Re: [RE-wrenches] AFCI tripping on SB 4000US-12

2023-06-20 Thread Martin Herzfeld via RE-wrenches
Comment below -

--

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer™ Emeritus
California Solar & Electrical Contractor License  #00833782  C-46, C-10,
C-7, C-61 - D-56, D-31
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Underwriters Laboratories (UL) Certified PV Systems Installer #17, OSHA 30
Certificate
OSHA-Authorized Construction Safety Trainer #32-0106614
CompTIA® Certified Technical Classroom Trainer (CTT+™ Certified)
#T3NSZCNBBKB4QTQG
Solar & Electrical Construction Consultant - 2nd Party Evaluations

International Code Council® (ICC) Certified Residential Electrical
Inspector - E1 #8343181
International Association of Electrical Inspectors (IAEI) Member - #7035507
Electric Vehicle Infrastructure Training Program (EVITP™) Certification
#4039206
Contract Solar (PV) Technical Inspector - 3rd Party Inspections

Certificate - Stanford | Center for Professional Development - Energy
Innovation and Emerging Technologies (EIET)


On Mon, Jun 19, 2023, 11:33 AM August Goers via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi William - Is this a TL-21 inverter
> <https://files.sma.de/downloads/SB3-5TL-21-IS-xx-14.pdf?_ga=2.101814081.1325009506.1687199204-2010138759.1678983058>
> line from maybe 8 or 10 years ago? If I recall correctly, that was around
> the time period that SMA was first shipping with AFCI detection - we had a
> few SMA inverters from that vintage producing false AFCI errors. I think
> that long home runs can be part of the issue and the inverter circuitry was
> a little too sensitive. You might try calling SMA to see if there is a
> firmware update or a way to disable AFCI if you feel comfortable
> with disabling that safety feature.
>

Simply, would this be 690.11 and not be a situation of comfort, but "not in
or on buildings,"  "metal(lic) raceways" or other requirements to comply
with the exception?

Separately, we've had a few phantom type AFCI errors on older modules and
> after tons of troubleshooting we think that it might have been internal to
> the modules themselves.
>
> Good luck!
>
> Best, August
>
>
> On Mon, Jun 19, 2023 at 11:11 AM William Miller via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Friends:
>>
>>
>>
>> We installed a bunch of Shell SQ-150-PC modules on a ground mount almost
>> 20 years ago.  The original SB2500 inverters died so we upgraded to
>> SB4000US-21 inverters.  We had some ground fault or AFCI issues a number of
>> years ago so we replaced all homeruns with PV wire which resolved the
>> problem.
>>
>>
>>
>> These panels have J-boxes which we interconnected with 1/2” NMLT.  The
>> home runs are with PV wire with absolutely no splices and the inter-panel
>> jumpers are THWN.
>>
>>
>>
>> Recently we started getting AFCI disturbances on one inverter.  We
>> isolated the fault to one string.  We opened every pull box and panel J-box
>> and all of the wiring looks dry, clean and tightly connected.  We inspected
>> every panel front and back and see no hotspots or visible corrosion.
>>
>>
>>
>> I have a megger I have never used.  The homerun is kind of long so maybe
>> it has insulation problems.  I could isolate the homerun and megger those
>> leads.  I am researching if I can megger PV modules.  It looks like this is
>> commonly done.  That looks like my next step.
>>
>>
>>
>> Does anyone have any ideas on what I should do next? I suppose I could
>> start swapping each of the 10 modules in the problem string with panels in
>> the non-problem strings, but that seems like a lot of work.
>>
>>
>>
>> Thanks in advance.
>>
>>
>>
>> William Miller
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>&

Re: [RE-wrenches] Cable Tray Marking

2020-09-03 Thread Martin Herzfeld
1.  In addition, there's a conflict of signal words for
NEC 110.21(B) Field-Applied Hazard Markings."Where caution, warning, or
danger signs or labels are required by this Code, the labels shall meet the
following requirements ..."  In other words, one signal word is DANGER and
the other signal word is WARNING.  Simply, DANGER *will* result in ... and
WARNING *could* result in ...

2.  Specifically, in NEC 2020 690.31(D)(2) the signal word of WARNING" was
*removed* and does not now appear to conflict?  In California, 2017
NEC/2019 CEC 690.31(G)(3) still has the WARNING signal word.  By the way,
NEC 392.18(H) refers to 110.21(B).

BTW, more information ANSI Z535 is found here:
https://webstore.ansi.org/standards/nema/ansiz5352011r2017-1668874

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy - Since 2016

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7 - Since 2004
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507 - Since 2006
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider


On Thu, Sep 3, 2020, 5:53 AM Rebekah Hren  wrote:

> This is interesting, since the definition of high voltage was changed to
> >1000V a few code cycles ago and it is somewhat consistently applied
> throughout the NEC at that voltage (except for workspace clearances...er).
> It seems this 392.18 label requirement could cause confusion and should be
> changed to apply to >1000V circuits.  However, the definition of high
> voltage only applies with Article 490 , Equipment >1000V so the Article 392
> Cable Tray folks can do what they want in terms of where they require high
> voltage labeling. I haven't done any research on the history of this
> labeling requirement.
>
>
> Corey maybe you would be willing to make a public input to change where
> the label is required to >1000V circuits, thus there would be no
> conflict with 690 since PV DC circuits in or on buildings cannot be >1000V.
> Due Sept 10!
>
> 490.2 Definition.
>
> The definition in this section shall apply only within this article.
> High Voltage.
>
> A potential difference of more than 1000 volts, nominal.
>
> Thanks for bringing this up Corey!
>
>
> On Thu, Sep 3, 2020 at 12:36 AM Ray  wrote:
>
>> This is interesting, because we were considering cable trays, too.  My
>> guess is that both requirements would apply.  Picky, but I don't see that
>> 690 exempts the requirements of 392. One is for PV, one is for over 600 v.
>> Some code iteration in the future might have combined language for PV over
>> 600 v " Danger - High Voltage Photovoltaic Source - Keep Away"  and of
>> course that's so verbose that the average Joe is just going to stick his
>> paws in there anyway.
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>>
>> On 9/2/20 7:54 PM, Corey Shalanski wrote:
>>
>> Wrenches,
>>
>> I am curious about the marking requirements for cable trays containing PV
>> source/output circuits rated over 600 volts, installed on a building:
>>
>>
>> NEC 392.18(H) requires a permanent, legible warning notice carrying the
>> wording “DANGER — HIGH VOLTAGE — KEEP AWAY” at least once every 10 ft.
>>
>> NEC 690.31(G)(3) requires a label or marking with the wording "WARNING:
>> PHOTOVOLTAIC POWER SOURCE" at least once every 10 ft.
>>
>> Does the 690.31 label take precedence? Are there any situations where
>> both labels would be required (or recommended)?
>>
>> --
>> Corey Shalanski
>> Jah Light Solar
>> Portland, Jamaica
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:www.member

Re: [RE-wrenches] IAEI Online Articles

2020-08-21 Thread Martin Herzfeld
FYI - I've been using the IAEI App found here:  http://bit.ly/IAEIApp1 with
access to past issues.

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7 - Since 2004
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507 - Since 2006
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider



On Thu, Aug 20, 2020, 2:41 PM Ryan Mayfield  wrote:

> Looks like they changed their URL (and access style), seems odd they don't
> have the old one redirect you...
>
>
> https://www.iaei.org/Online/Magazine/Online/IAEI_Magazine.aspx?hkey=859b0900-7ea8-490b-8915-0c5993d14a89
>
>
>
>
> On Thu, Aug 20, 2020 at 2:29 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> I thought it was just me. It has been like that for a few weeks.
>>
>>
>>
>>
>> On Thu, Aug 20, 2020 at 4:50 PM Corey Shalanski 
>> wrote:
>>
>>> Does anyone know what happened to the online IAEI magazine article
>>> website: https://iaeimagazine.org/
>>> <https://mailtrack.io/trace/link/de698899b103412449d867c0be5398aadcc7b953?url=https%3A%2F%2Fiaeimagazine.org%2F&userId=1613865&signature=aea8e3c01a292e70>
>>>
>>> It no longer seems to be accessible?
>>>
>>> --
>>> Corey Shalanski
>>> Jah Light Solar
>>> Portland, Jamaica
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/41e914c2085b3b5a62d4e5b1187860f35d19005c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=dff11691c36e45ba>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/f92a20adeaaf7eeb637ed7cc5da6d5b7b7badd43?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e7df488506df900e>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/8cdc54c93a33e19f4770fb6b456cfbc00a88993f?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=3792e65fea94a2d1>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/107b1d91b972afd352f51b2fde43966b8949ca1e?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=6490b797bc3f7405>
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> [image: photo] <https://www.mayfield.energy/>
> *Ryan Mayfield*
> *Founder & CEO*
>
> *(541) 231-9984 <(541)+231-9984>*  | *ryan@mayfield.energy
> *
>
> www.mayfield.energy
> <https://www.linkedin.com/in/ryanmayfield/>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] protecting wire below 8'

2020-07-18 Thread Martin Herzfeld
Simply, the '2.5 m' (8 ft) has been inferred from Article 110.27(A)(4).
It's interesting now that the distance in the 2019 CEC/2017 NEC has
increased based on voltage.  In other words, if the voltage is greater than
301 volts the minimum would be 8 ft 6 in. :)

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507 - Since 2006
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider

On Fri, Jul 17, 2020, 7:32 PM August Goers  wrote:

> Hi Kirk - We work in San Francisco where they have a local code amendment:
> <https://codelibrary.amlegal.com/codes/san_francisco/latest/sf_building/0-0-0-84935>
>
> 300.4(I)  Add the following section:
>  (I)   Subject to Physical Damage. Premises wiring systems installed less
> than 2.44 m (8 feet) above a walking surface or finished floor are
> considered subject to physical damage.
>
> As far as I'm aware otherwise, there is not a specific definition
> specifying 8' for physical damage in the broader NEC - I think it's just up
> to the AHJ.
>
> August
> Luminalt
>
>
>
>
> On Fri, Jul 17, 2020 at 8:38 AM Kirk Herander  wrote:
>
>> All,
>> Is there a reference to this so-called "8-foot rule" that someone could
>> point me to in the NEC? Thanks.
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-11 Thread Martin Herzfeld
Drake, I concur with your approach on this item -

1.  Either the shock hazard was reduced by NEC 690.12 with MLPE for the
workers *too* or folks have been qualified persons in accordance with NEC
690.4(C) to recognize and avoid the shock hazard for string inverters.

2.  Specifically, there's this incident on the list found here:
https://www.osha.gov/pls/imis/accidentsearch.accident_detail?id=101927.015
In other words, would this incident have been minimized with the use of
MLPE?

On Wed, May 6, 2020, 5:41 PM  wrote:

> Interestingly enough, the data on the link
> <https://www.osha.gov/pls/imis/AccidentSearch.search?p_logger=1&acc_description=&acc_Abstract=solar&acc_keyword=&sic=&naics=&Office=All&officetype=All&endmonth=05&endday=05&endyear=2002&startmonth=05&startday=05&startyear=2021&InspNr=>
>  provided
> shows accidents from gas explosions, falls, health problems and  industrial
> injuries. None of these incidents could have been prevented by module level
> power electronics. This is typical of the data that I've seen so far.
> ---
>
>
>
> On 2020-05-06 17:22, Martin Herzfeld wrote:
>
> There could be an issue of encouraging MLPE for worker safety?
>
> 1.  This is data involving incidents with workers in the OSHA Fatalities
> and Catastrophe Investigation Summaries found here:
>
> https://www.osha.gov/pls/imis/AccidentSearch.search?p_logger=1&acc_description=&acc_Abstract=solar&acc_keyword=&sic=&naics=&Office=All&officetype=All&endmonth=05&endday=05&endyear=2002&startmonth=05&startday=05&startyear=2021&InspNr=
>
> 2.  In the past I've observed an arc fault at the module level with
> traditional string systems without a listed arc-fault circuit interrupter
> NEC/CEC 690.11. The function in NEC/CEC 690.12 would be - to *reduce the
> shock hazard *- for *emergency responders* or *firefighters? (NEC 2020).*
> However, I've observed thermal events in the panelboard with plans and
> workmanship issues.
>
> On the other hand, falls are the #1 reason for incidents in the
> construction industry.
>
> All the best,
>
> Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
> Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
> 10037
> Contract Training Provider (CTP)
> Adjunct Professor, Energy
>
> California Solar & Electrical Contractor License  #00833782  C46, C10,
> D56, D31, C-7 - Since 2004
> Solar, Electrical, Trenching, Pole Installation & Maintenance,
> Instrumentation
>
> Contract Solar (PV) Technical Inspector - 3rd Party Inspections
> Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
> OSHA-Authorized Construction Trainer #32-0105338
> CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
>
> * Professional Member, International Association of Electrical Inspectors
> #7035507 - Since 2006
> * Accredited and Registered North American Board of Certified Energy
> Practitioners (NABCEP) Continuing Education (CE) Training Provider
>
>
> On Thu, Apr 30, 2020, 8:29 AM 
> wrote:
>
>
> I would like to see real data on the fire risk of string inverters.
> Anecdotal problems are not data.
>
> The industry is definitely heading toward MLPE due to the rapid shutdown
> requirements. In many cases MLPE makes sense, in other cases it doesn't.
>
> Systems that are more cost effective and reliable can often be built by
> using string inverters.
> ---
>
>
>
>
> On 2020-04-29 22:05, Jason Szumlanski wrote:
>
> "Rapid Shutdown does not prevent fires."
>
> Not true. If the effect of RS is to steer the market to MLPE, I believe it
> has a significant impact on reducing fire risk. As one who has watched a DC
> conductor fire smolder out of control, I am sold on an AC module or
> microinverter architecture. While RS on a DC array doesn't necessarily
> reduce fire risk within the array, it still has the potential to reduce
> severity and spread. Nothing is going to prevent all fires. I get that.
> We're talking about risk mitigation when it comes to RS.
>
> As for "dependable string inverters," the one dependable feature is
> failure at least once in the module lifetime, accompanied by a shocking
> repair bill.
>
> I'm not a shiny object following kind of guy, but the writing is on the
> wall. MLPE is the future. Modular, serviceable, disposable if you will.
> Like it or not, Edison is going to lose this battle to Tesla (Tom vs
> Nikola). And I live less than 5 minutes away from Tommy E's winter home in
> Fort Myers, FL. And I "grew up" in the industry living off-grid in DC
> power. 

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-06 Thread Martin Herzfeld
There could be an issue of encouraging MLPE for worker safety?

1.  This is data involving incidents with workers in the OSHA Fatalities
and Catastrophe Investigation Summaries found here:
https://www.osha.gov/pls/imis/AccidentSearch.search?p_logger=1&acc_description=&acc_Abstract=solar&acc_keyword=&sic=&naics=&Office=All&officetype=All&endmonth=05&endday=05&endyear=2002&startmonth=05&startday=05&startyear=2021&InspNr=

2.  In the past I've observed an arc fault at the module level with
traditional string systems without a listed arc-fault circuit interrupter
NEC/CEC 690.11. The function in NEC/CEC 690.12 would be - to *reduce the
shock hazard *- for *emergency responders* or *firefighters? (NEC 2020).*
However, I've observed thermal events in the panelboard with plans and
workmanship issues.

On the other hand, falls are the #1 reason for incidents in the
construction industry.

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7 - Since 2004
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507 - Since 2006
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider


On Thu, Apr 30, 2020, 8:29 AM  wrote:

>
> I would like to see real data on the fire risk of string inverters.
> Anecdotal problems are not data.
>
> The industry is definitely heading toward MLPE due to the rapid shutdown
> requirements. In many cases MLPE makes sense, in other cases it doesn't.
>
> Systems that are more cost effective and reliable can often be built by
> using string inverters.
> ---
>
>
>
>
> On 2020-04-29 22:05, Jason Szumlanski wrote:
>
> "Rapid Shutdown does not prevent fires."
>
> Not true. If the effect of RS is to steer the market to MLPE, I believe it
> has a significant impact on reducing fire risk. As one who has watched a DC
> conductor fire smolder out of control, I am sold on an AC module or
> microinverter architecture. While RS on a DC array doesn't necessarily
> reduce fire risk within the array, it still has the potential to reduce
> severity and spread. Nothing is going to prevent all fires. I get that.
> We're talking about risk mitigation when it comes to RS.
>
> As for "dependable string inverters," the one dependable feature is
> failure at least once in the module lifetime, accompanied by a shocking
> repair bill.
>
> I'm not a shiny object following kind of guy, but the writing is on the
> wall. MLPE is the future. Modular, serviceable, disposable if you will.
> Like it or not, Edison is going to lose this battle to Tesla (Tom vs
> Nikola). And I live less than 5 minutes away from Tommy E's winter home in
> Fort Myers, FL. And I "grew up" in the industry living off-grid in DC
> power. But AC distribution wins for safety at various scales.
>
>
>
>
>
>
> On Wed, Apr 29, 2020, 9:42 PM 
> wrote:
>
> Rapid Shutdown does not prevent fires; it was originally drafted to allow
> firefighters to vent a roof without being hindered by energized PV arrays.
> This rule was expanded to include other DC wiring from PV sources.
>
> As for PV safety, I'd like to see some significant, statistical evidence
> that shows there is a major fire danger from PV relative to other sources.
> A fire from a solar array gets a lot more press than one from a gas leak,
> bad wiring or an ash tray emptied into a wastepaper basket.
>
> Large public buildings should have all the protection that is available.
> Does one size fit all?
>
> Would it be reasonable to allow residential installations under 12 kW,
> with 1/4 of the roof adjacent to the array available for venting, to be
> excepted from 690.12? What about sparsely occupied commercial buildings
> with ample roof area open for ventilation?
>
> Many of us have chosen to work with renewable energy technology to lessen
> the harms caused by fossil fuel extraction and combustion. The need for
> non-carbon based energy sources has become extremely clear.
>
> The old string inverters still chug along year after year, with little or
> no maintenance. Someone must pay f

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Martin Herzfeld
1. I use a MLPE residential ground-mounted solution - rapid shutdown or
not.  w/Accessible MLPE.

2. There is a maximum physical string length for me to keep in mind, for
instance, found here:

"In the context of this document, string length refers to the number of
optimizers and modules in the string. When designing the installation make
sure to maintain the maximum physical string length as well: The total
cable length of the string (excluding power optimizers’ conductors) should
not exceed 1000ft./300m from DC+ to DC- of the inverter (2,300ft./700m when
using the SE14.4KUS, SE30KUS,SE33.3KUS, SE43.2KUS, SE66.6KUS and SE100KUS
inverters)"
https://www.solaredge.com/sites/default/files/string_sizing_na.pdf


All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
(IAEI) #7035507 - Since 2006
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider

On Wed, Apr 29, 2020, 8:17 AM Jay  wrote:

> Hi Drake
>
> I will disagree, there have been many roof top fires.
>
> But regardless we have to do these new regulations and I for one welcome
> the safety.
>
> The main issue is accessing the faulty/suspect component under the module
> possibly requiring removing multiple modules, a slow and expensive process.
>
> My technique is to install the MLPE at the edges of the array, using wire
> extensions. That way at most I have to remove a single module.  And Im
> working on a drop bracket which would allow better cooling and easier
> access without module removal to the MLPE, greatly reducing time to swap.
>
> Jay
>
> Peltz Power.
>
>
>
>
>
> On Apr 29, 2020, at 7:59 AM, drake.chamber...@redwoodalliance.org wrote:
>
> 
>
> Clearly, rapid shutdown increases cost and reduces reliability. Given the
> excellent safety record of PV, prior to rapid shutdown being required, it
> is unnecessary. The few anecdotal incidents of PV fires were not enough to
> justify the requirement, especially on smaller systems.
>
> According to a friend who worked for a local installation company that
> went under, a big part of the reason for their failure was the chronic
> replacement of microinverters and optimizers.
>
> What steps can be taken to create some balance in the rapid shutdown
> requirements that are in the NEC?
>
>
> ---
>
>
>
> On 2020-04-29 07:27, Sky Sims wrote:
>
> So far rapid shutdown has been a nightmare. It's added a lot of cost for
> no measurable benefit.
> Using always off devices like midnight solar and Tigo makes it impossible
> to test open circuit voltages. Which opens the door to tons of problems
> when commissioning systems.
> Also we've been trying out midnight Solar's product and have had an absurd
> failure rate. Which means lots of truck rolls and troubleshooting and
> system downtime. They send replacement product but they aren't paying for
> the lost weeks of productivity.
> We have Tigo product in hand and are deciding which project to try it on.
> But our big concern about using it is not only the inability to confirm
> open circuit voltage of the strings but also the way panels bypass if the
> device doesn't allow the panel to connect properly. Both of these features
> are a recipe for problems and potential troubleshooting nightmares. The
> warranty from Tigo doesn't cover our expense if the product fails. And
> that's really what our reservations about the product boil down to right
> now. If we're on a job with 50 units and one fails, the contractor or the
> homeowner will be the ones eating the expense of finding it and replacing
> it. There has to be a better option.
>
> Sky Sims
> Https://EcologicalSystems.biz
>
> On Apr 28, 2020, at 7:46 PM, Corey Shalanski  wrote:
>
> Now that 690.12 of the *NEC* 2017 has been in effect for several years, I
> am curious how designers and installers are meeting the associated
> requirements with string inverter-based systems (*not* considering
> microinverters or DC optimizers). I am generally a fan of the KISS
> principle, and as best I can determine the *

Re: [RE-wrenches] Industry Publications

2020-04-17 Thread Martin Herzfeld
I'd suggest IAEI magazine found here: https://iaeimagazine.org/magazine/

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7, Since 2004
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member Since 2006, International Association of Electrical
Inspectors
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider

On Thu, Apr 16, 2020, 9:28 PM Corey Shalanski  wrote:

> Wrenches,
>
> Like myself, I imagine many folks on this list were avid readers of "Home
> Power" and "SolarPro" magazines. I know some of you were even active
> contributors to these two wonderful publications.
>
> Is anyone aware of any similar resources - geared toward system
> designers/installers/technicians (or just general enthusiasts)? Besides
> this list, where are Wrenches turning to nowadays for relevant discussion
> of current industry topics?
>
> --
> Corey Shalanski
> Jah Light Solar
> Portland, Jamaica
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Ground mount fire code clarifications

2020-03-20 Thread Martin Herzfeld
Dan,

I think there should more discussions on ground-mounted arrays as an option
in addition to rooftop systems - to get out ahead of any issues.  In
addition, any renderings for ground-mounted arrays and ground-mounted stuff
as ESSs.

1.  By definition, a brush could mean a "slight and fleeting touch" - which
we do not want to do at these times :) or "undergrowth, small trees and
shrubs."

2.  The challenge also in one and and two family dwellings when there is a
setback of only (3) three feet as an accessory structure and the (10) foot
rule.

3.  I think mounts can be categorized in general as SPMs (Side of Pole
Mounts), TPMs (Top of Pole Mounts), MPM's (Multiple Pole Mounts) or an Open
Structure with the ability to walk underneath or a Closed structure where
you can not walk underneath.

4. BTW, you may wish to look at versions of ISEP and the IRC too?

"A.   RS402.4 (R324.6) Ground-mounted photovoltaic systems.

Ground-mounted photovoltaic systems shall be designed and installed in
accordance with Section (R301).

B.  RS402.4.1 (R324.6.1) Fire separation distances.

Ground-mounted photovoltaic systems shall be subject to the fire separation
distance requirements determined by the local jurisdiction."


5.  Gravel and the various types is also my goto soil amendment. In
California, I'd also suggest working with a C27 Landscaping Contractor on
what type of blue flowers would be okay.


What do you think?

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Provider

Telephone & Text: 510.243.0190


On Fri, Mar 20, 2020, 4:06 PM Dan Fink  wrote:

> Hello esteemed Wrenches; I am trying to clear this up for a client and his
> AHJ, which is also puzzled at how to interpret IFC 2018, Section 1204.4,
> which states:
>
> Setback requirements shall not apply to ground-mounted, free-standing
>> photovoltaic arrays. A clear, brush-free area of 10 feet (3048 mm) shall be
>> required for ground-mounted photovoltaic arrays.
>
>
> I found one lone informational note in a white paper stating this was to
> prevent a burning PV array from igniting surrounding vegetation and the
> fire spreading.
>
> So, has anyone dealt with an AHJ on this before? Our questions are:
>
>- What exactly is a "free-standing photovoltaic array" that is exempt?
>A pole mount? Couldn't burning debris from that ignite vegetation
>underneath?
>- What exactly does "A clear, brush-free area of 10 feet (3048 mm)"
>mean? "10 feet" is a linear measurement, not an area, that would be in
>square feet.
>- What is "brush"? Does grass count as brush?
>
> I would interpret this on the safe side as meaning that all vegetation
> under the PV array and out to a 10 foot perimeter should be cleared, except
> for pole-mount arrays (that exception makes no sense to me).
>
> I always recommend to clients that the area *under* the ground mount
> array should be pea gravel bordered by railroad ties, but out to 10 feet
> from the array edge seems excessive.
>
> Any input greatly appreciated!
>
> Dan Fink
> Executive Director, Buckville Energy Consulting
> NABCEP PV Associate
> NABCEP Certified PV System Inspector
> IREC Certified Instructor™ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP Registered Continuing Education Providers
> d anbo...@gmail.com
> 970-672-4342
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Re: [RE-wrenches] Solar set backs

2020-01-14 Thread Martin Herzfeld
Simply, an emphasis is now also on the location of ESSs in non-habitable
and habitable spaces and the size in kWh.

BTW, I attended a day of of a two day free IAFF Conference in California
announced through the IAEI, with UL found here:
https://connect.ul.com/meeting-challenges-of-built-environment-sacramento.html#meetingagenda


All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
https://www.youracclaim.com/badges/a54a49a9-31cb-4f52-b35f-9d7c90630bb9/public_url
Adjunct Professor, Energy, American River College
Contract Training Provider (CTP)

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Provider

On Tue, Jul 10, 2018, 2:38 PM Wayne Irwin 
wrote:

> Calfire code seems to be the standard being somewhat enforced as the
> standard nationwide.
>
> Wayne Irwin,
> President
> License #CVC56695
> State Licensed Solar Contractor
> Pure Energy Solar International Inc.
> wa...@pureenergysolar.com
> http://PureEnergySolar.com
> http://SolarChargingStation.net
> 352 377-6527 Office
> 352 336-3299 Fax
>
>
> The Sun Is Always Shining!
>
> The content of this message is Pure Energy Solar Confidential. If you are
> not the intended recipient and have received this message in error, any use
> or distribution is prohibited. Please notify me immediately by reply e-mail
> and delete this message from your computer system. Thank you.
> --
> *From:* RE-wrenches  on behalf
> of Daniel Young 
> *Sent:* Tuesday, July 10, 2018 5:25:01 PM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] Solar set backs
>
>
> Hey Gary,
>
>
>
> Ohio Fire Code does cover this. It’s a matter of if the Fire marshal in
> you project area wants to waive or alter the requirements.
>
>
>
> http://codes.ohio.gov/oac/1301:7-7-06v1
>
>
>
> Specifically 605.11.1.2 is for residential buildings. There is some
> conflict in terms of Hip roofs in the code there. 605.11.1.2.2 states a
> single 3ft path on one edge or another for a hip roof, but 605.11.1.2.4
> states that an 18 space is allowed when modules are mounted on two adjacent
> roof planes with a hip roof.
>
>
>
> With Regards,
>
>
>
> Daniel Young,
>
> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *gary easton
> *Sent:* Monday, July 09, 2018 3:39 PM
> *To:* RE-wrenches 
> *Subject:* [RE-wrenches] Solar set backs
>
>
>
> Hello Wrenches,
>
> What are you all seeing required as setbacks post 2017?  I am having
> inspectors vary between wanting a 3' lane at the bottom and sides to
> allowing the array down to the gutter, and from requiring between 18" and
> 3' at the ridge.
>
>
>
> --
>
> Gary Easton
> Appalachian Renewable Power
>
> Stewart, Ohio 45778
> NABCEP Certified Solar PV
>
> T: 740-277-8498
>
>  www.arp-solar.com
>
>
> “First they ignore you. Then they laugh at you. Then they fight you. Then
> you win.”
>
> ~Ghandi
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC in PDF format not availaible for 2020

2020-01-12 Thread Martin Herzfeld
FYI Only - In California, the Codes are found here:
https://www.dgs.ca.gov/BSC/Codes#@ViewBag.JumpTo

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Adjunct Professor, Energy, American River College
Contract Training Provider (CTP)

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Provider


On Sun, Jan 12, 2020, 6:11 AM Christopher Warfel <
cwar...@entech-engineering.com> wrote:

> I think that once a building code is adopted it must be made available at
> no charge. You bring up a good point.  The NEC is incorporated into many
> state's and the International Code.  Why can they charge for all access?
> Chris
> On 1/8/2020 6:36 PM, William Miller wrote:
>
> Friends:
>
>
>
> I find the PDF version best for my uses.  A portable, searchable,
> bookmark-able and cut and paste-able resource is essential for my work flow.
>
>
>
> I don’t think the NFPA is considering the needs of the field engineer when
> eliminating the PDF version.  Maybe there are some members of this forum
> that have the ear of the NFPA and can put in a word to restore the portable
> version.
>
>
>
> As an aside, I find it troubling that one has to pay to read any law of
> the land.  If a society makes rules, they should be freely available for
> all to review, free of charge.  That is just my altruistic bias.
>
>
>
> William Miller
>
> Miller Solar
>
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2020 not available as a portable PDF?

2020-01-09 Thread Martin Herzfeld
FYI -

1.  As a member of the IAEI, "after three consecutive renewals you are
eligible to receive a free National Electrical Code (NEC) book" as found
here:  https://www.iaei.org/Online/Benefits.aspx

2.  I've been a member of IAEI for years and I've have received free NEC
Code books.  I've enjoyed the portable NFPA NEC portable "phone app" which
did not required an internet connection found here:
https://www.nfpa.org/Codes-and-Standards/All-Codes-and-Standards/NFPA-digital-products
- also now not available.

3.  In other words, since I'm forced to use only the portable "paper copy,"
I'd rather receive it for free with other IAEI member benefits.

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
https://www.youracclaim.com/badges/a54a49a9-31cb-4f52-b35f-9d7c90630bb9/public_url
Adjunct Professor, Energy, American River College
Contract Training Provider (CTP)

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer

CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
https://www.youracclaim.com/badges/f23ae19b-0370-4ca1-99d1-418403a8faea/linked_in_profile
Contract Solar (PV) Technical Inspector - 3rd Party Inspections

* Professional Member, International Association of Electrical Inspectors
(IAEI)
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Provider


On Wed, Jan 8, 2020, 4:34 PM Bradley Bassett  wrote:

> The best price I've found for the handbook is at Barnes & Noble. If you go
> into the store you have to ask for the internet price. Also at least at my
> store they had it behind the counter in case you go looking for it.
>
> Brad
>
> On Wed, Jan 8, 2020 at 3:26 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> We are going backwards in this world. Thanks for making us less
>> productive, NFPA. #Greedy.
>>
>> On Wed, Jan 8, 2020 at 5:26 PM gary easton  wrote:
>>
>>> It’s a subscription.  The digital you pay for access each year.
>>>
>>> On Wed, Jan 8, 2020 at 5:20 PM Glenn Burt  wrote:
>>>
>>>> It is true, I have both 2017 and 2014 in PDF format.
>>>>
>>>> They must be concerned about piracy.
>>>>
>>>> -Glenn
>>>> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>>>>
>>>> -- Original message--
>>>> *From: *August Goers
>>>> *Date: *Wed, Jan 8, 2020 3:48 PM
>>>> *To: *RE-wrenches;
>>>> *Cc: *
>>>> *Subject:*Re: [RE-wrenches] NEC 2020 not available as a portable PDF?
>>>>
>>>> I've heard from multiple sources and confirmed myself that you can't
>>>> get the portable pdf of the NEC starting with the 2020 edition. The link
>>>> that Lorenzo shared seems to indicate that older versions including 2017
>>>> edition are available in a digital format.
>>>>
>>>> [image: image.png]
>>>>
>>>> August
>>>> Luminalt
>>>>
>>>>
>>>> On Wed, Jan 8, 2020 at 12:35 PM Christopher Warfel <
>>>> cwar...@entech-engineering.com> wrote:
>>>>
>>>>> Wrenches,
>>>>>
>>>>> I was told that the NEC 2020 will not be available as a file. You can
>>>>> only access on line, or via the book.  Has anyone confirmed this?  It
>>>>> seems pretty certain.   How many times is one out in the field and
>>>>> needs
>>>>> to reference the NEC?  Now to do so, you will need the book or a
>>>>> connection to the Internet.  I am having a hard time believing that
>>>>> NFPA
>>>>> would be this short-sighted.  Chris
>>>>>
>>>>> ___
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>
>>>>&g

Re: [RE-wrenches] Good Tablets for the Solar Installer

2019-09-19 Thread Martin Herzfeld
Kelly.

Simply, I use my phone for almost everything which is about the size of a
small piece of toast these days with Samsung DeX for with bluetooth full
size keyboard, mouse and HDMI display on my desk.

I am able with DeX to edit a annotate pdfs, presentations, Word, Excel,
micro and dc converter equipment configuration, FLIR attachment for third
party inspections, irradiance, quick augmented reality survey, online
meeting, email and other things.  I have a Suface as secondary,  I  do
most everything
needed and a lot less as well.

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507
* Registered North American Board of Certified Energy Practitioners
(NABCEP) Continuing Education (CE) Provider

On Tue, Sep 17, 2019, 1:08 PM Jerry Shafer  wrote:

> Kelly
> By the time you buy all the extras vs a basic laptop fewer items to carry
> and loose.
> I do programming in Hawaii and California and my Dell still can do e
> everything needed and a lot less money but that's just me "KISS"
>
> On Tue, Sep 17, 2019, 1:02 PM James Rudolph 
> wrote:
>
>> We are transitioning from Dell laptops to Surface Pro's with cell
>> service.
>> The flexibility of these units in the field seems to be unrivaled.
>>
>>
>>
>> *James B. Rudolph*
>>
>> *Hawai'i Unified*
>>
>> *Director of  Energy*
>>
>> *ES Electrician # 10816*
>>
>> *NABCEP Certified PV Installer # 091209-155*
>>
>> *808.594.9969*
>>
>>
>>
>>
>>
>>
>>
>> On Tue, Sep 17, 2019 at 9:14 AM Kelly Larson 
>> wrote:
>>
>>> Esteemed wrenches,
>>>
>>> I am looking to buy a PC tablet/laptop for testing in the field.  I will
>>> be using a Solmetric PVA, Seaward 210 and Survey, excel spreadsheet,
>>> internet, and email.
>>>
>>> I also would like to be able to read and annotate pdfs.
>>>
>>> Suggestions?  What do you use?  What are the advantages and shortcomings
>>> of your device?
>>>
>>> Thank you for your response in advance!
>>>
>>> Kelly
>>>
>>>
>>> ~~~
>>> Kelly Larson
>>> Electrical Engineer
>>> NABCEP Certified PV Installation Professional™
>>> NABCEP Certified PV Installer Specialist™
>>> NABCEP Certified PV Commissioning & Maintenance Specialist™
>>> IREC Certified Master Trainer™/ PV
>>> CA Electrical Contractor# 868189
>>> SolarKelly.com
>>>
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge reliability declining...???

2019-07-25 Thread Martin Herzfeld
Good to know.

1.  I just installed the latest SetApp inverters (the ones without
displays) for a ground-mounted array with the inverter in the dwelling.

2.  The ground-mounted system had to comply with CEC 2016/NEC 2014 690.12
in California because the system was "in the building." Would the inverter
in an indoor or outdoor location be a factor in the failures?

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
https://www.youracclaim.com/badges/a54a49a9-31cb-4f52-b35f-9d7c90630bb9/public_url
Adjunct Professor, Energy, American River College
Contract Training Provider (CTP)

Since 2004. California Solar Contractor License  #00833782  C46, D56, D31,
C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
https://www.youracclaim.com/badges/f23ae19b-0370-4ca1-99d1-418403a8faea/linked_in_profile

* Professional Member, International Association of Electrical Inspectors
* Registered North American Board of Certified Energy Practitioners
(NABCEP) Continuing Education (CE) Provider
https://coursecatalog.nabcep.org/providers/martin-herzfeld


On Wed, Jul 24, 2019, 7:37 AM Howard Arey  wrote:

> Have any of you seen significant declines in SolarEdge inverter
> reliability?
>
> We are having more inverter failures that at any time in the past five
> years of installing SolarEdge. Lots of Code 181 hardware failures mostly in
> the latest SetApp inverters (the ones without displays.)
>
> To compound matters, the RMA process is getting way too long and we are
> waiting appx 3 weeks on average to receive a replacement. Customers
> definitely not happy…
>
> What are you all seeing?
>
>
>
> *Howard “Scot” Arey*
>
> Owner, Solar CenTex
>
> NABCEP Certified PV Installation Professional
>
> 254-300-1228
>
> scot.a...@solarcentex.com
>
>
>
> www.solarcentex.com
>
> https://www.facebook.com/SolarCentex
>
> [image: Solar Centex Logo - No Back]
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] High altitude off-grid systems

2019-04-17 Thread Martin Herzfeld
1. In addition, manufactures provides guidance and altitude considerations
tables for those applications that require operation at high altitudes -
e.g. "altitudes in excess of 6,562 feet (2000 m)" of electromechanical
equipment (contactors and starters) and PV modules

2. For instance, one module manufacture "The installation place should be
less than 1,000m (3280ft) above sea level."  And higher altitude
installations are allowed only if wind pressure is a factor.

BTW, manufactures may not specifically follow NEC 90.9(B) and the dual
system of units :)

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
https://www.youracclaim.com/badges/a54a49a9-31cb-4f52-b35f-9d7c90630bb9/public_url
Adjunct Professor, Energy

California Solar Contractor License  #00833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation

Contract Technical Inspector
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
https://www.youracclaim.com/badges/f23ae19b-0370-4ca1-99d1-418403a8faea/linked_in_profile

* Member, California Solar & Storage Association
* Professional Member, International Association of Electrical Inspectors
#7035507
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Provider



On Tue, Apr 16, 2019, 5:12 PM Jay  wrote:

> For the Radian
> Page 59 of the operators manual ( it’s a different set of environmental
> specifications than the install manual or data sheets)
> 2000m max altitude.
>
> Jay
> Peltz power.
>
> On Apr 16, 2019, at 12:11 PM,  ch...@oasismontana.com> wrote:
>
> Let’s see it in writing, in the manuals included with the components and
> in the online, downloadable manuals.  Clarity is of the essence!
>
>
>
> Chris Daum
>
> Oasis Montana Inc.
>
> 406-777-4309 or 4321
>
> 406-777-4309 fax
>
> www.oasismontana.com
>
>
>
>
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *Lones Tuss
> *Sent:* Friday, April 12, 2019 1:14 PM
> *To:* RE-wrenches 
> *Subject:* Re: [RE-wrenches] High altitude off-grid systems
>
>
>
> Hello All
>
> Outback’s Product Warranty is not based or negated by the altitude of the
> installation.  Altitude ratings ensure full spec operation of the equipment
> up to the stated elevation . As noted in several posts due to thinner air
> cooling of equipment can be affected. Additional cooling may be required
> and or additional products to achieve the necessary load requirements.
>
>
>
>
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *jerrysgarage01
> *Sent:* Friday, April 12, 2019 11:26 AM
> *To:* RE-wrenches 
> *Subject:* Re: [RE-wrenches] High altitude off-grid systems
>
>
>
> Wrenches
>
> Here is the math, well the answer at sea level your body has 14.70 PSI
> exerted on it, at 10,000 feet you only have 10.163 PSI, reduced air
> pressure, reduced cooling or heating ability adjusted for standard sea
> level temp or just over 69%.
>
> I have done work in Hawaii on the big island up at the summit, it can be
> warm and very thin air, without air to cool no inverter will perform very
> well. I have some SMA, FX and Raidians in warm high altitude locations and
> added extra cooling to compensate for the lack of air. You will hear the
> cooling fans spinning faster, moving less air at higher altitudes.
>
> SMA sunny island does have a 9k plus operating altitude but de-rates at
> less the 7k.
>
> Jerry
>
> PV inspector
>
>
>
>
>
>
>
> Sent from my Verizon, Samsung Galaxy smartphone
>
>
>
>  Original message 
>
> From: Jay Pozner 
>
> Date: 4/12/19 10:06 AM (GMT-08:00)
>
> To: RE-wrenches 
>
> Subject: Re: [RE-wrenches] High altitude off-grid systems
>
>
>
>
>
>
>
> We do a fair amount of systems at "altitude".  Recently we had an issue
> with a Radian system at about 10,000'.  An 8048 inverter screaming (fans
> running hard) with just 2000 watts of load.  I hounded tech support for two
> years, and even after switching power modules, etc in the end the techs
> claim a fairly substantial deration (that I can't quote right now) of
> inverter performance because of cooling issues.  We  ultimately added
> another inverter to the system at the end of last summer.  I hope this
> season we will see a better result.   It makes sense, given the difference
> in air density, but I do scratch my head and wonder why we haven't seen
> such issues wit

Re: [RE-wrenches] Ibew is working to exclude C-46 contractor’s from installing Batteries.

2018-03-30 Thread Martin Herzfeld
1.  "... license gives one the ability to do anything, " but maybe not as
well as a solar energy systems *specialty* contractor in California. :)

2.  Experience requirements for both and all may be found here:
http://www.cslb.ca.gov/Contractors/Applicants/Contractors_License/Exam_Application/Experience_For_Exam.aspx

3.  For example, I also have a C-7 (Instrumentation - Monitoring), D31(Pole
Mounts) and D56 (Trenching - Ground-Mounts)

In other words, bump cap, hard hat (helmet), or feather?

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
https://www.youracclaim.com/badges/a54a49a9-31cb-4f52-b35f-9d7c90630bb9/public_url

Adjunct Professor, Energy, American River College

California Solar Contractor License  #00833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation
email: m...@herzfeld.org

Contract PV Systems Inspector
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

Registered North American Board of Certified Energy Practioners (NABCEP)
Continuing Education (CE) Provider

On Mon, Mar 26, 2018, 5:01 PM James Rudolph 
wrote:

> Aloha All,
> Does anybody know the requirements for the C-46? I would assume if you
> could qualify for that ( C-46) you could also qualify for a C-10 (C-13
> Hawaii).
> The full license gives one the ability to do anything, and this seems like
> the way to go for versatility. "If you can't beat'em...join them."
>
> *C-10 - Electrical Contractor*
>
> An electrical contractor places, installs, erects or connects any
> electrical wires, fixtures, appliances, apparatus, raceways, conduits,
> solar photovoltaic cells or any part thereof, which generate, transmit,
> transform or utilize electrical energy in any form or for any purpose.
>
>

>
>
> *C-46 - Solar Contractor*
>
> A solar contractor installs, modifies, maintains, and repairs thermal and
> photovoltaic solar energy systems. A licensee classified in this section
> shall not undertake or perform building or construction trades, crafts, or
> skills, except when required to install a thermal or photovoltaic solar
> energy system.
>

What is needed to qualify:


http://www.cslb.ca.gov/Contractors/Applicants/Contractors_License/Exam_Application/Experience_For_Exam.aspx


>
>
> *James B. Rudolph*
>
> *Hawaii Unifed*
>
> *Director of  Energy*
>
> *ES Electrician # 10816*
>
> *NABCEP Certified PV Installer # 091209-1*
>
>
>
>
>
>
> On Fri, Mar 23, 2018 at 3:02 PM, Jason Andrade <
> ja...@westcoastsustainables.com> wrote:
>
>> Hi at this point I believe this is a California only issue, but I was
>> contacted by CalSeia today and was asked to be involved in a discussion
>> regarding a move where only a C-10 contractor can install a battery based
>> system
>> This was news to me but they sent me a pdf outlining the issue and I will
>> read it over this weekend has anyone else heard about this?
>> My instant response is what special training does the c10 have that the
>> c46 doesn’t ?
>> Jason Andrade
>> West Coast Sustainables
>>
>> Sent from my iPhone
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Covering modules

2017-12-23 Thread Martin Herzfeld
1. NEC 690.18 was removed from the Code in 2017 and an "opaque covering"
for Installation and Service of an Array.

2.  Light to the underside of the array is still an issue too for a
ground-mount - albedo. Try this in sunlight on a windy day? :)

I'd also suggest "treating everything as if it were hot."

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
https://www.youracclaim.com/badges/a54a49a9-31cb-4f52-b35f-9
d7c90630bb9/public_url
Adjunct Professor

California Solar Contractor License  #00833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation

Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

Registered North American Board of Certified Energy Practioners (NABCEP)
Continuing Education (CE) Provider

On Dec 23, 2017 11:52 AM,  wrote:

I always thought this was a waste of time, waste of materials, and gives a
false sense of security.   I have had the crap shocked out of me while
trying to hurry and finish up string connections in a combiner box when it
was almost dark and could barely see so now I never assume near darkness
means it’s safe on higher voltage strings.

Was trying to avoid having to make another trip to finish.  These days we
make sure positive leg of each string is blocked off at combiner before
starting the module mounting and connecting as we go.  This way we always
know to treat everything as if it’s hot.



Sent from my iPad
Jeff Yago
DTI Solar. Inc.
804-457-9566
jry...@dtisolar.com


> On Dec 23, 2017, at 11:04 AM, Jay  wrote:
>
> Hi All, happy holidays.
>
> I’m looking for any studies or data about the dangers of “covering
modules” and assuming they are safe to work on.
>
> I have a group that I think is going to need some harder data than me
telling them it’s not safe.
>
> Thanks
>
> Jay
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or
g/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or
g/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread Martin Herzfeld
Has anyone worked with them with a Sunny Island?  Space is not an issue for
this client.

Martin Herzfeld, IREC Certified Master Trainer ™ for PV Installation
Professional #IREC 10037
California Solar Contractor License  #00833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation

UL Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #C0068034
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

Registered NABCEP Continuing Education (CE) Provider


On Jul 20, 2016 2:00 PM, "Jerry Shafer"  wrote:

We had a customer request them but once we found out how many it would
take, he decided on the deka unigee instead. l dont like running my OB's at
such a low voltage as they seem to get hotter due to the higher current.
Some of our other product lines don't even reccomend aquions due to that
low voltage, suggest asking your inverter manufacture too.

On Jul 20, 2016 10:52 AM, "Drake" 
wrote:

> Hello Wrenches,
>
> I have a client who is going to take the plunge and buy a set of Aquion
> Batteries. They look pretty good on paper, but I'm not sure how well an
> inverter would function at the 40 V minimum. Does anyone have experience to
> recommend them or warn against using them?
>
> Thanks,
>
> Drake
>
> Drake Chamberlin
>
>
>
>
>
> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
> Solar PV 740-448-7328 <740-448-7328> *http://athens-electric.com/
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 40 series DC disconnect

2016-12-16 Thread Martin Herzfeld
2014 NEC 690.18 is now removed in NEC 2017?

Martin Herzfeld, IREC Certified Master Trainer ™ for PV Installation
Professional #IREC 10037
Contract Training Provider (CTP)
California Solar Contractor License  #00833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation

Contract PV Technical Inspector
Roof & Ground Mounted Solar PV Systems
Licensed Contractor & Consultant - Since 2004
BBB Accredited Business
Email: m...@herzfeld.org

UL Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #C0068034
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

Martin Herzfeld is a registed NABCEP Continuing Education (CE) Provider


On Dec 15, 2016 1:09 PM,  wrote:

William,



I was also surprised to see SMA go down this road (ala Fronius IG). I can’t
speak to why they did this. I’m installing my first 40 series right now.



I have never supported covering the array as a viable method of removing
voltage. It is far safer to unplug the strings on the roof if you want to
remove voltage. Not sure why they did not suggest unplugging instead of
tarping.



Either way, many jurisdictions will require an external dc disconnect with
this new configuration—what a waste. If SMA were smart, they would put
connectors in their dc connection box to be compliant with the 2017 NEC
which would solve their problem. It means a design change. They must be
expecting this product to be connected to a rapid shutdown switch
box—that’s the only thing that makes sense.



Bill.





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *William Miller
*Sent:* Wednesday, December 14, 2016 10:45 AM
*To:* RE-wrenches 
*Subject:* Re: [RE-wrenches] SMA 40 series DC disconnect



Bill:



That is exactly my point.  Carports and ground-mounts do not need RS, but
any system requires safe means to disconnect DC.  So how do you accomplish
this with the 40 series?



Sure, using the DC connector is one way to disconnect the DC input to the
40 series electronics.  However, the service manual cautions against this.
Below is the verbatim text from the manual.



>From SMA Document SB30-77-1SP-US-40-AT-PU-SG-xx-11 Service Manual:



• If an external DC disconnecting switch is available, open the external DC
disconnecting

switch.

• If there is no external DC disconnecting switch, cover the PV modules
with opaque

material (e.g. foil).

• Ensure that there is no voltage on the DC conductors of the PV array.

• Wait five minutes before working on the inverter.

• Leave the *DC-in *connecting terminal plate plugged into the Connection
Unit and only

touch it on the black enclosure.



I was told that the term ‘foil’ is a poor translation from German, and
likely means a tarp.  In any event, this verbiage is quite unfortunate as
it precludes using the connector as a disconnect.  I wonder if there is
some criteria on what kind of connectors can be used as a disconnecting
means and which cannot.  I am sure it has something to do with ‘touch-safe’
requirements.  The DC connector in the 40 series may not meet this
criteria.  The external leads could possibly come free of the connector
body as they are just insert-connected.  I would be very reticent to send
out a technician to work on one of these without some serious consideration
of the implications.



SMA seems like they are interested in this conundrum and I am withholding
judgement pending receiving a response from them.  I just thought it very
curious that they moved the location of the disconnect in the DC power flow
scheme.   Seems to me like a fundamental change that flew under the radar.
See below for a rendering of the change in DC power flow:



Formerly:  PV--àIntegrated Disconnectàchassis separation



40 Series:  PV àchassis separation--àIntegrated Disconnect





William



PS:  I remember wasting an entire afternoon in a conference room in San
Diego arguing with Fronius about the same concept.  They too insisted that
to service the IG series inverter one had to just tarp the modules.  Let us
please put that myth to rest once and for all:  Tarping modules is not
viable.



Wm





[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600 <(805)%20438-5600>



*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *billbroo...@sbcglobal.net
*Sent:* Wednesday, December 14, 2016 7:40 AM
*To:* 'RE-wrenches' 
*Subject:* Re: [RE-wrenches] SMA $0 series DC disconnect



William,



I’m not sure you meant to imply this, but carports and ground mounts do not
need any RS equipment unless you were to bring the dc conductors into a
building, which would not be smart.



The 2017 NEC allows connectors to be used as isolation devices for
equipment as long as the circuit current is below 30 amps, which it always
is on individual strings. I realize California will not be on t

Re: [RE-wrenches] traveling with digital meters

2015-11-19 Thread Martin Herzfeld
I typically travel in the US and I carry on my meters by placing them in a
separate bag all together in a separate bin.

1. "When in doubt, leave it out"  as found here:
http://www.tsa.gov/data/guide/PackSmart.html

2.  By the way, on my most recent trip, a passenger sat next to me knitted
with knitting needles.

All the best,

Martin Herzfeld, IREC Certified Master Trainer ™ for PV Installation
Professional #IREC 10037
California Solar Contractor License  #833782  C46, D56, D31, C-7
Solar, Trenching, Pole Installation & Maintenance, Instrumentation
Roof & Ground Mounted Solar PV Systems
Licensed Contractor & Consultant - Since 2004
Contract PV Technical Inspector
BBB Accredited Business

UL Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #C0068034
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

NABCEP Advanced Continuing Education (CE) Training Provider for
Certification and Recertification Classes in Solar (PV) Technology
On Nov 9, 2015 4:40 PM, "Dan Fink"  wrote:

> Hi Jay - I was busted for the probes in Canada. Too sharp. Fortunately it
> was a tiny airport and my checked bags were right outside on the tarmac, so
> the nice Air Canada lady went out and put the probes in.
> So now I check the probes, and carry on the meter.
>
> Dan Fink
> Adjunct Professor, Ecotech Institute
> IREC Certified Instructor™ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Accredited Continuing Education Providers™
> 970.672.4342
>
>
>
> On Mon, Nov 9, 2015 at 4:49 PM, jay  wrote:
>
>> Hi All,
>>
>> I believe this was talked about in the past, but I can’t find it.
>>
>> I’m going to be traveling out of the country with a clamp on w/probes
>>
>> And curious if I should/can check this or carry it on?
>>
>> thanks
>>
>> jay
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UL 1703 coming to California

2015-01-01 Thread Martin Herzfeld
FYI - Also additional information is here too ... :
http://productspec.ul.com/ <http://productspec.ul.com/index.php>

Martin Herzfeld
California Solar Contractor License  #833782
C46, C-7, D31, D56
Trenching Contractor, Pole Installation & Maintenance, Instrumentation

UL Certified PV Installer #17, OSHA 30
Principal Contract Solar Technical Inspector
OSHA-Authorized Construction Trainer #C 0068034
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
Project Contractor & Consultant

Telephone & Text: 510.243.0190

August,

Here's some additional info:

http://solarprofessional.com/articles/design-installation/fire-classification-for-roof-mounted-pv-systems?v=disable_pagination

Best regards,

David Brearley
Senior Technical Editor, *SolarPro* magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com
Direct: 541.261.6545

Check out this AMAZING music video tribute to SolarPro:
http://bit.ly/1qfMCCh

On Dec 9, 2014, at 7:50 AM, re-wrenches-requ...@lists.re-wrenches.org wrote:


>
>
> >
> >
> > >
> > > > Send RE-wrenches mailing list submissions to
> > > > re-wrenches@lists.re-wrenches.org

> > > >
> > > > To subscribe or unsubscribe via the World Wide Web, visit
> > > >
http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>
> > > > or, via email, send a message with subject or body 'help' to
> > > > re-wrenches-requ...@lists.re-wrenches.org

> > > >
> > > > You can reach the person managing the list at
> > > > re-wrenches-ow...@lists.re-wrenches.org

> > > >
> > > > When replying, please edit your Subject line so it is more specific
> > > > than "Re: Contents of RE-wrenches digest..."
> > > > When responding to posts within the Digest, be sure to restore the
Subject: line to the original, and please edit out any extraneous lines
from the quoted message.
> > > > Today's Topics:
> > > >
> > > >   1.  UL 1703 coming to California - anyone ready? (August Goers)
> > > >   2. Re: UL 1703 coming to California - anyone ready? (August Goers)
> > > >   3. Re: UL 1703 coming to California - anyone ready? (Glenn Burt)
> > > >   4. Re: Magnum Back Plates (Baxter, Gary)
> > > >
*> > > > From:* August Goers 
*> > > > Subject:** [RE-wrenches] UL 1703 coming to California - anyone
ready?*
*> > > > Date:* December 8, 2014 5:07:54 PM CST
*> > > > To:* RE-wrenches 
*> > > > Reply-To:* RE-wrenches 
> > > >
> > > >
> > > > Hi All California Wrenches,
> > > >
> > > >
> > > >
> > > > As far as I understand, UL 1703 goes into law in California on Jan
1, 2015 and will require new fire rating classifications for many projects.
Is anyone else currently planning what racking and modules they will be
using to meet these requirements? I’ve been trying to get my head around
this for a while now and I’m having a hard time finding substantial
information from both racking and module manufacturers.
> > > >
> > > >
> > > >
> > > > A little info:
> > > >
> > > >
> > > >
<http://osfm.fire.ca.gov/informationbulletin/pdf/2014/IB14002PVFireClassification.pdf>
> > > >
http://osfm.fire.ca.gov/informationbulletin/pdf/2014/IB14002PVFireClassification.pdf
<http://osfm.fire.ca.gov/informationbulletin/pdf/2014/IB14002PVFireClassification.pdf>
> > > >
> > > >
> > > >
> > > > Best,
> > > >
> > > >
> > > >
> > > > August
> > > >
> > > >
> > > >
> > > > Luminalt
> > > >
> > > >
> > > >
> > > >
*> > > > From:* August Goers 
*> > > > Subject:** Re: [RE-wrenches] UL 1703 coming to California - anyone
ready?*
*> > > > Date:* December 8, 2014 6:48:34 PM CST
*> > > > To:* RE-wrenches 
*> > > > Reply-To:* RE-wrenches 
> > > >
> > > >
> > > > All –
> > > >
> > > >
> > > >
> > > > Bill Brooks wrote back to me and shared a draft NREL whitepaper on
fire performance of PV systems he wrote. If you are interested, please
contact me off list and I will share it with you (he said it was okay to
share).
> > > >
> > > >
> > > >
> > > > Best,
> > > >
> > > >

Re: [RE-wrenches] PV panel backing

2014-09-01 Thread Martin Herzfeld
I concur with Dan.  Unless a controlled environment, a patch job on a
module with a customer is wrong on so many levels.

Martin Herzfeld
California Solar Contractor License  #833782
Trenching Contractor, Pole Installation & Maintenance, Instrumentation

UL Certified PV Installer #17, OSHA 30
Principal Contract Solar Technical Inspector
OSHA-Authorized Construction Trainer
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
Project Contractor & Consultant

Telephone & Text: 510-243-0190

Ron,

It's been my experience the only adhesives that work reliably on PV
backsheets are those designed for the purpose, such as Dow 804 et. al..
Substances such as silicone sealant, tool polymerics, and others will
appear to be suitable when first applied, but they eventually peel loose
over a period of 1-5 years.

Issue #2: Heat of sufficient temperature to melt the backsheet may also
have been hot enough to affect solder joints on and among the cells.
Crystallized solder connections will conduct current, but are more
resistive, and eventually will degrade due to heating and cooling, leading
to overheating and eventual failure.  Then too there's a possibility of
micro-fractures created in the cells due to the heat, which take time to
become apparent, but will also cause a PV module to quit working .. or at
least quit working at its rated specifications.

Issue #3:  When PV are manufactured, the layers at a minimum are
manufactured from tempered glass, EVA, cells and buss, EVA, then the
backsheet (tedlar, kevlar, etc.), in that order.  The module is assembled
under conditions of heat and vacuum.  With the backsheet melted, the
environmental integrity of the laminate has been compromised, allowing
ambient humidity into the PV.  While it may be functional now, long-term
prospects for continued proper operation are questionable at best.

Unless there's a pressing reason to try to salvage the module, it's better
to replace it.

Dan Lepinski


On Sun, 8/31/14, Ron Young  wrote:

Subject: [RE-wrenches] PV panel backing
To: "RE-wrenches" 
Date: Sunday, August 31, 2014, 6:32 AM

Hello Wrenches,

I have an installation of 165w PV on a pole mount that was exposed to a
fire from the rear when the customers shop burned. 6 of the 10 panels
survived with only replacement of the MC4 plugs required but one of the
panels that is still functioning had the rear coating melted off. The cells
and electrical grid still function. Can anyone recommend a replacement
coating that may salvage this panel for a few more years. I know if left
exposed it will soon deteriorate but am wondering if some kind of commonly
available non conductive rubberized or latex type of coating might do the
job?

Ron Young

___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown for pole mounts

2014-05-02 Thread Martin Herzfeld
In other words, for ground-mounts, in accordance with 2014 NEC 690.12(1),
would it be okay to run the DC conductors not inside, but on the side of
the building "5" feet directly to the inverter?

Martin Herzfeld
California Solar Contractors License  #833782
Trenching Contractor, Pole Installation and Maintenance, Instrumentation

UL Certified PV Installer #17, OSHA 30
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
OSHA-Authorized Construction Trainer

Telephone & Text: 510-243-0190

Martin Herzfeld is an Accredited Business of the BBB since 2008.

Aaron,

An exterior utility service panel with an underground service lateral is not
considered in or on the building.

Keep the dc conductors off of the building and you will be fine with a
ground-mounted PV system. Don't bring them inside the building, and don't
run them along the exterior of the building.

The whole requirement is to deenergize conductors that a firefighter might
come in contact with while fighting a fire. The most important conductors
are those inside the building. A PV array on top of a buiding is also
required to deenergize the conductors within 10 feet of the array (PV Output
Circuit Conductors). The array is allowed to remain at full voltage.

Bill.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Aaron
Mandelkorn
Sent: Friday, April 18, 2014 1:35 PM
To: RE-wrenches
Subject: [RE-wrenches] Rapid shutdown for pole mounts

The rapid shutdown language is so confusing. When looking at the rapid
shutdown language, does PV systems "on" a building refer to only situations
where the array is on a building; or does it include DC conductors as well.
For example, if the DC conductors from a pole mounted array run up the side
of a building before punching in to the inverter, does this require rapid
shutdown?  Is this PV system considered "on" a building?

Aaron

Aaron Mandelkorn
Owner/Solar Specialist
Renewable Energy Outfitters
719-221-5249
970-596-3744
www.reosolar.com
reoso...@gmail.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

---
This email is free from viruses and malware because avast! Antivirus
protection is active.
http://www.avast.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] CA Fire code

2014-01-09 Thread Martin Herzfeld
1.  In addition to the thoughts shared, for instance, for one AHJ:

(A) I think "Photovoltaic Installations west of Interstate 280 require PV
modules to have a minimum Class A fire rating" - requirements and
'additional information' since 2009 were revised and updated here ...?

http://www.cityofpaloalto.org/gov/depts/utl/residents/resources/pcm/pv_permitting_and_interconnection.asp

(B) Also ground-mount options - not only just rooftops - CSFM Guidelines
Section 5.0, ...

http://www.cityofpaloalto.org/civicax/filebank/documents/34052
http://osfm.fire.ca.gov/informationbulletin/pdf/2012/IB_12-004_FireApparatusAccessRoadsPhotovoltaicFacilities.pdf
http://osfm.fire.ca.gov/training/pdf/Photovoltaics/Fire%20Ops%20PV%20lo%20resl.pdf

You may first check with the specific jurisdiction for more information ...

2.  In addition, you may want to join or attend the IAEI meetings in
California, there's good information on this and other topics at the
monthly meetings and CEUs.

http://www.iaei.org

3.  By the way, I attended at the very last stakeholder meeting in SF and
the publications here for new changes and updates ...

http://www.solarabcs.org/about/publications/reports/flammability-testing/index.html

4. Wildland Hazard/Building Codes

http://www.fire.ca.gov/fire_prevention/fire_prevention_wildland_zones.php

We'll check it out on an install, if in the area ...

Martin Herzfeld
California Contractor License  #833782
UL Certified PV Installer #17, OSHA 30
Certified Technical Classroom Trainer (CTT+)
OSHA-Authorized Construction Trainer

Wrenches,
If you are in a wild land fire zone in CA, it looks like we are all in for
a rude awakening. Our local AHJ is requiring not only set backs for
ventilation of roofs, but also THAT ALL PANELS ON THE ROOF CARY A CLASS A
FIRE RATING! It doesn't take allot of research to realize that this pretty
much eliminates roof-top solar as an option, as if you can eve find a class
A panel, they are cost prohibitive. I'm wondering a couple things. One, has
anyone had luck using the local political process to postpone the
enforcement of the class A requirement? and two, has anyone found readily
available Class A modules?
  This issue seems to have caught the industry with it's pants down, as
industry lobby doesn't even seem to be aware that the the local AHJ's would
have this interpretation. Is this the end of roof top solar in 60% of
California? What are y'all doing to deal with this issue?

--

Lars Ortegren

President

California Solar Electric Company

.PO Box 480

149 E.Main St

Grass Valley, CA 95945

Phone : (530)274-3671 Fax: (530)274-7518

 California C-10 Electical Contractor #779624

Certified NABCEP Continuing Education Provider

Certified NAPCEP Technical Sales and Installation Profesional

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Advanced PV Training Recommendations

2013-04-25 Thread Martin Herzfeld
By the way, I think there was also input to the UL PV Installer
Certification announced here:
http://lms.ulknowledgeservices.com/common/ncsresponse.aspx?rendertext=pvinstaller_pressrelease
On Apr 23, 2013 8:34 AM, "Andrew Truitt"  wrote:

>
> Eric - Check out IREC's Solar Instructor Training Network 
> (SITN)<http://www.sitnusa.org/>.
> They also have an associated free on-line companion course geared towards
> code officials called the Photovoltaic Online Training Course 
> (PVOT)<https://www.nterlearning.org/web/guest/course-details?cid=402>.
> The PVOT course was developed by IREC with input from Brooks Engineering.
>
>
> For a brighter energy future,
>
>
> Andrew Truitt
> NABCEP Certified PV Installation Professional™ (ID# 032407-66)
>
> Principal
> Truitt Renewable Energy Consulting, LLC
>
> (202) 486-7507
>
> LinkedIn Profile <http://www.linkedin.com/pub/andrew-truitt/8/622/713>
>
> Company Website <http://truittreconsulting.weebly.com/>
>  <%28202%29%20486-7507>
>
>
>
>
> "Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
> to fission. And it just so happens that there's an enormous fusion reactor
> safely banked a few million miles from us. It delivers more than we could
> ever use in just about 8 minutes. And it's wireless!"
>
> ~William McDonough
>
>
>
>
>
>
>
> On Mon, Apr 22, 2013 at 3:10 PM, Martin Herzfeld 
> wrote:
>
>> "But, as you all know, there are always more details to master, code
>> issues to be clarified, and new technologies coming down the pike."
>>
>> 1. Specifically, not only practical safeguarding code issues, but also
>> the I codes and standards, - CEC, CBC, ... there are courses with the ICC
>> 2013 TriChapter IAEI Events which included advanced fire-stopping,
>> PV plan-check and permitting workshops and updates, CalGreen code,Energy
>> ...
>>
>> 2. There are other options with certification - or 'feathers' in the ANSI
>> Z89 hardhat.  In California, you are required to have a contractors license
>> in accordance to B&P code - if not this happens -
>>
>> 3. In other words, the license is the hat and certification is the
>> 'feather.' The license itself is also certification.
>>
>> 4. With an OSHA 30 certificate, I'd suggest also adding some new feathers
>> for OSHA safety health and environmental specifically applicable to our
>> trade: http://osha4you.com/courses/osha-courses-by-industry  "Hands-on
>> and hands-off" construction courses at Sacramento at the safety center. The
>> trainers have more than 25+ years of experience.
>>
>> 5. There's also the UL PV Installer Certification with the International
>> Brotherhood of Electrical Workers (IBEW),  offering UL's Photovoltaic (PV)
>> Installer Certification to IBEW members and the National Electrical
>> Contractors Association (NECA) - may be difficult to qualify and complete -
>> I think there are now more than 30 +
>>
>> 6. Some differences in the certification models as discussed here:
>> http://nti.njatc.org/Portals/3/C%20Group/2012%20NTI%20UL%20PV%20Certification.pdf
>>
>> 7. By the way, if you are looking for an Advanced Photovoltaics Course in
>> Sacramento 3 days for free ~$0.00? I'd suggest consider
>> https://usage.smud.org/etcstudent/ClassDescription.aspx?Id=814 this year
>> with Bill Brooks of Brooks Engineering?
>>
>> 8. I agree - there's more to a license and certification than submitting
>> a writing sample.
>>
>> >
>> The MREA (Midwest renewable energy association) offers classes, some
>> on-line now. Really good Instructors.
>>
>> www.midwestrenew.org
>>
>> Jesse
>>
>> Sent from my iPhone
>>
>> On Apr 12, 2013, at 8:03 PM, jay peltz  wrote:
>>
>> > HI Eric,
>> >
>> > I'm going to advise you to look at SEI
>> > Solar energy international.
>> >
>> > http://www.solarenergy.org/
>> >
>> > Full disclosure, I teach part time from them.
>> >
>> > Cheers,
>> >
>> > jay
>> >
>> > peltz power
>> >
>> > On Apr 12, 2013, at 12:46 PM, SunHarvest wrote:
>> >
>> >> Wrenchers -
>> >>
>> >> I am in need of hands-on advanced training for my own continuing
>> education. I have a California C46 solar contractor's license and plenty of
>> experience designing and installing systems. But, as you all know,
>

Re: [RE-wrenches] Advanced PV Training Recommendations

2013-04-22 Thread Martin Herzfeld
"But, as you all know, there are always more details to master, code issues
to be clarified, and new technologies coming down the pike."

1. Specifically, not only practical safeguarding code issues, but also the
I codes and standards, - CEC, CBC, ... there are courses with the ICC 2013
TriChapter IAEI Events which included advanced fire-stopping,
PV plan-check and permitting workshops and updates, CalGreen code,Energy
...

2. There are other options with certification - or 'feathers' in the ANSI
Z89 hardhat.  In California, you are required to have a contractors license
in accordance to B&P code - if not this happens -

3. In other words, the license is the hat and certification is the
'feather.' The license itself is also certification.

4. With an OSHA 30 certificate, I'd suggest also adding some new feathers
for OSHA safety health and environmental specifically applicable to our
trade: http://osha4you.com/courses/osha-courses-by-industry  "Hands-on and
hands-off" construction courses at Sacramento at the safety center. The
trainers have more than 25+ years of experience.

5. There's also the UL PV Installer Certification with the International
Brotherhood of Electrical Workers (IBEW),  offering UL's Photovoltaic (PV)
Installer Certification to IBEW members and the National Electrical
Contractors Association (NECA) - may be difficult to qualify and complete -
I think there are now more than 30 +

6. Some differences in the certification models as discussed here:
http://nti.njatc.org/Portals/3/C%20Group/2012%20NTI%20UL%20PV%20Certification.pdf

7. By the way, if you are looking for an Advanced Photovoltaics Course in
Sacramento 3 days for free ~$0.00? I'd suggest consider
https://usage.smud.org/etcstudent/ClassDescription.aspx?Id=814 this year
with Bill Brooks of Brooks Engineering?

8. I agree - there's more to a license and certification than submitting
a writing sample.

>
The MREA (Midwest renewable energy association) offers classes, some
on-line now. Really good Instructors.

www.midwestrenew.org

Jesse

Sent from my iPhone

On Apr 12, 2013, at 8:03 PM, jay peltz  wrote:

> HI Eric,
>
> I'm going to advise you to look at SEI
> Solar energy international.
>
> http://www.solarenergy.org/
>
> Full disclosure, I teach part time from them.
>
> Cheers,
>
> jay
>
> peltz power
>
> On Apr 12, 2013, at 12:46 PM, SunHarvest wrote:
>
>> Wrenchers -
>>
>> I am in need of hands-on advanced training for my own continuing
education. I have a California C46 solar contractor's license and plenty of
experience designing and installing systems. But, as you all know,
there are always more details to master, code issues to be clarified, and
new technologies coming down the pike. I'd like to focus on off-grid and
on-grid w/BB systems over straight grid-tie.
>>
>> I'm looking at Solar Living Institute as that's here in NorCal, where I
live.
>>
>> Are there any training schools/programs that you guys would recommend?
>>
>> My main requirements are that the instructor has 20+ years of hands-on
experience and that the training is hands-on and fully comprehensive. I am
interested in getting NABCEP certified but I'm more concerned with getting
professional, in-depth training than with qualifying for NABCEP exam
requirements.
>>
>> Thanks!
>>
>> Eric
>> SunHarvest
>>
>>
>> - Original Message -
>>>
>>> From: John Berdner
>>> To: RE-wrenches
>>> Sent: Thursday, April 04, 2013 11:44 AM
>>> Subject: Re: [RE-wrenches] Combining conductors
>>>
>>> Larry:
>>>
>>> Yes, you can parallel conductors (there is an NEC limit on minimum size
allowed to parallel).
>>> You just add the ampacity of the two conductors.
>>> To convince yourself you can also check Table 8 Conductor Properties
and sum the cross sectional areas of all the parallel conductors to see the
equivalency to a single larger conductor.
>>>
>>> Best Regards,
>>>
>>> John Berdner
>>> General Manager, North America
>>>
>>> SolarEdge Technologies, Inc.
>>> 3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new
address.)
>>> T: 510.498.3200, X 747
>>> M: 530.277.4894
>>>
>>> From: re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher,
Starlight Solar Power Systems
>>> Sent: Thursday, April 04, 2013 9:51 AM
>>> To: RE-wrenches
>>> Subject: [RE-wrenches] Combining conductors
>>>
>>> Wrenches,
>>>
>>> Here's a tough one for me to understand. I am installing 2 volt AGM
batteries. There are two terminals for each battery polarity. I have some
height limits so I need to use the minimum wire size. Here's my question:
If I combine two identical conductors, what is the equivalent single
conductor size?
>>>
>>> I found one "rule of thumb" that says doubling like conductors creates
a AWG decrease of 3. Example: two #2 will be equivalent to 2/0. Is this
true?
>>>
>>> Thank you,
>>>
>>> Larry Crutcher
>>> Starlight Solar Power Systems
>>>
>>>
>>>
>>>
>>>
>>>
>>> CONFIDENTIALITY NOTICE: This e-mail and 

Re: [RE-wrenches] AHJ's & NABCEP

2013-02-11 Thread Martin Herzfeld
They are different.

1. The license distinguishes the qualified from the unqualified and
the license qualifier is allowed to practice in the jurisdiction. A
qualified person is also defined in NEC Article 100. The definition of
AHJ may not be as many think as defined in NEC Article 100.

2. As an employee is different from an independent contractor, the
certification resources may become one set of resources to study to
qualify for a license.

3. Some states are different than others.
http://www.nascla.org/licensing_information

4. However, other certifications provide further distinction as the
qualifier. There's another certification targeted to contractors, ...

martinHerzfeld
California Licensed Solar Contractor #833782
UL Certified PV Installer #17
CTT+ Certified Trainer

On Feb 2, 2013 5:23 PM, "Maverick Brown"  wrote:
>
> I would go by state law.
>
> I'll be frank. NABCEP and licensed electrical work are almost incongruous, 
> but are certainly separate.
>
> I am closer to being an electrician and will be glad when my electrical 
> engineering degree and NABCEP cert will be useful. ;-)
>
> I hope the future will have NABCEP working with states to better integrate 
> the knowledge of solar with electrical work.
>
>
> Thank you,
>
> Maverick
>
>
> Maverick Brown
> BSEET, NABCEP Certified Solar PV Installer ®
> President & CEO
> Maverick Solar Enterprises, Inc.
> Office: 512-919-4493
> Cell:512-460-9825
>
> Sent from an iPhone.
>
> On Feb 2, 2013, at 6:15 PM, Ian Eastman  wrote:
>
>> Hi Re-wrenchers,
>> Does anyone know where to find some good information on talking to your 
>> local AHJ concerning using the NABCEP cert. for a Solar Contracting License? 
>> Arguments, facts...?
>> Thanks,
>> Ian
>>
>> --
>> Ian Eastman | Installation/Project Management
>> GO SOLAR!
>> Cell: 307.413.6789  •  i...@cesolar.com
>> Creative Energies
>> Victor, ID office 208.354.3001
>> Lander, WY office  307.332.3410
>> Salt Lake City, UT office 801.487.6489
>> www.CreativeEnergies.biz
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org