resurrecting an old system

2013-11-20 Thread Todd - Work
I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread RFletcher
Do an air test, fix the obvious stuff that's broken, buy a new pump and 
flush/test the existing pipe with water. An air test will get most big leaks 
it's pretty hard to find little pin hole leaks using air if it is a large 
volume system. My 2 cents.

Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 6:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Craig.Prahl
Scott, you understand my concerns.  Unfortunately this is a challenging client 
and you better have any requirement opinion backed up with documentation 
otherwise it's just an opinion for what that's worth.



Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A 
Futrell
Sent: Tuesday, November 19, 2013 8:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

No code restrictions, but certainly foam systems concerns.  55 gallon drums to 
second floor with stairs?  Bladder tanks?  Lay 'em down to replace bladder that 
gets torn.  Craig, am I missing something?  If not, I've seen this before and 
it gets ugly real fast.  I've worked on an existing hanger that they buried the 
big tanks in a corner, tore the bladder and have to cut the roof open to lift 
them out, to lay it down, to replace it.

Scott Futrell
 
(763) 425-1001 x12 Office
(612) 759-5556 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Tuesday, November 19, 2013 3:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Location of foam system valve room on 2nd floor - permitted?

I've got a real-estate problem.  I have an Industrial process structure which 
requires a second fire protection valve room for a supplementary foam system 
consisting of 6 deluge risers and foam concentrate tank.  Owner says there's no 
room around the building so stack it on top of the existing fire sprinkler 
riser room.  This is a high hazard operation.  

While I'm digging through codes I was wondering if anyone here knew off the top 
of their head any specific code prohibitions to their idea?

I need chapter and verse to show them if it's not permitted or recommended.

Thanks,

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Scott A Futrell
Do they have maintenance personnel that can assist you?  I really have had the 
same problem, but when you get the guys that have to work on it involved they 
can provide some welcome support.

Good luck.

Scott
 
(763) 425-1001 Office
(612) 759-5556 Cell

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Wednesday, November 20, 2013 7:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

Scott, you understand my concerns.  Unfortunately this is a challenging client 
and you better have any requirement opinion backed up with documentation 
otherwise it's just an opinion for what that's worth.



Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A 
Futrell
Sent: Tuesday, November 19, 2013 8:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

No code restrictions, but certainly foam systems concerns.  55 gallon drums to 
second floor with stairs?  Bladder tanks?  Lay 'em down to replace bladder that 
gets torn.  Craig, am I missing something?  If not, I've seen this before and 
it gets ugly real fast.  I've worked on an existing hanger that they buried the 
big tanks in a corner, tore the bladder and have to cut the roof open to lift 
them out, to lay it down, to replace it.

Scott Futrell
 
(763) 425-1001 x12 Office
(612) 759-5556 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Tuesday, November 19, 2013 3:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Location of foam system valve room on 2nd floor - permitted?

I've got a real-estate problem.  I have an Industrial process structure which 
requires a second fire protection valve room for a supplementary foam system 
consisting of 6 deluge risers and foam concentrate tank.  Owner says there's no 
room around the building so stack it on top of the existing fire sprinkler 
riser room.  This is a high hazard operation.  

While I'm digging through codes I was wondering if anyone here knew off the top 
of their head any specific code prohibitions to their idea?

I need chapter and verse to show them if it's not permitted or recommended.

Thanks,

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread Scott A Futrell
I like the replace it all option...
How old is the system to start with?
You need to replace all the sprinklers, if some have popped you don't know 
how many others may be damaged.
What about gaskets in grooved couplings?
Is the water supply now equal to the original pump and pond? If not, pipe size 
changes, right?
You could minimize the liability by replacing everything...

Scott
 
(763) 425-1001 Office
(612) 759-5556 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 7:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Misc storage and QR sprinkler deduction

2013-11-20 Thread Todd - Work
I am working on a school project where there is a basement that will be used 
for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high 
storage of miscellaneous stuff, which I am calling Class IV. This would be a 
0.20/1500 sprinkler density, which is the same as the requirement for OH2. 
Since I have a marginal water supply and am at the far end of the system, 
minimizing the design is critical. 

My question is this; can I use the RA deduction for QR heads in OH2 with the 
curves for low piled storage? Or does the fact that this is storage negate that 
reduction?

Must be my day for question



Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Mark A. Sornsin, P.E.
Just to reiterate Scott's point:  Maintenance is huge and his examples are 
extremely valid.  We were once painted into a corner on our first foam job many 
years ago.  The foam tanks were put on a mezzanine above the risers.  But we 
ensured there was plenty of room on the mezzanine for bladder removal, and 
double doors on the exterior wall of the mezzanine for better access to 
remove/replace bladders or tanks (via fork lift). Not ideal, but serviceable.

(BTW - my favorite example of lack of maintenance foresight is a foam job (by 
others) which included a vertical bladder tank located below a second level - 
with about 2 ft. of clearance above the tank. When the bladder needs 
replacement, the entire tank will have to be disconnected and removed from the 
building.  There may also be some other piping that needs removal to allow this 
to happen. Of course, this is a non-issue if you simply blow-off 
maintenance...).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Wednesday, November 20, 2013 7:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

I have two possible Aces up my sleeve.

IFC 2009 509.2: Equipment Access.  Approved access shall be provided and 
maintained for all fire protection equipment to permit immediate safe operation 
and maintenance of such equipment.

This site has a dedicated fire service who act as first response to all the 
client facilities who occupy this industrial park.  They are the AHJ for the 
park.  They will be contacted to get their input.  There is also the State Fire 
Marshal's office that also has input.

Second is the fact that the proposed location provides no way to bring (6) 4 
lines into the building.

So I've got some ammo to shoot down this concept.

Craig L. Prahl, CET
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A 
Futrell
Sent: Tuesday, November 19, 2013 8:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

No code restrictions, but certainly foam systems concerns.  55 gallon drums to 
second floor with stairs?  Bladder tanks?  Lay 'em down to replace bladder that 
gets torn.  Craig, am I missing something?  If not, I've seen this before and 
it gets ugly real fast.  I've worked on an existing hanger that they buried the 
big tanks in a corner, tore the bladder and have to cut the roof open to lift 
them out, to lay it down, to replace it.

Scott Futrell

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: resurrecting an old system

2013-11-20 Thread Todd - Work
The owner wants to re-use the system and we have to prove to him that it needs 
to be replaced, if it does. I'm thinking after a physical inspection and air 
test, it would tell us if we have something that could be used or not. The 
building is approximately 30 ft to the peak and 25 to the hip and is wide open 
for storage and maintenance of large equipment (demolition company). However, 
working on mains around the perimeter will be difficult at best. 

My guess is that when the system was shut down, they just opened the 2 drain 
and didn't bother with low points. I think most of the low stuff will have to 
be replaced. But it would be helpful if at least the high piping could remain.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

 On Nov 20, 2013, at 9:06 AM, Scott A Futrell sco...@ffcdi.com wrote:
 
 I like the replace it all option...
 How old is the system to start with?
 You need to replace all the sprinklers, if some have popped you don't know 
 how many others may be damaged.
 What about gaskets in grooved couplings?
 Is the water supply now equal to the original pump and pond? If not, pipe 
 size changes, right?
 You could minimize the liability by replacing everything...
 
 Scott
  
 (763) 425-1001 Office
 (612) 759-5556 Cell
 
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - 
 Work
 Sent: Wednesday, November 20, 2013 7:02 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: resurrecting an old system
 
 I am working with a company that bought a building where the sprinkler system 
 had been turned off about 10 years ago. The fire department is requiring that 
 a system be turned on. The existing system was fed from a pump taking suction 
 from a pond (disconnected and removed). There has been some cracking and 
 splitting of fittings at low points and some heads have popped. 
 
 The first step was to have a contractor come in and made a detailed visual 
 inspection of the system, including internal. That showed that all of the 
 pipe up high appears to be in good shape and could possibly be re-used. 
 However, there was some mud (not scale) that had collected in some of the 
 mains.
 
 My thought was that the next step would be to fix or cap off the broken areas 
 and do an air test to see what the integrity of the system really is, then 
 flush the system if all looks good. However, would you want to flush out the 
 mains before you do an air test? If there is a problem with the mains in the 
 area covered by the mud, would the air test not show it? On the other side, 
 flushing would create a problem since there is no public water supply. We 
 would probably have to get a fire department pumper involved. Also, you could 
 have an issue if the water finds a leak and water starts spraying down on 
 equipment
 
 Thoughts? Flush or air test first?
 
 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Misc storage and QR sprinkler deduction

2013-11-20 Thread Brad Casterline
Todd,
Since occupancy classifications are based on quantity and/or combustibility
and expected rates of heat release, uhhh...???

-Original Message-
From: Todd - Work [mailto:t...@fpdc.com] 
Sent: Wednesday, November 20, 2013 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Misc storage and QR sprinkler deduction

I am working on a school project where there is a basement that will be used
for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high
storage of miscellaneous stuff, which I am calling Class IV. This would be a
0.20/1500 sprinkler density, which is the same as the requirement for OH2.
Since I have a marginal water supply and am at the far end of the system,
minimizing the design is critical. 

My question is this; can I use the RA deduction for QR heads in OH2 with the
curves for low piled storage? Or does the fact that this is storage negate
that reduction?

Must be my day for question



Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Misc storage and QR sprinkler deduction

2013-11-20 Thread Ed Kramer
Todd, take a peek at 13.2.2 (2)   (2013 edition).

Ed Kramer
Lawrence, KS

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Misc storage and QR sprinkler deduction

I am working on a school project where there is a basement that will be used
for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high
storage of miscellaneous stuff, which I am calling Class IV. This would be a
0.20/1500 sprinkler density, which is the same as the requirement for OH2.
Since I have a marginal water supply and am at the far end of the system,
minimizing the design is critical. 

My question is this; can I use the RA deduction for QR heads in OH2 with the
curves for low piled storage? Or does the fact that this is storage negate
that reduction?

Must be my day for question



Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Craig.Prahl
Ok just to follow up with the outcome.

Had our meeting with the client, explained access issues and Code requirement 
of Approved access.

Our 2nd foam room will be at grade level in one of two decent locations.  They 
may even push Process guys out of the way for this FP system.  That's a huge 
thing in the industrial world. 

A win for fire protection this early in the day has me cautious about the rest 
of the day.  ;)

Thanks guys for all the shared input and insight.

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A. 
Sornsin, P.E.
Sent: Wednesday, November 20, 2013 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

Just to reiterate Scott's point:  Maintenance is huge and his examples are 
extremely valid.  We were once painted into a corner on our first foam job many 
years ago.  The foam tanks were put on a mezzanine above the risers.  But we 
ensured there was plenty of room on the mezzanine for bladder removal, and 
double doors on the exterior wall of the mezzanine for better access to 
remove/replace bladders or tanks (via fork lift). Not ideal, but serviceable.

(BTW - my favorite example of lack of maintenance foresight is a foam job (by 
others) which included a vertical bladder tank located below a second level - 
with about 2 ft. of clearance above the tank. When the bladder needs 
replacement, the entire tank will have to be disconnected and removed from the 
building.  There may also be some other piping that needs removal to allow this 
to happen. Of course, this is a non-issue if you simply blow-off 
maintenance...).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Wednesday, November 20, 2013 7:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

I have two possible Aces up my sleeve.

IFC 2009 509.2: Equipment Access.  Approved access shall be provided and 
maintained for all fire protection equipment to permit immediate safe operation 
and maintenance of such equipment.

This site has a dedicated fire service who act as first response to all the 
client facilities who occupy this industrial park.  They are the AHJ for the 
park.  They will be contacted to get their input.  There is also the State Fire 
Marshal's office that also has input.

Second is the fact that the proposed location provides no way to bring (6) 4 
lines into the building.

So I've got some ammo to shoot down this concept.

Craig L. Prahl, CET
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A 
Futrell
Sent: Tuesday, November 19, 2013 8:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Location of foam system valve room on 2nd floor - permitted?

No code restrictions, but certainly foam systems concerns.  55 gallon drums to 
second floor with stairs?  Bladder tanks?  Lay 'em down to replace bladder that 
gets torn.  Craig, am I missing something?  If not, I've seen this before and 
it gets ugly real fast.  I've worked on an existing hanger that they buried the 
big tanks in a corner, tore the bladder and have to cut the roof open to lift 
them out, to lay it down, to replace it.

Scott Futrell

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread Forest Wilson Fire Sprinkler Comtractor
I would air test first but I think you will need the water test to find leaks  


Sent from my Galaxy S®III

 Original message 
From: Scott A Futrell sco...@ffcdi.com 
Date: 11/20/2013  9:06 AM  (GMT-05:00) 
To: sprinklerforum@lists.firesprinkler.org 
Subject: RE: resurrecting an old system 
 
I like the replace it all option...
How old is the system to start with?
You need to replace all the sprinklers, if some have popped you don't know 
how many others may be damaged.
What about gaskets in grooved couplings?
Is the water supply now equal to the original pump and pond? If not, pipe size 
changes, right?
You could minimize the liability by replacing everything...

Scott
 
(763) 425-1001 Office
(612) 759-5556 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 7:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread rongreenman .
Push Like button now.


On Wed, Nov 20, 2013 at 7:24 AM, craig.pr...@ch2m.com wrote:

 Ok just to follow up with the outcome.

 Had our meeting with the client, explained access issues and Code
 requirement of Approved access.

 Our 2nd foam room will be at grade level in one of two decent locations.
  They may even push Process guys out of the way for this FP system.  That's
 a huge thing in the industrial world.

 A win for fire protection this early in the day has me cautious about the
 rest of the day.  ;)

 Thanks guys for all the shared input and insight.

 Craig L. Prahl, CET
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com



 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A.
 Sornsin, P.E.
 Sent: Wednesday, November 20, 2013 9:44 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Location of foam system valve room on 2nd floor - permitted?

 Just to reiterate Scott's point:  Maintenance is huge and his examples are
 extremely valid.  We were once painted into a corner on our first foam job
 many years ago.  The foam tanks were put on a mezzanine above the risers.
  But we ensured there was plenty of room on the mezzanine for bladder
 removal, and double doors on the exterior wall of the mezzanine for better
 access to remove/replace bladders or tanks (via fork lift). Not ideal, but
 serviceable.

 (BTW - my favorite example of lack of maintenance foresight is a foam job
 (by others) which included a vertical bladder tank located below a second
 level - with about 2 ft. of clearance above the tank. When the bladder
 needs replacement, the entire tank will have to be disconnected and removed
 from the building.  There may also be some other piping that needs removal
 to allow this to happen. Of course, this is a non-issue if you simply
 blow-off maintenance...).

 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
 http://www.kfiengineers.com

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 craig.pr...@ch2m.com
 Sent: Wednesday, November 20, 2013 7:26 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Location of foam system valve room on 2nd floor - permitted?

 I have two possible Aces up my sleeve.

 IFC 2009 509.2: Equipment Access.  Approved access shall be provided and
 maintained for all fire protection equipment to permit immediate safe
 operation and maintenance of such equipment.

 This site has a dedicated fire service who act as first response to all
 the client facilities who occupy this industrial park.  They are the AHJ
 for the park.  They will be contacted to get their input.  There is also
 the State Fire Marshal's office that also has input.

 Second is the fact that the proposed location provides no way to bring (6)
 4 lines into the building.

 So I've got some ammo to shoot down this concept.

 Craig L. Prahl, CET
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com



 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Scott A
 Futrell
 Sent: Tuesday, November 19, 2013 8:21 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Location of foam system valve room on 2nd floor - permitted?

 No code restrictions, but certainly foam systems concerns.  55 gallon
 drums to second floor with stairs?  Bladder tanks?  Lay 'em down to replace
 bladder that gets torn.  Craig, am I missing something?  If not, I've seen
 this before and it gets ugly real fast.  I've worked on an existing hanger
 that they buried the big tanks in a corner, tore the bladder and have to
 cut the roof open to lift them out, to lay it down, to replace it.

 Scott Futrell

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose 

RE: resurrecting an old system

2013-11-20 Thread Mike Hill
You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread John O'Connor
Mike,
I would respectfully urge flushing prior to full 200# test, simply because
this system contains mud and other debris, that could, still in place, allow
pinhole leaks to remain undetected.  Flush to eliminate debris that could be
allowing a successful pressure test.  Once flushed, the system may still
show leaks resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike
Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1432 / Virus Database: 3629/6352 - Release Date: 11/20/13

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Misc storage and QR sprinkler deduction

2013-11-20 Thread ParsleyConsulting

Todd,
I completely agree with Ed.
13.2.1 (5) would let it qualify as miscellaneous storage, and use Table 
13.2.1, and Figure 13.2.1.
13.2.2 (2) tells you that the same, except you can apply 
Chapter 11 for OH 1  2, and EH 1  2


So, if you apply 13.2.2(2), and Table 13.2.1, class IV to not more than 
10'-0requires OH2. The QR reduction in 11.2.3.2.3.1 (2) applies to OH 
design.


Looks to me like you can apply that area reduction per NFPA 13.
*

PARSLEY CONSULTING

*

Ken Wagoner

760.745.6181 voice

760.745.0537 fax

website: www.ParsleyConsulting.com http://www.ParsleyConsulting.com

On 11/20/2013 7:15 AM, Ed Kramer wrote:

Todd, take a peek at 13.2.2 (2)   (2013 edition).

Ed Kramer
Lawrence, KS

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Misc storage and QR sprinkler deduction

I am working on a school project where there is a basement that will be used
for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high
storage of miscellaneous stuff, which I am calling Class IV. This would be a
0.20/1500 sprinkler density, which is the same as the requirement for OH2.
Since I have a marginal water supply and am at the far end of the system,
minimizing the design is critical.

My question is this; can I use the RA deduction for QR heads in OH2 with the
curves for low piled storage? Or does the fact that this is storage negate
that reduction?

Must be my day for question



Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Misc storage and QR sprinkler deduction

2013-11-20 Thread John Denhardt
As long as you are in Chapter 13, Chapter 11 modifiers apply as applicable.

John

It should be recognized that the above is my opinion as a member of the NFPA 13 
Technical Committee on Sprinkler Discharge Criteria, and has not been processed 
as a formal interpretation in accordance with the NFPA Regulations Governing 
Committee Projects and should therefore not be considered, nor relied upon, as 
the official position of the AFSA nor the NFPA, nor any of their technical 
committees.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ed Kramer
Sent: Wednesday, November 20, 2013 10:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Misc storage and QR sprinkler deduction

Todd, take a peek at 13.2.2 (2)   (2013 edition).

Ed Kramer
Lawrence, KS

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Misc storage and QR sprinkler deduction

I am working on a school project where there is a basement that will be used
for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high
storage of miscellaneous stuff, which I am calling Class IV. This would be a
0.20/1500 sprinkler density, which is the same as the requirement for OH2.
Since I have a marginal water supply and am at the far end of the system,
minimizing the design is critical. 

My question is this; can I use the RA deduction for QR heads in OH2 with the
curves for low piled storage? Or does the fact that this is storage negate
that reduction?

Must be my day for question



Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread John Denhardt
I would suggest a slightly modified approach.

Test and repair as needed until tight.  Flush and then retest.

You really need to flush and retest due to the leaks that might be uncovered 
after proper flushing.  I agree with Scott on cost.  Given the total cost in 
the end, it might be wiser for the owner to spend the money on replacing the 
system.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John 
O'Connor
Sent: Wednesday, November 20, 2013 11:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

Mike,
I would respectfully urge flushing prior to full 200# test, simply because
this system contains mud and other debris, that could, still in place, allow
pinhole leaks to remain undetected.  Flush to eliminate debris that could be
allowing a successful pressure test.  Once flushed, the system may still
show leaks resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike
Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1432 / Virus 

RE: resurrecting an old system

2013-11-20 Thread Matt Grise
The other benefit to the owner with replacement is a warranty. If the system is 
patched back together, then it could end up being a source of constant 
headaches and expense if leaks start to show up. 

Replacing the system could end up being a faster option depending on how many 
rounds of testing, flushing, and patching are needed.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John 
Denhardt
Sent: Wednesday, November 20, 2013 10:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

I would suggest a slightly modified approach.

Test and repair as needed until tight.  Flush and then retest.

You really need to flush and retest due to the leaks that might be uncovered 
after proper flushing.  I agree with Scott on cost.  Given the total cost in 
the end, it might be wiser for the owner to spend the money on replacing the 
system.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John 
O'Connor
Sent: Wednesday, November 20, 2013 11:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

Mike,
I would respectfully urge flushing prior to full 200# test, simply because this 
system contains mud and other debris, that could, still in place, allow pinhole 
leaks to remain undetected.  Flush to eliminate debris that could be allowing a 
successful pressure test.  Once flushed, the system may still show leaks 
resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System 
froze and there were lots of issues. The occupant's first indication of a 
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and 
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much longer, 
so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street pressure, 
we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also 
separated the system into smaller sections before we started testing, so as to 
help us locate leaks.

I would try to salvage as much of the existing system as possible, if only to 
help the owner save some money. Why discard the system because of what you 
think might be wrong.
Find out what is actually wrong. System may be easily and confidently repaired 
or you may find enough issues or concerns spread out through the entire 
building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air