There has been a lot of great information that has been shared. This
list is truly awesome!
My takeaway is that, if Li-Ion is going to be used in a system with an
old FX inverter, probably the Discover would be the best choice.
Due to cost and potential compatibility issues, a better
hese parameters:
>>
>>
>>
>> 1. DOD for flooded L16s: 50%
>>
>> 2. DOD for Blue Planet: 100%
>>
>>
>>
>> I hope I am wrong.
>>
>>
>>
>> Also, we often install battery arrays that are upwards of 4,000 AH. For
gust 9, 2020 12:02 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Best Battery
Wrenchel have been very happy with all my Blue Planet battery
systems, best battery you will install.
Jerry
On Sun, Aug 9, 2020, 11:19 AM
mailto:drake.chamber...@redwoodalliance.org>
t;>
>>
>>
>> 1. DOD for flooded L16s: 50%
>>
>> 2. DOD for Blue Planet: 100%
>>
>>
>>
>> I hope I am wrong.
>>
>>
>>
>> Also, we often install battery arrays that are upwards of 4,000 AH. For
>> example, we installed 5,668
looded L16s: 50%
>>>
>>> 2. DOD for Blue Planet: 100%
>>>
>>>
>>> I hope I am wrong.
>>>
>>>
>>> Also, we often install battery arrays that are upwards of 4,000 AH. For
>>> example, we installed 5,668 of East
ce.
William Miller
*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of
*Jerry Shafer
*Sent:* Sunday, August 9, 2020 12:02 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Best Battery
.@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]] On Behalf Of Jerry Shafer
Sent: Sunday, August 9, 2020 12:02 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Best Battery
Wrenchel have been very happy with all my Blue Planet battery systems, best
battery you will install.
Jerr
t design? Is it
> practical to install 9 cabinets? Does the system detect and compensate for
> circulating currents in this many parallel strings?
>
>
>
> Thanks in advance.
>
>
>
> William Miller
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-
tect and compensate for
> circulating currents in this many parallel strings?
>
> Thanks in advance.
>
> William Miller
>
>
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Jerry Shafer
> Sent: Sunday, August 9, 2020 12:02
nches-boun...@lists.re-wrenches.org [3]] ON BEHALF OF Jerry
Shafer
SENT: Sunday, August 9, 2020 12:02 PM
TO: RE-wrenches
SUBJECT: Re:
[RE-wrenches] Best Battery
Wrenchel have been very happy with all my Blue
Planet battery systems, best battery you will install.
Jerry
On Sun,
Aug 9, 2020, 11:19
in this many parallel strings?
Thanks in advance.
William Miller
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jerry Shafer
*Sent:* Sunday, August 9, 2020 12:02 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Best Battery
Wrenchel have been very happy
Kirk
I would be interested in your amended programming with outback and blue
planet
Jerry
On Mon, Aug 10, 2020, 6:43 AM Kirk Herander wrote:
> http://outbackpower.com/downloads/documents/appnotes/lithium_app_note.pdf
>
> This doesn't explain it, just omits older FX inverters from the Outback
>
I agree on the Trace and Xantrex SW's for offgrid. Bullet proof and easy
to install. I could never go back though to not having the graphics that a
networked system enables. Just to easy to look at a 24 hour battery graph
and see that the battery charged. Also multiple banks can be looked at.
I agree, the AES has a much friendlier voltage range. Thanks for
sharing, Dave. I also do not use the RE Optics, I've moved away from
Outback as well, after having issues with the FXR line, tech support,
and wiring in the tiny enclosure that comes with the Radians. Had
decent luck with
Ah that was the metric I didn’t understand the 2-10, is minutes.
got it
j
> On Aug 10, 2020, at 1:24 PM, Dave Angelini Offgrid Solar
> wrote:
>
> I have forwarded this to Schneider. They gave me a case number in 30 minutes.
> I disagree that "all" Li batteries need this. Obviously
Appreciate forwarding this to Schneider. So you never had any issues
programming their monitoring system or getting it connected to the
internet via the customer's router?
What is the LBCO recommended for the Li+ batteries you are using?
Default on many inverters for FLA is 42 or 44 volts,
I have forwarded this to Schneider. They gave me a case number in 30
minutes. I disagree that "all" Li batteries need this. Obviously simplyphi
does need LBCO to be increased. The LBCO delay does help at 10 minutes from
2 minutes default BTW.
I have not had your issues with tech support.
It relates specifically to Simpliphi, but all brands of Li+ need much
higher LBCO set points compared to Lead acid. Hysteresis and time don't
fix the fact that once the batteries shut off before the inverter, the
entire system is inoperable, with no charging available from the PV. It
creates
http://outbackpower.com/downloads/documents/appnotes/lithium_app_note.pdf
[http://outbackpower.com/downloads/documents/appnotes/lithium_app_note.pdf]
This doesn't explain it, just omits older FX inverters from the Outback
compatible list.
In terms of programming, I did not use Blue Planet's
Hey Ray,
Your comment on Schneider LBCO relates to which brand?
Sympliyfi? Curious because I will send this in again. I did last time and
they said to make sure the config person knows that you can also set the
default LBCO hysteresis from 2V to 10V and the LBCO time from 60 seconds up
to 600
For some reason (that I never got an answer to from Outback or Blue Planet)
older FX inverters are not compatible with Blue Ion LFP batteries. The newer
FXR series are.
Considering one only needs to change slightly charge voltages, duration, etc.
to meet BI recommendations, it's a mystery why
Kilovault Pl AGM for backup power, i am replacing C 15 year old backup
power batteries now much cheaper when cycling is infrequent. By the way
most AGM need cycling.
On Sun, Aug 9, 2020, 3:10 PM Ken Schaal wrote:
> Any thoughts on Kilovault that Morningstar is teaming up with?
> Time for me
My favorite right now is Simpliphi: company has been around since 2002,
and as the name implies, they are simple to install. There is no
external monitoring or comm, just an output breaker on each battery that
can be reset if the internal BMS ever shuts down for any reason. We've
done
Hi Kirk,
Can you explain why it wouldnt work?
Just setpoints.
Jay
> On Aug 9, 2020, at 4:13 PM, Kirk Herander wrote:
>
>
> For some reason (that I never got an answer to from Outback or Blue Planet)
> older FX inverters are not compatible with Blue Ion LFP batteries. The newer
> FXR
I have outback FX systems operating for years now, the lab l had used FX's
and midnite systems, it does need to be 48 volts nominal.
Jerry
On Sun, Aug 9, 2020, 4:13 PM Kirk Herander wrote:
> For some reason (that I never got an answer to from Outback or Blue
> Planet) older FX inverters are not
P.S. The system consists of an old Outback FX inverter and an MX60, with
a 2600 W array.
---
On 2020-08-09 13:12, drake.chamber...@redwoodalliance.org wrote:
Hello Wrenches,
What is the best Li-Ion battery to use with an off grid system?
Thanks,
Drake
Athens Electric
--
HI Drake,
I think it really depends on what inverter you have, what the size is, what
features you want and why do you want lithium?
For example to me, as they are black boxes, I will only use one that has a
physical external monitor, not only a web based, which at this point is pretty
much
I looked at this and decided on a new set of Rolls flooded lead calcium
for my grid-tied backup system.
On 8/9/2020 1:10 PM, Ken Schaal wrote:
Any thoughts on Kilovault that Morningstar is teaming up with?
Time for me to replace my 10 yr old. Deka AGMs.
Not many outages, mostly float. No TOU
Any thoughts on Kilovault that Morningstar is teaming up with?
Time for me to replace my 10 yr old. Deka AGMs.
Not many outages, mostly float. No TOU rates. Net metered.
Thanks
Ken Schaal
CommonWealth Solar
On Sun, Aug 9, 2020, 4:01 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
My favorite are Discover AES and Fortress Power. They both communicate
open loop with Schaner Electric. The best battery I have installed as of
this date. Always like Surette and US battery for FLA.
Dave Angelini
Offgrid Solar
"we go where powerlines
don't"
Wrenchel have been very happy with all my Blue Planet battery systems, best
battery you will install.
Jerry
On Sun, Aug 9, 2020, 11:19 AM wrote:
> Hello Wrenches,
>
> What is the best Li-Ion battery to use with an off grid system?
>
> Thanks,
>
> Drake
> Athens Electric
>
> --
>
Hello Wrenches,
What is the best Li-Ion battery to use with an off grid system?
Thanks,
Drake
Athens Electric
--
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings: