Rectifiers / Battery Chargers

1999-06-24 Thread Chris Healy

IEC950 clause 1.1.3 explicitly excludes  battery backup systems and
transformers , which are not an integral part of the equipment;..

Searching the IEC data base for applicable standards for rectifiers for
stationary battery systems does not provide any results.

The only examples of this type of  equipment I have seen claim
compliance to UL1950 or EN60950, or the applicable Australian Standard

Am I missing something here or is there really no applicable
international standard for rectifiers for stationary battery systems and
the only way around the problem to take a very liberal view of the term
integral part and apply the standard for the connected equipment?
--
Chris Healy
Liaison Manager, Standards and Approvals

Lucent Technologies email: ch...@jna.com.au
JNA Telecommunications  Ph (direct) : +61 2 9935
5728
16 Smith St, Chatswood, NSW 2067 AUSTRALIA  Fax : +61 2 9417 3862



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Australian electricity supply

1999-04-30 Thread Chris Healy
Any thing other than 415/240 will be a problem. 240/120  or 480/240 does not 
exist
in the normal distribution system. Where these exist it is from a specific
customer installation.

It is my understanding that the 250V areas of Western Australia are now the same
as the remainder of Australia and have been for some time.

jrbar...@lexmark.com wrote:

 Chris,
 The 1996 World Electricity Supplies shows Australia as :
 *  50Hz +/-0.1% frequency.
 *  415/240V or 240/120V +/-6% for households.
 *  415/240V or 480/240V +/-6% for commercial.
 *  22kV, 11kV, or 6.6kV +/- 6% for industrial.

 The 1991 edition of Electric Current Abroad shows:
 *  Albany,  Kalgoorie, and Perth as nominal 250/440V.
 *  The rest of Australia as nominal 240/415V.
   John Barnes  Advisory Engineer
   Lexmark International

 chris.colgan%tagmclarenaudio@interlock.lexmark.com on 04/29/99 04:47:33 AM

 Please respond to chris.colgan%tagmclarenaudio@interlock.lexmark.com

 To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
 cc:(bcc: John Barnes/Lex/Lexmark)
 Subject:  Australian electricity supply

 Hello group

 Can anyone tell me the limits of the Australian consumer mains supply
 voltage, ie 240V +?% -?%.

 I have ordered a copy of World Electricity Supplies but it hasn't arrived
 yet.

 Thanks

 Chris Colgan
 EMC  Safety
 TAG McLaren Audio Ltd

 mailto:chris.col...@tagmclarenaudio.com

 =
 Authorised on 04/29/99 at 09:47:52; code 37160057E31C4EB1.

 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).

 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).

--
Chris Healy
Liaison Manager, Standards and Approvals

JNA Telecommunications Limited  email: ch...@jna.com.au
A Lucent Technologies CompanyPh (direct) : +61 2 9935 5728
16 Smith St, Chatswood, NSW 2067 AUSTRALIA   Fax : +61 2 9417 3862



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Australian electricity supply

1999-04-29 Thread Chris Healy
Chris,

Try the following URL:
http://www.standards.org.au/standardization/electrotechnology/news/1999%2D03%2D25/1999%2D03%2D25.htm

There has been much discussion as to how to safely migrate to the standard
IEC 230V and the article describes the current situation and proposals for
the future.


Colgan, Chris wrote:

 Hello group

 Can anyone tell me the limits of the Australian consumer mains supply
 voltage, ie 240V +?% -?%.

 I have ordered a copy of World Electricity Supplies but it hasn't arrived
 yet.

 Thanks

 Chris Colgan
 EMC  Safety
 TAG McLaren Audio Ltd

 mailto:chris.col...@tagmclarenaudio.com

 =
 Authorised on 04/29/99 at 09:47:52; code 37160057E31C4EB1.

 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).

--
Chris Healy
Liaison Manager, Standards and Approvals

JNA Telecommunications Limited  email: ch...@jna.com.au
A Lucent Technologies CompanyPh (direct) : +61 2 9935 5728
16 Smith St, Chatswood, NSW 2067 AUSTRALIA   Fax : +61 2 9417 3862



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: low-watt transformer fusing

1998-12-06 Thread Chris Healy

Jeff,

The normal practice is to wind a thermal protective device in the
transformer. For larger transformers it is normally a resetable device but
for small transformers, a one time operation type is often used.


 On Fri,
4 Dec 1998, JENKINS, JEFF wrote:

 Hi folks,
 
 I have a question about transformer fusing.  I have an application that uses
 a 10W transformer connected across 400Vac mains.  It is my understanding
 that this requires a fuse rated to at least 400V, which would mean 500V
 because that's the next larger size available.  However, the smallest
 amperage fuse available at that voltage rating is 100mA.  This by far
 exceeds the transformer rating.  I thought about performing the EN 60742
 test of loading the transformer until the primary current is 2.1 x 100 mA =
 210 mA and taking thermal measurements, but I am quite sure the transformer
 will burn up under this large a load.
 
 The standards being used to evaluate this product are:
 EN 50178
 UL 1012
 CSA C22.2 No. 107.1
 
 Any suggestions?
 
 Regards,
 
 Jeff Jenkins
 Senior Regulatory Compliance Engineer
 Advanced Energy Industries, Inc.
 Fort Collins, CO USA 80525
 
 Opinions are my own and not necessarily shared by Advanced Energy
 Industries, Inc. or its affiliates.
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 

Chris Healy
Liaison Manager, Standards and Approvals

JNA Telecommunications Limited  email: ch...@jna.com.au
A Lucent Technologies CompanyPh (direct) : +61 2 9935 5728
16 Smith St, Chatswood, NSW 2067 AUSTRALIA   Fax : +61 2 9417 3862




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Australia EMC Limits

1998-11-19 Thread Chris Healy

Richard, Barry,

Please note that clauses 1, 3.1, 4.1 and 4.2. are modified by the
regulations.  4.2 relates to the class A/B issue. 

The notice can be found at http://www.aca.gov.au/legal/index.htm#Notices,
under, Radiocommunications Standards (Electromagnetic Compatibility) No. 1
of 1996 

Clasue 8 is the relevant clause.
.
Standard for information technology equipment 

 8. (1) Subject to subclause (2), this clause applies to the
performance, in the frequency band 9 kHz to 400GHz, of a device that:

 (a) has any of the following as its primary function in relation to
data or telecommunication messages:

  (i) entry; 

  (ii) storage; 

  (iii) display; 

  (iv) retrieval; 

  (iv) transmission; 

  (vi) processing; 

  (vii) switching; 

  (viii) control; and 

 (b) may be equipped with 1 or more terminal ports typically operated
for information transfer; and 

 (c) has a rated supply voltage not greater than 600 volts. 

 (2) This clause does not apply to a device to which clause 5, 6 or 7
applies. 

 (3) For the purposes of paragraph 162 (1) (a) of the Act, the
standard for the performance of the device is the
 standard set out in Australian/New Zealand Standard AS/NZS 3548:1995,
other than clause 1 and subclauses
 3.1, 4.1 and 4.2. 

 (4) For the purposes of the application of that Standard: 

 (a) telecommunications equipment is class A ITE, and must comply with
the class A ITE limits set out in the
 Standard; and 

 (b) a device (other than telecommunications equipment) is class B
ITE, and must comply with the class B ITE
 limits set out in the Standard, if: 

  (i) it is intended for household use; or
  (ii) it has no fixed place of use; or
  (iii) it is a personal computer; or
  (iv) it is auxiliary equipment that is, or is intended to be,
connected to a personal computer; and 

 (c) any other device is class A ITE, and must comply with the class A
ITE set out in the Standard. 

 (5) Paragraph (4) (a) ceases to have effect at the end of 31 December
1997. 

..


On Wed, 18 Nov 1998, Barry Esmore wrote:

 Richard
 
 Yes it provides both Class A and Class B limits and is identical to the
 European 
 IEC/CISPR 22 specification.
 
 Barry Esmore
 
 
 --
  From: WOODS, RICHARD wo...@sensormatic.com
  To: 'emc-pstc' emc-p...@majordomo.ieee.org
  Subject: Australia EMC Limits
  Date: Wednesday, 18 November 1998 8:46
  
  Does the Australian ITE emissions standard AS/NZS 3548 provide both Class
 A
  and Class B limits?
  
  -
  This message is coming from the emc-pstc discussion list.
  To cancel your subscription, send mail to majord...@ieee.org
  with the single line: unsubscribe emc-pstc (without the
  quotes).  For help, send mail to ed.pr...@cubic.com,
  j...@gwmail.monarch.com, ri...@sdd.hp.com, or
  roger.volgst...@compaq.com (the list administrators).
  
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 

Chris Healy
Liaison Manager, Standards and Approvals

email   : ch...@jna.com.au  JNA Telecommunications Limited
Ph (direct) : +61 2 9935 5728 16 Smith St, Chatswood, NSW 2067
Fax : +61 2 9417 3862   AUSTRALIA




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: IEC320 and Double insulation

1997-04-22 Thread Chris Healy

Hans,
  
The obvious problem with the following is in the special appliance
coupler. It allows a class I product to be connected without an earth. An
IEC320 double insulated coupler has only two pins and can not be connected
to a Class I product. A coupler which can be connected to a class I
product but not connect the earth can cause a hazard.

On Mon, 21 Apr 1997 hans_mellb...@non-hp-santaclara-om4.om.hp.com wrote:

 Item Subject: cc:Mail Text
 
 Fellow professionals;
 
 Is there anything in the EN60950 regulations re: LVD that would prevent me 
 from using a IEC three prong receptacle in my product connected to a 
 special power cord with only two wires and to a class 0 plug (two prong for 
 Europe) and the mating IEC 320 connector at the other end? (assume that my 
 product is designed to be double insulated).
 
 Best Regards
 
 Hans
 

Chris Healy
Liaison Manager, Standards and Approvals

email   : ch...@jna.com.au  JNA Telecommunications Limited
Ph (direct) : +61 2 9935 5728 16 Smith St, Chatswood, NSW 2067
Fax : +61 2 9417 3862   AUSTRALIA




IT and other Power Syatems

1997-02-21 Thread Chris Healy

The discussion on IT power systems has returned me to a subject which has
caused problems for some time. In Australia TT and IT power systems are
not allowed, and a PE is always provided. This makes life relatively
straight forward locally, but as some of our equipment has features which
rely on this situation, it causes problems when we export products where
the power systems are inconsistent.

A main problem is that there is a general lack of appreciation that the
equipment requirements can vary depending with the power system. It is
also common that a customer, often including technical types, are not even
aware there are different types of power systems. Now it is possible to
make most equipment double insulated and compatible with almost all
requirements for the different systems, but for some types of equipment
this requires a reduction in functions or features in the equipment, or
versions with different implementations.

There are a number of lists available on the net which list voltages and
even plug types for various countries, but we really need some more
details, including;
PE availability (always, where required or installation specific, rarely)
Power System (TN-(C, C-S, S), TT, TI other)
Voltage tolerance.
 
Is any one aware of a comprehensive listing of this nature?

From the discussions re Norway, it appears that would be a useful tool.
 
Chris Healy
Liaison Manager, Standards and Approvals

email   : ch...@jna.com.au  JNA Telecommunications Limited
Ph (direct) : +61 2 9935 5728 16 Smith St, Chatswood, NSW 2067
Fax : +61 2 9417 3862   AUSTRALIA






Re: C-Tick mark

1997-01-15 Thread Chris Healy

Bill,

I feel a bit like a PR rep. for Standards Australia and the SMA today.  

Both the C-tick and the RCM are available as software and hard copy
format from Standards Australia. The catch is that you need to supply a
copy of an authorization to use the mark from the relevant regulator.
Foreign manufacturers will need to obtain a copy if required from their
Australian agent, representative etc.

A representation of the C-tick is available on the SMA web site,
http://www.sma.gov.au. 

A specification for the RCM is in; 

AS/NZS4417 Marking of electrical products to indicate compliance with
regulators  Part 1: General rules for use of the mark.


On Wed, 15 Jan 1997, Bill Lyons wrote:

 In message pine.ult.3.95.970115070827.27600a-100...@clix.jna.com.au 
 Chris Healy wrote:
 
 Chris,
 
 Can you advise where definitive representations of the C-tick and RCM can 
 be obtained?  Quite a number of people (myself included) would like to 
 know what they actually look like.
 
 Art Michael amich...@connix.com is one of those who have been asking 
 this.
 
 Regards, Bill.
 
 -- 
 Bill Lyons - b...@lyons.demon.co.uk / w.ly...@ieee.org
 
 

Chris Healy
Liaison Manager, Standards and Approvals

email   : ch...@jna.com.au  JNA Telecommunications Limited
Ph (direct) : +61 2 9935 5728 16 Smith St, Chatswood, NSW 2067
Fax : +61 2 9417 3862   AUSTRALIA




Re: EMC and Safety approvals

1997-01-13 Thread Chris Healy
On Thu, 9 Jan 1997 hans_mellb...@non-hp-santaclara-om4.om.hp.com wrote:

 Item Subject: cc:Mail Text
 
 Author:  HANS MELLBERG at non-hp-santaclara,om4
 Date:01/09/97 02:03 PM
 

 
 Please also report on the Australian C-tick mark. How do I get one, and 
 is it good for New Zealand?
 
Hans,

As already stated, the Australian Spectrum Management Agency's web page
has most of the information you require for Australia under EMC Framework.
http://www.sma.gov.au. 

While the SMA in Australia and the Department of Commerce in New Zealand
both use the C-Tick mark, the rules for using the mark are currently
different. There are moves to align the requirements but this is likely
to take a couple of years.

The one important point in both countries is that the responsibility for
placing the mark on the equipment and meeting the other requirements must
be accepted by the importer or local manufacturer of the product in the
country of sale.


Chris Healy
Liaison Manager, Standards and Approvals

email   : ch...@jna.com.au  JNA Telecommunications Limited
Ph (direct) : +61 2 9935 5728 16 Smith St, Chatswood, NSW 2067
Fax : +61 2 9417 3862   AUSTRALIA




Re: DC Power entry

1997-01-07 Thread Chris Healy
On Sun, 5 Jan 1997, Robert Johnson wrote:

 Does anyone know any reason why the IEC 320 C-14 connector style cannot
 be used for DC power? Specifically, we have an application for primary
 power entry in the 48-70 Vdc range, typical of telecom applications, and
 I see no clear reason for redesign to implement a different connector.
 

 
 Bob Johnson
 

I have searched all the standards and other information I have regarding
this subject and not found an answer. On talking to test labs and others
on the issue, it tends to make them very nervous. 

The main issue relates to the use of IEC320 appliance couplers (mains
cables with IEC320-C14 connectors). These are so freely available and
so widely used for mains connection that it is very likely that equipment
using a IEC320-C14 connector will be connected to the mains at some time,
at least by accident. 

The products I was concerned with started out as mains equipment which
required a 48VDC version. The problem was solved by designing a supply
which ran from 35VDC to 264VAC. This made everyone happy. 

After much effort, I never did get a conclusive answer to using the IEC320
for a 48V only application. Designing a wider range power was a safer(as
in less solution risk as well as user risk)  solution. 

Chris Healy
Liaison Manager, Standards and Approvals

email   : ch...@jna.com.au  JNA Telecommunications Limited
Ph (direct) : +61 2 9935 5728 16 Smith St, Chatswood, NSW 2067
Fax : +61 2 9417 3862   AUSTRALIA