For the Radian
Page 59 of the operators manual ( it’s a different set of environmental 
specifications than the install manual or data sheets)
2000m max altitude. 

Jay
Peltz power. 

> On Apr 16, 2019, at 12:11 PM, <ch...@oasismontana.com 
> <ch...@oasismontana.com> wrote:
> 
> Let’s see it in writing, in the manuals included with the components and in 
> the online, downloadable manuals.  Clarity is of the essence!
>  
> Chris Daum
> Oasis Montana Inc.
> 406-777-4309 or 4321
> 406-777-4309 fax
> www.oasismontana.com
>  
>  
>  
> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
> Lones Tuss
> Sent: Friday, April 12, 2019 1:14 PM
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] High altitude off-grid systems
>  
> Hello All
> Outback’s Product Warranty is not based or negated by the altitude of the 
> installation.  Altitude ratings ensure full spec operation of the equipment 
> up to the stated elevation . As noted in several posts due to thinner air 
> cooling of equipment can be affected. Additional cooling may be required and 
> or additional products to achieve the necessary load requirements.
>  
>  
>  
> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
> jerrysgarage01
> Sent: Friday, April 12, 2019 11:26 AM
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] High altitude off-grid systems
>  
> Wrenches
> Here is the math, well the answer at sea level your body has 14.70 PSI 
> exerted on it, at 10,000 feet you only have 10.163 PSI, reduced air pressure, 
> reduced cooling or heating ability adjusted for standard sea level temp or 
> just over 69%.
> I have done work in Hawaii on the big island up at the summit, it can be warm 
> and very thin air, without air to cool no inverter will perform very well. I 
> have some SMA, FX and Raidians in warm high altitude locations and added 
> extra cooling to compensate for the lack of air. You will hear the cooling 
> fans spinning faster, moving less air at higher altitudes.
> SMA sunny island does have a 9k plus operating altitude but de-rates at less 
> the 7k.
> Jerry
> PV inspector 
>  
>  
>  
> Sent from my Verizon, Samsung Galaxy smartphone
>  
> -------- Original message --------
> From: Jay Pozner <j...@nunatakenergy.com>
> Date: 4/12/19 10:06 AM (GMT-08:00)
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] High altitude off-grid systems
>  
>  
>  
> We do a fair amount of systems at "altitude".  Recently we had an issue with 
> a Radian system at about 10,000'.  An 8048 inverter screaming (fans running 
> hard) with just 2000 watts of load.  I hounded tech support for two years, 
> and even after switching power modules, etc in the end the techs claim a 
> fairly substantial deration (that I can't quote right now) of inverter 
> performance because of cooling issues.  We  ultimately added another inverter 
> to the system at the end of last summer.  I hope this season we will see a 
> better result.   It makes sense, given the difference in air density, but I 
> do scratch my head and wonder why we haven't seen such issues with the older 
> FX's, and some of the older legacy systems?
>  
> I also know that the Midnite classic charge controllers seem to run the fans 
> quite hard as well.  I haven't had to replace any of the fans, and the 
> controllers are performing great, but wonder if that will be an issue in the 
> future.   It would be great if some manufactures would give us a quality, 
> competitively priced, equipment that is rated for altitude, but I don't think 
> there are that many options out there as of now
>  
>  
> .
> 
> Jay Pozner
> (970) 642-5554
> www.nunatakenergy.com
> NABCEP Certified PV Installer:
> Cert.#031310-177
> 
>  
>  
> On Fri, Apr 12, 2019 at 9:17 AM Steve Higgins <st...@surrette.com> wrote:
> Not to add fuel to the fire... and it's been almost 7 years since I've been 
> with an Inverter manufacturer so here is my .02 cents...  So again, I hope 
> I'm not overstepping the boundaries of the Wrenches list. 
>  
> If I remember correctly the main issue with the high altitude installs are 
> some of the components that are used to build the inverter/controllers aren't 
> rated to be used at high altitude, one of the main components that have this 
> issue is the electrolytic capacitors.    Of course, the specs vary from 
> component to component.   I've seen some rated as low as 8000 ft to some as 
> rated as high as 30,000 ft.   It really just depends on the part(s) that the 
> manufacturer used to build the product. 
>  
> As you gain altitude the temperatures and the air pressure decrease, as it 
> was explained to me years ago the problem is with the temperature decrease, 
> this will affect the capacitance of the capacitor.  The colder temps will 
> reduce the overall capacitance of the capacitor, just like it will with a 
> battery. 
> 
> These caps are generally used to filter noise from circuits, so when these 
> fail, or the capacitance values fall, you don't get the filtering you need 
> and this induces noise into your circuitry possibly causing overall failure 
> or worse,  the dreaded intermittent failure.   Generally, if the 
> inverters/controllers are kept on and warm, you won't have too many problems, 
> it's when they are in extremely cold temperatures is when you will start 
> having issues.  
>  
> Hope this helps!   Have a good weekend!   
>  
> 
> 
> Steve Higgins ⋅ Technical Services Manager
> t +1.902.597.4020  m +1.206.790.5840
> f +1.902.597.8447  e st...@surrette.com
> 
> CONFIDENTIALITY: The information transmitted herein is intended only for the 
> addressee and may contain confidential, proprietary and/or privileged 
> material. Any unauthorized review, distribution or other use of or the taking 
> of any action in reliance upon this information is prohibited. If you receive 
> this email in error, please contact the sender and delete or destroy this 
> message and all copies.
>  
>  
> On Fri, Apr 12, 2019 at 7:47 AM <ch...@oasismontana.com> wrote:
> Folks:
>  
> The issue here ulltimately isn’t whether it works or not, it’s if it’s 
> WARRANTED.  Some purchasers (in this case the USFS) mandate that all 
> equipment be warranted for high altitudes.  And that leaves out several major 
> suppliers.
>  
>  
> Chris Daum
> Oasis Montana Inc.
>  
>  
> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Ray
> Sent: Thursday, April 11, 2019 10:55 PM
> To: re-wrenches@lists.re-wrenches.org
> Subject: Re: [RE-wrenches] High altitude off-grid systems
>  
> We've had some systems at 11,000 ft plus, for almost 20 years.  We have 
> mixtures of Outback, Midnite, Blue Sky, and old Trace equipment.  Never any 
> issues with electronics related to altitude.  Actually the altitude related 
> system issues are generator derating, and array output exceeding STC ratings 
> on really clear cold days due to the thin atmosphere.  The third issue would 
> be installers not being able to catch our breath after jogging back to the 
> truck. 
> 
> Ray Walters
> Remote Solar
> 303 505-8760
> On 4/11/19 3:39 PM, Dan Fink wrote:
> Hi Chris; I am deeply concerned about this as nearly 100% of the systems I 
> install are at 8000 ft (2500m) or higher. I've never had a problem with 
> warranty claims to Outback or Schneider up to this time. If this is a "new 
> thing" I'd really like to know about it, on list or off.
>  
> The alitude de-rate stuff seems to involve dialectric ratings on the 
> transformer coils, and low air density for cooling. I think that's all in 
> ANSI.
>  
> 
> Dan Fink
> Director of Solar Education, Greendustrial Training LLC
> IREC Certified Instructor™ for: 
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP PV Associate
> Executive Director, Buckville Energy Consulting
> NABCEP Registered Continuing Education Providers
> dan.f...@greendustrialtraining.com
> 970-672-4342
> 
>  
>  
>  
> On Thu, Apr 11, 2019 at 1:28 PM <ch...@oasismontana.com> wrote:
> Hi folks:
>  
> I am curious as to how many of you sell/install battery/inverter systems at 
> high altitudes?  Have you had any particular issues with them?  Last year we 
> discovered (in a mostly costly fashion) that Schneider inverters (and also 
> Outback) are not warranted above 6500 ft. 
>  
> Magnum inverters are warranted to 15,000 ft max altitude. 
>  
> Best,
>  
> Chris Daum
> Oasis Montana Inc.
> 406-777-4309 or 4321
> 406-777-4309 fax
> www.oasismontana.com
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
>  
> 
> _______________________________________________
> List sponsored by Redwood Alliance
>  
> List Address: RE-wrenches@lists.re-wrenches.org
>  
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>  
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>  
> Check out or update participant bios:
> www.members.re-wrenches.org
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to