Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread Darryl Thayer via RE-wrenches
My first thought is what meter are you using? Some meter will have high input impedance and give false value On Tue, Oct 15, 2024 at 1:09 PM rick--- via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Back on the Sol-Ark topic again. We have a customer whose 12kW is > measuring -195VDC

Re: [RE-wrenches] 208V residential service

2024-10-17 Thread Darryl Thayer via RE-wrenches
sounds strange to me. is the service 120 208 meaning 120 to neutral, and 120 to neutral and 208 between phases? meaning you are two legs of a 3-phase? if you are trying to use a single phase 240 volt inverter, be careful of the inverter wiring. some inverters can not be connected because you do

Re: [RE-wrenches] 120/240V to 200V 3 phase (Japanese Electrical Scheme)

2024-07-25 Thread Darryl Thayer via RE-wrenches
Sorry for the confusing reply, Ijust checked with my supplier of speed drives, it is now allen bradley, he said 15 kW is awfully big reply On Thu, Jul 25, 2024 at 1:05 PM Darryl Thayer wrote: > You made me think and that is sometimes not good. Is this 200 v between > phases? Then a 120-208 th

Re: [RE-wrenches] 120/240V to 200V 3 phase (Japanese Electrical Scheme)

2024-07-25 Thread Darryl Thayer via RE-wrenches
hi sorry to waste your time. my supplier now Allen Bradley said 15 kW is awfully big for a speed drive , I am not sure you meant 1.5 kW, that is about $1000, AND NO Problem with single phase 240 volt input. On Thu, Jul 25, 2024 at 11:49 AM James Jarvis via RE-wrenches < re-wrenches@lists.re-wrenc

Re: [RE-wrenches] 120/240V to 200V 3 phase (Japanese Electrical Scheme)

2024-07-25 Thread Darryl Thayer via RE-wrenches
You made me think and that is sometimes not good. Is this 200 v between phases? Then a 120-208 three phase output should work fine. However I am not sure a 15kW inverter will supply the power. I have had good luck with sol-ark 15 kW powering small motors single phase, but a speed drive has recti

Re: [RE-wrenches] 120/240V to 200V 3 phase (Japanese Electrical Scheme)

2024-07-25 Thread Darryl Thayer via RE-wrenches
I think you stated the answer, use a frequency drive, your AC source or even DC source can charge the capacitors in the drive. Call your local ABB drive supplier and they will tell you how to set up. If you need 15 kW I find the drive has to be larger than 15 kW, because you are supplying with si

Re: [RE-wrenches] Simpliphi Phi 3.8 48V Case Color

2024-05-29 Thread Darryl Thayer via RE-wrenches
I was under impression that white case has a communication and black has none. Some inverters can communicate some can not with the white case. On a new project have matched inverter and battery. On Wed, May 29, 2024, 6:15 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org>

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Darryl Thayer via RE-wrenches
I had a similar pipe leak. I forgot how I located it, but I used a vaccumn gauge or pump and to determine how far down the well the the leak was and pulled the pump and pipe and found a crack. On Sat, May 25, 2024 at 8:41 PM Bradley Bassett via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrot

Re: [RE-wrenches] Fortress Avalon

2024-05-14 Thread Darryl Thayer via RE-wrenches
I am looking at going high voltage as opposed to 48 volts. This is my largest battery system, I have a large distance between battery and inverter, 40 feet, the cost of wire, 50 kW, at 50 volts is 1000 amps. I am thinking this is too big for me. On Tue, May 14, 2024, 7:29 PM Mac Lewis via RE-wren

Re: [RE-wrenches] Large transformer losses

2024-04-26 Thread Darryl Thayer via RE-wrenches
Do you know the transformer impedance? On Fri, Apr 26, 2024, 5:54 PM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi all. > > Anyone know what the tare loss and efficiency is of a 75 kw transformer? > And it would be run mostly at 1-10kw max. > > This one specifically. > hamm

Re: [RE-wrenches] Large transformer losses

2024-04-26 Thread Darryl Thayer via RE-wrenches
Hi Jay I have gotten this type of information directly from Hammond, I would think from transformer to House line loss should be considered. From my Experiance, people go to 400 amp services mostly for circuit count. I have measured a few transformers in past but I don't know where data is now.

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-26 Thread Darryl Thayer via RE-wrenches
I agree with John also. one of the better-performing off-grid houses I worked on used a 48 to 12-V Samlex converter. The 12-volt thick-walled refrigerator was about 4 amps at 12 volts. The lights, radio, and small TV drew very few amps each/ I also used an Outback 3648 inverter, which the homeown

Re: [RE-wrenches] speaking of batteries

2024-04-23 Thread Darryl Thayer via RE-wrenches
If the batteries have a 10-year life, I don't think it would make much difference. LA batteries show an increase in internal resistance after a few recharges. Typically, the BMS in a Li battery will ensure at top balance all cells balance, If the batteries are being properly recharged. On Tue, A

Re: [RE-wrenches] Clamping CTs Around Live Conductors - White Paper References and/or Anecdotal Information Requested

2024-03-08 Thread Darryl Thayer via RE-wrenches
I have done it many times. YES terminate the secondary first. As an older CT is a step up the voltage transformer and can generate thousands of volts. Many of new type Cats are low voltage output and are safe to work with. On Fri, Mar 8, 2024, 10:46 AM Jerry Shafer via RE-wrenches < re-wrenches@

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Darryl Thayer via RE-wrenches
I used to be Lead AGM for Off-grid; I used the Pure Lead Thin Plate for an install 4 years ago from AltE, and it is still working fine. I believe the LiFe is the battery for off-grid and the trick is to find the correct BMS, On Sat, Feb 17, 2024 at 11:43 AM Drake Chamberlin via RE-wrenches < re-w

Re: [RE-wrenches] Fortress

2024-02-15 Thread Darryl Thayer via RE-wrenches
Is it similar to my problem with my Simplify batteries? Over time, the BMS did not allow all cells to charge the same. To correct this, I had to charge each battery separately, and after this, they stayed equivalent for more years. On Thu, Feb 15, 2024 at 7:50 AM Jay via RE-wrenches < re-wrenches@

Re: [RE-wrenches] No payment for Sunpower warranty service vendor credits?

2024-02-13 Thread Darryl Thayer via RE-wrenches
Advice, please; I was about to purchase a SunPower inverter. Have other people been having problems? I cannot reach their support line with my questions. As many of you know, I am a small contractor. I have noticed a reluctance of solar equipment suppliers, both Outback and Sol-Ark, who have recent

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Darryl Thayer via RE-wrenches
About 4 years ago I wrote about my failure of Simplify in service 3 years. after much delay, I took each unit to shop and charged each one on bench power supply, all returned to full function and are still working today off grid system. I agree with the comments they are tricky, MorningStar knows

Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance

2024-01-01 Thread Darryl Thayer via RE-wrenches
I had a some way similar experience I used fire raptor and added a relay to use Raptor signal to shutdown inverter. On Mon, Jan 1, 2024, 2:01 PM Mac Lewis via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hello Wrenches, > > I need to retrofit a Schneider XW+ system with a rapid shutd

Re: [RE-wrenches] Home grid stacked battery heating

2023-11-05 Thread Darryl Thayer via RE-wrenches
Great site, Allan, but many facts still need to be included. Was there a discharge or charge going on? How much power was being drawn by the heaters? If this is for a standalone system, energy consumption is very important. What is the lower temperature cell discharge limit of Blue Planet? What

Re: [RE-wrenches] Outback Radian Generator Charging

2023-10-27 Thread Darryl Thayer via RE-wrenches
You have had many good suggestions but note you are on border line power, at 2200 teet your power is down 10% note gen's are 80% of name plate, and you are asking for 7.2 kW from a Genny that with atmospheric correction is 7.2 kW On Fri, Oct 27, 2023, 8:27 AM Amos Post via RE-wrenches < re-wrenche

Re: [RE-wrenches] Well pump with Sol-Ark

2023-10-11 Thread Darryl Thayer via RE-wrenches
I have off grid customers where I have them install 1/2 HP pump, also Franklin soft start seems to help, low cost but I do not know how it works, it has a start capacitor I think. On Wed, Oct 11, 2023, 1:23 PM James Jarvis via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > On Wed, Oct

Re: [RE-wrenches] Generator question

2023-09-25 Thread Darryl Thayer via RE-wrenches
Generators are load responsive. They can not be back feed, one approach is to take heavy loads and have the inverter drop these loading heav load situations. bring these loads on line with a PLC On Mon, Sep 25, 2023 at 11:22 AM Chris Daum via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrot

Re: [RE-wrenches] Franklin Home Power

2023-09-16 Thread Darryl Thayer via RE-wrenches
sorry for a dumb question but what is the voltage ranges of the Franklin? On Thu, Sep 14, 2023 at 4:26 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Enphase does generator support as well. Fortunately, I do not need that, > so maybe it opens up my options. It's

Re: [RE-wrenches] Power conditioner for Trace inverter

2023-09-09 Thread Darryl Thayer via RE-wrenches
gt;> *Dave Angelini Offgrid Solar >> "we go where powerlines don't" >><http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ >> <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/> >> e-mail offgridso...@st

Re: [RE-wrenches] Power conditioner for Trace inverter

2023-09-08 Thread Darryl Thayer via RE-wrenches
New washing machines are small loads 400 Watts about. On Fri, Sep 8, 2023, 2:27 PM Darryl Thayer wrote: > I once used a ferro-resonant transformer to clean up a sine wave. You > have to know the power. > > On Fri, Sep 8, 2023, 1:59 PM Chris Daum via RE-wrenches < > re-wrenches@lists.re-wrenches

Re: [RE-wrenches] Power conditioner for Trace inverter

2023-09-08 Thread Darryl Thayer via RE-wrenches
I once used a ferro-resonant transformer to clean up a sine wave. You have to know the power. On Fri, Sep 8, 2023, 1:59 PM Chris Daum via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi folks: > > > > I have a fellow with a Trace SW5548, purchased from us in 2001. It’s > been worki

Re: [RE-wrenches] Wind machines

2023-08-18 Thread Darryl Thayer via RE-wrenches
I agree wit most of the comments. I have tested many VAWT none were any good. i had presented my study at the MIdwest Energy Fair, showing much higher trust on the turbine's and much lower performance. I just wanted to let you know that sume no performance at all. On Fri, Aug 18, 2023 at 10:52

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Darryl Thayer via RE-wrenches
I need clarification; however, here is my interpretation for you. The utility feeds the meter and then the 100A breaker. Then you want this 100A breaker to feed the 220A bus panel. This 220A panel then supplies through a 100A breaker the house load. The solar also feeds the 220A panel. If the sola

Re: [RE-wrenches] 200a manual xfer switch w/ small aux contact : who makes it?

2023-07-26 Thread Darryl Thayer via RE-wrenches
I have seen such equipment from generator suppliers, they will be reversing contactors, Look for reversing disconnecting switches I have used them from SQ D and Eaton, and GE. On Wed, Jul 26, 2023 at 5:26 PM Mick Abraham via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi, Mechanix~

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-22 Thread Darryl Thayer via RE-wrenches
How about a Morningstar relay driver? I have not done this exact thing before.but similar things. On Thu, Jul 20, 2023 at 4:05 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI All, > > I wanted to revisit this thread for one reason. > > If you turn off the inverter at the

Re: [RE-wrenches] How to make PV Watts calculate solar on north facing roof

2023-07-19 Thread Darryl Thayer via RE-wrenches
t; > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Darryl Thayer via RE-wrenches > *Sent:* Wednesday, July 19, 2023 12:17 PM > *To:* newrewrenches > *Cc:* Darryl Thayer >

[RE-wrenches] How to make PV Watts calculate solar on north facing roof

2023-07-19 Thread Darryl Thayer via RE-wrenches
Customer wants me to propose adding solar modules to north roof. I don't know how to get answer from PV Watts? ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Lithium battery recommendation

2023-07-14 Thread Darryl Thayer via RE-wrenches
I have one of four one alarm locked no tech support On Fri, Jul 14, 2023, 2:11 PM Darryl Thayer wrote: > Yes the pytes are good price, I had problems and no tech support > > On Fri, Jul 14, 2023, 1:51 PM Andrew Perkins via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Jay we hav

Re: [RE-wrenches] High current dc combiner vibration

2023-07-01 Thread Darryl Thayer via RE-wrenches
Hi you have the correct people on the job but get at the basics the forces causing the vibration is magnetic. You have to break the magnetic path. If it was electrical a simple cut in the enclosure. But it is magnetic which is much harder to stop. If the hum stops with the cover off replace the c

Re: [RE-wrenches] Manufactured homes

2023-06-30 Thread Darryl Thayer via RE-wrenches
check with Iron Ridge as they have done for me On Fri, Jun 30, 2023 at 4:15 PM Bruce Erickson via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi California guys, > > We have a couple of leads that are manufactured homes, that have to be > permitted through the CA Housing and Communi

Re: [RE-wrenches] LG Chem RESU10H Battery Question

2023-06-30 Thread Darryl Thayer via RE-wrenches
Hi David I think although it is 450 volts out, the battery is actually moch lower voltage and has a buck boost charge controller. It bucks the voltage down to charge the battery and boost the voltage to serve the load. If you open the battery and rewire you will need a BMS, you can find on line bu

Re: [RE-wrenches] High current dc combiner vibration

2023-06-30 Thread Darryl Thayer via RE-wrenches
Are we all thinking single phase? Another idea would be to use plastic enclosures in at least some way to break the magnetic path. This is a lot of current, and it will cause magnetic heating where the magnetic loop is complete. On Thu, Jun 29, 2023 at 10:19 AM Kirk Herander via RE-wrenches < re-

Re: [RE-wrenches] High current dc combiner vibration

2023-06-29 Thread Darryl Thayer via RE-wrenches
Hi all, just a few comments, The inverter charger has a ripple on the DC. All have this; Outback is no exception. However, all wires should be run together, positive and negative same conduit and same hole, as the AC ripple magnetic effects cancel from both wires. Also, the circuit breaker has an

Re: [RE-wrenches] Iron Edison Lithium SOC drift

2023-06-29 Thread Darryl Thayer via RE-wrenches
I have had similar problems with other equipment. fully the battery to top balance and then reset the SOC On Thu, Jun 29, 2023 at 7:04 AM Jeremy Rodriguez via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > We have about 20 units out in service. > All of the batteries SOC readings have

Re: [RE-wrenches] Lithium battery charge rate

2023-06-27 Thread Darryl Thayer via RE-wrenches
Hi Jay and all, I belive Steve meant C/2 or C/3; just a typo. My oldest set of LiFe is almost 10 years? It has a fastest charge rate of C/0.2 because the 10 kWh is charged by 1.6 kW solar. These batteries are doing fine. I do not have a way of measuring the current capacity but On Mon, Jun 26,

Re: [RE-wrenches] Lithium battery charge rate

2023-06-26 Thread Darryl Thayer via RE-wrenches
Hi Jay, Larry says is correct. My experience, with cells and there BMS is they need to get up to top balance voltage then the BMS will stop charging the full cells and bring the remainder of cells up to fill charge. My oldest set is about 6 years old, since I understood they have been fine On Mo

Re: [RE-wrenches] Need detailed help with Pytee battery

2023-06-05 Thread Darryl Thayer via RE-wrenches
e in the future. > Good Luck, > Howie > Sun Catcher > 802-272-0004 > > > > On Sat, Jun 3, 2023 at 1:08 PM Darryl Thayer via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> I have a Pytee battery that has gone into alarm. Won't come out.

[RE-wrenches] Need detailed help with Pytee battery

2023-06-03 Thread Darryl Thayer via RE-wrenches
I have a Pytee battery that has gone into alarm. Won't come out. Pytee says to connect the computer and diagnose. That is all they said. They do not answer emails asking for further advice. Does anyone know what to do? Sps to use? Address to use? __

Re: [RE-wrenches] Fortress LFPs & ENVY 12kw inverter

2023-06-01 Thread Darryl Thayer via RE-wrenches
Hello, just an onion of an old person. I have needed a lot of tech help, I find Sol-Ark the best tech, So I would go with experiance. On Thu, Jun 1, 2023 at 11:19 AM Kirk Herander via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hello All, > > I am sizing my first Fortress system, 1

Re: [RE-wrenches] Just getting old?

2023-05-17 Thread Darryl Thayer via RE-wrenches
Was the inverter connected at the time of testing? If so I suspect the inverter is loading the solar array below Vmp On Wed, May 17, 2023 at 11:23 PM frenergy via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Wrenches, > > I've got a call from a customer that said their

Re: [RE-wrenches] Battery balancers

2023-05-16 Thread Darryl Thayer via RE-wrenches
Hi Jay, if this is the LA AGM thin plate, I tried to look into this a few years ago. Being AGM, they have a recombination feature; when overcharged, they recombine the H2 O2, thus self-balancing, just like the top balance in LiFe. The caution is not to charge too fast in absorb mode. I decided n

Re: [RE-wrenches] Metering

2023-05-13 Thread Darryl Thayer via RE-wrenches
I have used Egauge in this situation many times. They even have revenue-grade Current Transformers.(CTs) Their tech support is good, I find even I can set them up easily. They use normal English in their documentation. On Thu, May 11, 2023 at 3:21 PM Larry Brown via RE-wrenches < re-wrenches@li

Re: [RE-wrenches] Old and new Radian

2023-05-10 Thread Darryl Thayer via RE-wrenches
Sorry if this is nonsense, but your existing Radian is your "AC grid source," It can act as the paralleling. AC coupling source. I did this about 20 to 30 years ago, using FX inverters, not Radians, to power a large motor. Can your Radian Mate 3 run in grid zero? Or if not, one inverter runs all

Re: [RE-wrenches] problem using Radian on TOU metering

2023-05-03 Thread Darryl Thayer via RE-wrenches
I am in Minnesota utility is Xcel energy On Tue, May 2, 2023 at 9:12 PM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Which utility has such low rates? > > SMUD? > > Jay > > > > On May 2, 2023, at 12:05 PM, Darryl Thayer via RE-wrenches <

[RE-wrenches] problem using Radian on TOU metering

2023-05-02 Thread Darryl Thayer via RE-wrenches
Hello, I apologize for perhaps a dumb question. I did go online to ask Outback twice, no answer.System Radian 8 kW and Mate3 with 2 each 1.5 kW solar arrays into 2 ea. MX60s. Battery 20 kWh LiFe open loop. The owner wants the lowest energy bill. The rates are; off-peak at 0.04/kWh and on-pe

Re: [RE-wrenches] active vs apparent power readings with solar

2023-04-29 Thread Darryl Thayer via RE-wrenches
Hi all, if the micros are not producing power I would expect an extremely low power factor. The power factor of all inverters is low not in use. Make sure electrician is measuring during production. My measurements are extra low for micro inverters. On Thu, Apr 27, 2023, 4:11 PM August Goers via

Re: [RE-wrenches] active vs apparent power readings with solar

2023-04-28 Thread Darryl Thayer via RE-wrenches
This power factor is impossible, can he measure the apparent power then the real power separately devide the real by apparent to get power factor. I guess he has connections wrong, wrong leg of split phase. If the inverter is off, then possible, do you measure current off the inverter and DC into

Re: [RE-wrenches] Lithium upgrade when Magnasine goes to float too soon

2023-04-18 Thread Darryl Thayer via RE-wrenches
Hello, I have had similar serious problems when working with old batteries. Their voltage rises rapidly when charging. The older batteries will lose in capacity and more so charging rate. Have the batteries been equalized periodically? If not, they will develop sulfur on the plates. The solutio

Re: [RE-wrenches] PV and EMP

2023-03-10 Thread Darryl Thayer via RE-wrenches
It depends upon the pulse. It you are referring to a an EMP caused by a solar storm this is hard on large electrical grids. No problem on Solar equipment. The voltage current is Ndf/dt number of turns times rate of change of flux, the grid can collapse but if you disconnect from grid (multimode

Re: [RE-wrenches] Fire fighters

2023-03-08 Thread Darryl Thayer via RE-wrenches
Hello the answer is yes. On a job several years ago to finish I worked after dark. It was a full moon, and a street light was nearby I got bit from a 500 Voc module string. I am sure I did not have 500 V but it only takes 20 ma. To be deadly. I did not get my volt ohm meter out but I should hav

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread Darryl Thayer via RE-wrenches
Hello i have an XW Pro that starts a 2 HP induction motor reliably, i noticed th scope indicates battery voltage current issue, be sure your batteries can supply the starting surge. I recently installed a new set of batteries. Some not all Li can surge. On Sat, Jan 14, 2023, 5:13 PM bob--- via

Re: [RE-wrenches] Utility transformer limitations

2022-12-26 Thread Darryl Thayer via RE-wrenches
n avoided an $8k invoice > from the utility. The utility was not transparent about this option at > first and only made it clear after some persistence. > > > > Good luck, > > > > Garrison Riegel > > Celestar Solar > > > > On Dec 25, 2022, at 3:14 PM, Dar

Re: [RE-wrenches] Utility transformer limitations

2022-12-25 Thread Darryl Thayer via RE-wrenches
It is common practice for the utility to overload the transformer a lot for the potential load. They expect no one will use their service at maximum, furthermore, they expect non coincidence of loads. Look at the transformer most have a label as to the kW or the unit, and the utility should give

Re: [RE-wrenches] XW Grid Support or?

2022-12-25 Thread Darryl Thayer via RE-wrenches
Assuming this is a zero instantaneous no export, not on the daily or monthly. I have installed a few XW, and XW PRO inverters, however, I have never done an instantaneous no export project on the entire service. The problem is the load. Ideally you want to monitor the service entrance and contr

Re: [RE-wrenches] Magnum MS4024 grief

2022-12-18 Thread Darryl Thayer via RE-wrenches
Hi, happy holidays to all. Of course it sounds like a dual bonding situation. Inverter generators are normally floating neutral, rotating generators are normally neutral bonded internally in the generator. The GFCI detects a neutral current on the ground wire. If the generator is bonded interna

Re: [RE-wrenches] solar lease questions

2022-12-17 Thread Darryl Thayer via RE-wrenches
Hi all, not enough information. Does her grid allow export? Does she have a period of poor sun? What is her daily or monthly consumption? Is there an AC or DC limit on connected solar power? Will her AHJ or Utility allow line side tap? The system seems to be poorly designed. Power Walls are AC c

Re: [RE-wrenches] BACKUP system revival

2022-12-17 Thread Darryl Thayer via RE-wrenches
Hello and happy holidays. About 10 years ago, I had a similar problem with a similar customer who wanted a similar problem solved. The Generac auto transfer switch needed a 12 volt source. When the grid went down the generac transfer switch disconnected and waited about 10 to 15 seconds then sta

Re: [RE-wrenches] Frequency converter?

2022-10-06 Thread Darryl Thayer via RE-wrenches
Hi Chris, this a Darryl kluge approach. Get a 50 Hz battery charger, a LiFePO battery. And a off grid inverter. 20 kW is tough, maybe a 15 kW inverter woild surfice. The battery plus battery chsrger should be sized to handle 300 amps 48 volts. 15 kW / 50 volts= 300 A. If the battery can handle 2

Re: [RE-wrenches] Enphase String Breaker Heating Up

2022-08-04 Thread Darryl Thayer via RE-wrenches
Hello, breakers are thermal-magnetic the current heats the breaker; if the current is high enough for long enough, a solder pot inside melts; this current and excessive heat causes other breakers to open Are you sure the string current is less than 80% of the breaker rating and the wire connecting

Re: [RE-wrenches] Battery disconnect solution

2022-05-09 Thread Darryl Thayer via RE-wrenches
I want to comment, maybe without value. The breaker you mention is called a "shunt trip" breaker. This is common type breaker in the electrical industry. The MN breaker has a 24 volt solenoid that trips the breaker. Shunt Trip breakers have the solenoid voltage for the system voltage. BUT the w

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Darryl Thayer via RE-wrenches
Yes but how do you trigger fire raptor except by the fire raptor switch? It will take care of by manual control but what about 690.11? On Tue, Apr 19, 2022, 5:06 PM Jerry Shafer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > You may want to look at fire raptor as a RSD option. > Je

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Darryl Thayer via RE-wrenches
I understand the complete Tigo line and any sun-spec MLPE will work, however, it also requires the RSD box from Schneider I don't have experience with any other than the firestop tigo On Tue, Apr 19, 2022 at 11:42 AM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI All > > I

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Darryl Thayer via RE-wrenches
don't think there is a > real safety issue here, but I also don't see how the NEC allows the > conductor to be sized for anything less than 200A. > > Jason > > > On Sun, Apr 17, 2022, 11:29 AM Darryl Thayer via RE-wrenches < > re-wrenches@lists.re-wrenches.

Re: [RE-wrenches] Is There an "Off-grid" (i.e. constant voltage) Version of Microinverters?

2022-04-17 Thread Darryl Thayer via RE-wrenches
r > > Peter T. Parrish, Ph.D. > President, California Solar Engineering > 1107 Fair Oaks Blvd Ste. 351 > South Pasadena, CA 91030 > (323) 839-6108 > > On 04/16/2022 3:59 PM Darryl Thayer via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > > yes, t

Re: [RE-wrenches] Is There an "Off-grid" (i.e. constant voltage) Version of Microinverters?

2022-04-17 Thread Darryl Thayer via RE-wrenches
ident, California Solar Engineering >> 1107 Fair Oaks Blvd Ste. 351 >> South Pasadena, CA 91030 >> (323) 839-6108 >> >> On 04/16/2022 3:59 PM Darryl Thayer via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >> >> yes, there are t

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Darryl Thayer via RE-wrenches
in an >> off-grid scenario with a generator and smart load, we would now need to >> integrate an AC disconnect for generator input (grid) and either a fused >> disconnect or loads panel for any smart load output. With the 12K unit, the >> integrated breakers help cut down on BOS

Re: [RE-wrenches] Is There an "Off-grid" (i.e. constant voltage) Version of Microinverters?

2022-04-16 Thread Darryl Thayer via RE-wrenches
yes, there are three versions of the cybo inverter, the one that I a most familiar with produced a 60 HZ AC signal; the voltage did not exceed 120 volts or 240 volts. The voltage out times the current out was equal to the voltage in times current in. This allowed me to operate a resistance load,

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Darryl Thayer via RE-wrenches
Hello, The overcurrent device is to protect the conductors. you can put any size wire, but you must protect with the overcurrent device. REmember in solar equipment; you may have more than one supply source. The DC best example is solar modules connected in parallel, on On Fri, Apr 15, 202

Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Darryl Thayer via RE-wrenches
Hi, Ron, Yes, you must be careful of the MPPT inputs. You state Sol-Ark has an 18 amp max input, meaning you can not have more than 1 string supplying an MPPT if your 60 cell modules are 10 amps Isc. You state Sol-Ark has a maximum voltage per MPPT of 500 volts, this voltage is *not Voc x number

Re: [RE-wrenches] Water Pumping 24/7

2022-04-01 Thread Darryl Thayer via RE-wrenches
Subject:* Re: [RE-wrenches] Water Pumping 24/7 > > > > Hi Darryl, > > I’d love to see that math on that.you mind sharing? > > -Wes > > 303-653-3073 > > > > > > On Mar 27, 2022, at 1:27 PM, Darryl Thayer via RE-wrenches < > re-wrenches@lists.re-w

Re: [RE-wrenches] Water Pumping 24/7

2022-03-27 Thread Darryl Thayer via RE-wrenches
Hello, Sorry to be so late but I have been overloaded. Just a note on physics of lifting water. The calculation indicates if you pump 1 gallon per minute up 300 feet it required a water hp of 5 HP Use this base number and good pumps are about 70% efficient. If the flow rate is not 1 GPM adjust t