Hi Gary,

I was pretty suspicious of what the unit was claimed to do so I didn't give 
them any money.  It's good that we have a reflector like this one with 3000 
+ members on the list that can give their $0.02 as well as their technical 
expertise / opinions.

Thanks for replying to my original post.

Don, KD9PT

----- Original Message ----- 
From: "Gary Schafer" <gascha...@comcast.net>
To: <Repeater-Builder@yahoogroups.com>
Sent: Wednesday, February 11, 2009 3:43 PM
Subject: RE: [Repeater-Builder] OT Power Factor


> This is funny. All they appear to be doing is placing a capacitor across 
> the
> line at the service panel which gives some power factor correction to 
> motor
> or other inductive loads. But that correction is AT THE POWER PANEL which 
> is
> only inches or a few feet at the most away from the meter.
>
> If you are not being billed for reactive power but only for real power
> consumed, as you are in a typical home, then it does absolutely nothing 
> for
> you. It does not lower the current in your motor and does not help prolong
> its life. It only lowers the current going thru the meter. And since that
> extra current is reactive it cost you no more or no less whether it is 
> there
> or not.
>
> The other thing is, if you have no motors in inductive appliances running
> that capacitor is still across the line drawing CAPACTIVE reactance 
> current.
> Just the opposite of when the inductive load is on by itself.
> You would need a capacitor reactance value to match the inductive 
> reactance
> value  to fully cancel any reactive current.
>
> Not that this hurts anything on you electric bill as you still get billed
> only for real power used and not reactive power.
>
> You have just given away $299.95.
>
> 73
> Gary  K4FMX
>
>
>> -----Original Message-----
>> From: Repeater-Builder@yahoogroups.com [mailto:Repeater-
>> buil...@yahoogroups.com] On Behalf Of Mike Reed
>> Sent: Wednesday, February 11, 2009 1:42 AM
>> To: Repeater-Builder@yahoogroups.com
>> Subject: Re: [Repeater-Builder] OT Power Factor
>>
>> The device works by changing the voltage waveform to get the most work 
>> for
>> the least energy. NASA came up with idea many years ago, and it does work
>> well. I think this was designed more for household appliances and such,
>> not
>> repeater systems, unless you are counting the cooler that holds the
>> 807's...
>>  73
>>  Mike - N7ZEF
>>
>> ----- Original Message -----
>> From: "Don Kupferschmidt" <d...@httpd.org>
>> To: <Repeater-Builder@yahoogroups.com>
>> Sent: Tuesday, February 10, 2009 1:44 PM
>> Subject: Re: [Repeater-Builder] OT Power Factor
>>
>>
>> Hello group,
>>
>> I need to chime in here and ask about a device that being sold as an
>> enhancement for saving electrical energy in a residence.
>>
>> The device is called Power-Save 1200 and you can see it at
>> www.power-save.com.  From what I can glean from the web site it's a power
>> factor correction device that attaches to the load center wiring 
>> panel.via
>> 3
>> wires; 2 are attached to a dedicated 20 amp 2 pole 220 volt circuit
>> breaker,
>> the other remaining wire is attached to ground.  The instructions go on 
>> to
>> say that this device is designed to condition all power consumed by
>> inductive loads (electric motors) in the home regardless of installation
>> location.
>>
>> Their web site states: SAVE UP TO 25% ON YOUR MONTHLY ELECTRIC BILLS!
>> (Direct quote).  There is a video on the web site that shows a volt / amp
>> meter reading before and after the device is activated.  The unit sells
>> for
>> $299.95 + shipping & handling.  The dealer who told me about this device
>> states that the unit will pay for itself over time.
>>
>> My brother in law is an electrician and we have gotten into a lively
>> discussion about this device and the theory behind it.  I say that while
>> the
>> device will probably work as advertised, it may not provide a complete
>> savings to the owner as it is attached to the load center and not the
>> individual motor.  In essence, isn't the power company getting some
>> benefit
>> of this device since it's attached to the grid via the breakers which are
>> being fed by the power company?
>>
>> TIA for your comments.
>>
>> Don Kupferschmidt, KD9PT
>>
>>
>> ----- Original Message -----
>> From: "Eric Lemmon" <wb6...@verizon.net>
>> To: <Repeater-Builder@yahoogroups.com>
>> Sent: Monday, February 09, 2009 8:09 PM
>> Subject: RE: [Repeater-Builder] OT Power Factor
>>
>>
>> > Tom,
>> >
>> > Excellent questions!  The first is easy:  Residences and light
>> commercial
>> > occupancies have meters that measure real (true) power only.  That's
>> > because
>> > only real power does work, and that's what you are paying for.  The
>> > classic
>> > kWh meter with the spinning aluminum disk was perfected by Ferraris and
>> > Shallenberger more than a century ago, and millions are in service
>> today.
>> > The most recent improvement is a magnetically-levitated disk that 
>> > nearly
>> > eliminates any errors due to bearing friction.  A revenue-grade kWh
>> meter
>> > is
>> > extremely accurate, and very seldom requires service.
>> >
>> > True power is consumed only when the applied voltage and the resulting
>> > current are in phase.  In this specific case, volts times amps equals
>> > watts.
>> > When the current is not in phase with the applied voltage, we enter the
>> > mysterious world of apparent power, which is expressed as volt-amperes.
>> > Nearly all apparent power seems to be consumed by inductive apparatus
>> such
>> > as motors and transformers, except that such currents are returned to
>> the
>> > source as the magnetic field collapses.  Suffice it to say that the
>> > current
>> > actually flows in the circuit, but it does no real work.  When the 
>> > power
>> > factor (PF) is poor, a lot of current flows in the circuit that must be
>> > provided by the utility through larger diameter wires and bigger
>> > transformers.  Since PF is the ratio of true power to apparent power,
>> the
>> > utilities are always looking for ways to keep the PF close to unity, so
>> > that
>> > they can put off installing thicker wires and bigger substations.  As 
>> > an
>> > incentive for heavily-motored industries to increase the PF, some
>> > substantial penalties are levied on those who don't correct their PF.
>> The
>> > easy way to increase the typical PF is to add parallel capacitance so
>> that
>> > the inductive reactance is compensated by capacitive reactance.  The
>> goal
>> > is
>> > to get the PF above 0.95.
>> >
>> > Another reason for adding capacitors across the line is for voltage
>> > regulation.  In rural areas with long distribution lines- usually at
>> > 12,000
>> > volts- the voltage drop due to reactive currents can be significant.
>> The
>> > utility will add capacitor banks every few miles to help keep voltage
>> drop
>> > within narrow limits.  This is as good a time as any to state that the
>> > standard nominal utilization voltage in the United States is 120/240
>> > VAC on single-phase systems, and 120/208 VAC on three-phase systems.
>> > There
>> > hasn't been "110" or "220" in this nation for more than half a century,
>> > but
>> > some (usually older) folk still use those terms.
>> >
>> > The standard kWh meter does its magic by using a simple principle.  The
>> > torque on the aluminum disk is caused by two coils (or sets of coils)
>> that
>> > create a combined magnetic field.  One coil creates a magnetic field
>> > proportional to the applied voltage, while the other coil creates a
>> > magnetic
>> > field proportional to the line current.  When both voltage and current
>> are
>> > present, the disk spins.  A small permanent magnet acts as an eddy-
>> current
>> > brake, and ensures that the speed of the disk's rotation is exactly
>> > proportional to the product of voltage and current that are in phase-
>> true
>> > power.  The disk is geared to a register that records the revolutions
>> over
>> > time, resulting in power times time- energy.
>> >
>> > The rotating-disk kWh meter is being replaced with all-electronic 
>> > meters
>> > in
>> > many areas.  Such meters can record reactive power usage, and also
>> record
>> > the times that peak demands occurred.  Some really fancy electronic
>> meters
>> > can be remotely polled with a wireless system, so the meter reader can
>> > drive
>> > by the house or business and get the data on the fly.  Carrier-current
>> > data
>> > transfer systems are now in use that allow the utility to read meters
>> from
>> > a
>> > central office that is miles away.  Not only does the utility not have
>> to
>> > set meter readers out into rural areas, but any power outage is
>> > immediately
>> > revealed due to the loss of data.
>> >
>> > Back to your original question about your customer's motors.  If he is
>> not
>> > being penalized by the utility for excessive reactive power demand
>> (i.e.,
>> > low PF) then he will save nothing.  However, the judicious application
>> of
>> > capacitors may improve the voltage regulation within his building. 
>> > Some
>> > mountaintop repeater sites have a power feed that is many miles long,
>> and
>> > voltage drop caused by air conditioning and power supplies can be
>> > significant.  Some older Motorola and GE station supplies are not very
>> > efficient and have low PF when lightly loaded.  The typical site
>> > owner/manager is usually not a power engineer, and may be ignorant of
>> the
>> > significant inefficiencies of a low-PF power system.  This may exist 
>> > for
>> > years without anyone doing anything about it, leading to recurring
>> station
>> > problems and poor power quality.  The national standard for nominal
>> > utilization voltage is 120 VAC +/- 5%.  If the receptacle voltage goes
>> > below
>> > 114 VAC or exceeds 126 VAC, something needs to be done.
>> >
>> > 73, Eric Lemmon WB6FLY
>> >
>> >
>> > -----Original Message-----
>> > From: Repeater-Builder@yahoogroups.com
>> > [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Thomas Oliver
>> > Sent: Sunday, February 08, 2009 11:43 PM
>> > To: repeater-builder@yahoogroups.com
>> > Subject: [Repeater-Builder] OT Power Factor
>> >
>> > Question for any electrical engineers out there.
>> >
>> > Are the meters on the side of buildings metering real power or apparent
>> > power?
>> >
>> > Is power factor correction worth doing if the power company is not
>> dinging
>> > the customer for low power factor?
>> >
>> > This article
>> >
>> http://powerelectronics.com/power_management/motor_power_management/705PET
>> 23
>> > .pdf
>> >
>> <http://powerelectronics.com/power_management/motor_power_management/705PE
>> T2
>> > 3.pdf>   talks about residential power factor correction and my
>> conclusion
>> > (from this article) is the savings would never be recouped.
>> >
>> > Second conclusion is the only benefit with correction is the wires
>> between
>> > the source and load don't heat up as much. What about the wires in the
>> > motor
>> > or transformer? do they also heat less? I would think so.
>> >
>> > Third conclusion is by correcting power factor you are helping the
>> utility
>> > company more than yourself because these phase differences "standing
>> > waves"
>> > exist all the way back to the power generation source therefore the
>> > utility
>> > lines have more loss due to their greater length than the customers
>> > building
>> > wiring has.
>> >
>> > The reason I am researching this is a customer of mine has roughly 50 
>> > hp
>> > of
>> > total motors in his shop and wanted to know if he could save 30% on his
>> > electric bill like some salesman of power factor correction black boxes
>> > told
>> > him he could.
>> >
>> > I realize I am going to have to look at his energy bill to see if there
>> is
>> > a
>> > charge for low power factor and maybe call the utility company to see 
>> > if
>> > he
>> > will get a lower rate if he adds PFC devices
>> >
>> >