Yea, i suspected that. Me bad. been a while for sure.
On 6/25/2020 6:31:24 PM, William Miller wrote:
Kirk:
If my memory is correct: What you describe below are port assignments if one is
stacking FXR inverters for 120/240 with a Hub 10.3. It also requires changing
DIP jumpers from factory defaul
The master-slave config types and port assignments have always been confusing.
The quick start guide lists a config where the master is port 1 and the slave
is port 7. I believe port 7 is called the sub-master in this config. With only
2 inverters it functions as the slave to the master in port
Well after just a little over 2 hours on hold I did get through to a very
understanding tech support rep. I explained the issue and that the only LED
on the board that was on was the D21 (Remote Pwr). Today I learned that
this is powered by the Hub. Thus the PSB is indeed dead. I was given a
choice
Kirk:
If my memory is correct: What you describe below are port assignments if
one is stacking FXR inverters for 120/240 with a Hub 10.3. It also
requires changing DIP jumpers from factory defaults. This is not accurate
for stacking Radians. With Radians I think secondary inverters can use a
Ok back to outback defective board in the comms side of the inverter,
contact outback and what ever you do do NOT leave your number for a call
back as it will never come, call first thing, stay on hold and wait.
Jerry
On Thu, Jun 25, 2020, 2:00 PM Chris Schaefer
wrote:
> Since the Flexnet on por
Since the Flexnet on port 3 was active and could be seen on the Mate, thus
I moved the slave on port 2 to port 3 and moved the FlexNet from port 3 to
port 4. No change. I did try another OB factory green cable to no avail.
Christopher
On Thu, Jun 25, 2020 at 4:25 PM Jerry Shafer
wrote:
> Chris
Chris
Did you skip over and plug in to port 3 with the slave, swap the cord,
Jerry
On Thu, Jun 25, 2020, 12:54 PM Chris Schaefer
wrote:
> The system is critical to a farm watering operation so I wasn't able to
> shut it down to try and swap the port 1 inverter with the port 2 inverter.
> As for
The system is critical to a farm watering operation so I wasn't able to
shut it down to try and swap the port 1 inverter with the port 2 inverter.
As for changing the power save settings, that is what alerted me to the
issue. Under no circumstance can you see a port 2 via the Mate. That's what
had
Wrenches
It sounds like a out of the box board failure, even if the slave is in
standby it is connected to the hub and you see it, if you swapped the
cable, port location, its time to talk to OB tech and get a board sent out,
Jerry
On Thu, Jun 25, 2020, 12:37 PM William Miller
wrote:
> Christoph
Did you try putting the slave inverter to port 1?
Jay
> On Jun 25, 2020, at 10:35 AM, Chris Schaefer wrote:
>
>
> G'Day All,
>
> So I started up a system recently with two Radian 8048A's. The master is
> connected to port 1 and the slave connected to port 2 with the FlexNet at
> port 3. Th
Christopher;
Just spit-balling here: is the secondary inverter asleep (hate the
master/slave terminology…)? Try changing power save settings to make sure
the secondary is awake and see if that changes the situation. Seems
unlikely this will solve the problem, but it may provide some kind of c
Hey Chris,
Sounds like a failed power supply board Outback part SPARE-215. If the unit is
under warranty you should be able to get a replacement through OB tech support.
> Sent from a IPhone, with touch screen keys on the fly. Please excuse
> shortcuts and typos.
>
Roland Shackelford
NABCE
G'Day All,
So I started up a system recently with two Radian 8048A's. The master is
connected to port 1 and the slave connected to port 2 with the FlexNet at
port 3. There are no OB charge controllers in the system. When the hub is
polling (led's scrolling) nothing shows up for the slave at port 2