** *300.3(B) Conductors of the Same Circuit.* All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4) [which don't help here]. National Electrical Code 2008 Edition

On 2013/11/19, 12:38, August Goers wrote:

Hi All --

On a related note, I've become good friends with some of the inspectors in San Francisco and they called me yesterday with a question. Is it okay to run _individual_ DC conductors through EMT for wire management purposes? We have always run paired positive and negative conductors in conduit so the question had never occurred to me. Obviously, you have to bond both ends of the conduit if it is over 250 v. I know that AC would have induction issues with running individual conductors but I'm not sure with DC.

Thanks,

August

August Goers

Principal

Luminalt Energy Corporation

o: 415.641.4000

m: 415.559.1525

www.luminalt.com <http://www.luminalt.com>

*From:*re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org> [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *William Miller
*Sent:* Monday, November 18, 2013 11:33 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] PV Wiring methods

Bill:

There is no need to stuff MC4 cables into standard conduit. You can either slot the pipe using our easy method or install bulkhead type connectors. The connectors are readily available. I get them from PV Cables in Northern California..

Wire routing problems and some solutions can be found on our web-site:

http://millersolar.com/MillerSolar/practices/PV_wiring/_PV_Wiring2.html

Since the industry won't provide wire management solutions, we are making our own. Questions: Just write or call.

William Miller

*From:*re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org> [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *frenergy
*Sent:* Thursday, November 14, 2013 7:46 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] PV Wiring methods

William, Bill....from another Bill,

Two things: For the rest of us (maybe it's just me?!) that's still trying to figure out how (or why) to stuff a MC4 connector into conduit and my hesitation in using SS wire ties for fear of the sharp edges cutting or chaffing into cables, I'm open for advice. Any wire I use on the roof is rated for that type of service and I have some off-grid systems that have been in the sun for some 25 years where the wire still looks nearly new even when flexing it to look for checking/cracks. It seems the wire/insulation can take it, thus it seems like the key to "wire management is to keep the wire from moving and off the roof, secured to the racking, thus not compromising the insulation.



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org