > > >
> >
> http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> > > >
> > >
> > > --
> > > 1983 300D
> > > 1966 230
> > >
> > >
> > > _______________________________________
> > > http://www.okiebenz.com
> > > For new parts see official list sponsor:
> > http://www.buymbparts.com/
> > > For used parts email [EMAIL PROTECTED]
> > >
> > > To Unsubscribe or change delivery options go to:
> > >
> >
> http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> > >
> >
> > _______________________________________
> > http://www.okiebenz.com
> > For new parts see official list sponsor:
> > http://www.buymbparts.com/
> > For used parts email [EMAIL PROTECTED]
> >
> > To Unsubscribe or change delivery options go to:
> >
> http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
> >
>
>
>
>       
> ____________________________________________________________________________________
> Never miss a thing.  Make Yahoo your home page.
> http://www.yahoo.com/r/hs
>
>
> _______________________________________
> http://www.okiebenz.com
> For new parts see official list sponsor: http://www.buymbparts.com/
> For used parts email [EMAIL PROTECTED]
>
> To Unsubscribe or change delivery options go to:
> http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
>

_______________________________________
http://www.okiebenz.com
For new parts see official list sponsor: http://www.buymbparts.com/
For used parts email [EMAIL PROTECTED]

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com

Reply via email to