Re: [RE-wrenches] Cable Tray Marking

2020-09-03 Thread Martin Herzfeld
1. In addition, there's a conflict of signal words for NEC 110.21(B) Field-Applied Hazard Markings."Where caution, warning, or danger signs or labels are required by this Code, the labels shall meet the following requirements ..." In other words, one signal word is DANGER and the other signal

Re: [RE-wrenches] Cable Tray Marking

2020-09-03 Thread Rebekah Hren
This is interesting, since the definition of high voltage was changed to >1000V a few code cycles ago and it is somewhat consistently applied throughout the NEC at that voltage (except for workspace clearances...er). It seems this 392.18 label requirement could cause confusion and should be

Re: [RE-wrenches] Cable Tray Marking

2020-09-02 Thread Ray
This is interesting, because we were considering cable trays, too.  My guess is that both requirements would apply.  Picky, but I don't see that 690 exempts the requirements of 392. One is for PV, one is for over 600 v.  Some code iteration in the future might have combined language for PV

[RE-wrenches] Cable Tray Marking

2020-09-02 Thread Corey Shalanski
Wrenches, I am curious about the marking requirements for cable trays containing PV source/output circuits rated over 600 volts, installed on a building: NEC 392.18(H) requires a permanent, legible warning notice carrying the wording “DANGER — HIGH VOLTAGE — KEEP AWAY” at least once every 10

[RE-wrenches] Cable tray

2015-08-31 Thread Brian Mehalic
Hello wrenches, question about running conductors in cable tray. So we have our allowance in 690.31(C)(2) for using small PV Wire in cable tray for PV source and output circuits. I'm trying to determine what adjustment factor to apply when there are a bunch of small conductors. 392.80(A)(2)(a)

Re: [RE-wrenches] Cable tray

2015-08-31 Thread billbrooks7
31, 2015 2:56 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Cable tray Hello wrenches, question about running conductors in cable tray. So we have our allowance in 690.31(C)(2) for using small PV Wire in cable tray for PV source and output circuits. I'm

Re: [RE-wrenches] Cable tray

2013-04-01 Thread Chris Mason
: From: John Berdner john.berd...@solaredge.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: Sunday, March 31, 2013, 1:08 PM Dan: I have to disagree with your statement regarding costs and voltage. While clearance and creepage distances

Re: [RE-wrenches] Cable tray

2013-04-01 Thread Exeltech
, Chris Mason cometenergysyst...@gmail.com wrote: From: Chris Mason cometenergysyst...@gmail.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: Monday, April 1, 2013, 9:23 AM With regards to 600V costs Vs 1000V costs, once 1000V equipment becomes

Re: [RE-wrenches] Cable tray

2013-04-01 Thread Chris Mason
. .. to name a few. Ends up being higher-cost products. Dan --- On *Mon, 4/1/13, Chris Mason cometenergysyst...@gmail.com* wrote: From: Chris Mason cometenergysyst...@gmail.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: Monday, April

Re: [RE-wrenches] Cable tray

2013-04-01 Thread boB
--- On *Mon, 4/1/13, Chris Mason /cometenergysyst...@gmail.com mailto:cometenergysyst...@gmail.com/* wrote: From: Chris Mason cometenergysyst...@gmail.com mailto:cometenergysyst...@gmail.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches

Re: [RE-wrenches] Cable tray

2013-03-31 Thread Chris Mason
As we see more 1000V installations, chances are that 600V rated equipment will find its way into installations it is not rated for. To avoid problems and so we don't need two SKUs and lots more inventory, the manufacturers need to move all their product to 1000V ratings. I suspect it does not cost

Re: [RE-wrenches] Cable tray

2013-03-31 Thread Exeltech
dielectric rating). This results in more rigorous (consequently more expensive) UL testing.  Etc. All adds up. Dan --- On Sun, 3/31/13, Chris Mason cometenergysyst...@gmail.com wrote: From: Chris Mason cometenergysyst...@gmail.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches

Re: [RE-wrenches] Cable tray

2013-03-31 Thread Ryan
...@gmail.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: Sunday, March 31, 2013, 8:21 AM As we see more 1000V installations, chances are that 600V rated equipment will find its way into installations it is not rated for. To avoid

Re: [RE-wrenches] Cable tray

2013-03-31 Thread John Berdner
USA (*Please note of our new address.) T: 510.498.3200, X 747 M: 530.277.4894 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Exeltech Sent: Sunday, March 31, 2013 9:10 AM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray Hello

Re: [RE-wrenches] Cable tray

2013-03-31 Thread Chris Mason
/31/13, Chris Mason cometenergysyst...@gmail.comcometenergysyst...@gmail.com * wrote: From: Chris Mason cometenergysyst...@gmail.comcometenergysyst...@gmail.com Subject: Re: [RE-wrenches] Cable tray To: RE-wrenches re-wrenches@lists.re-wrenches.orgre-wrenches@lists.re-wrenches.org Date

Re: [RE-wrenches] Cable tray

2013-03-31 Thread Exeltech
specific aspects of the BOS hardware -- which I addressed. Regards to all, Dan Lepinski Sr. Engineer Exeltech / Exeltech Solar Products --- On Sun, 3/31/13, John Berdner john.berd...@solaredge.com wrote: From: John Berdner john.berd...@solaredge.com Subject: Re: [RE-wrenches] Cable tray

Re: [RE-wrenches] Cable tray

2013-03-30 Thread Jay Peltz
Hi Bill I'm with you all the way. I love to do things Telecomm style. Very clean, safe and better IMHO. 1000v PV wire can be bought at PV cables.com Cheers Jay Peltz Power. ___ List sponsored by Home Power magazine List Address:

Re: [RE-wrenches] Cable tray

2013-03-29 Thread Bill Loesch
mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Allan Sindelar *Sent:* Wednesday, March 27, 2013 8:51 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Cable tray Andrew, We have used #10 USE-2 for about 16 years, and our high-elevation New Mexico sun

Re: [RE-wrenches] Cable tray

2013-03-29 Thread Bill Hoffer
-wrenches *Subject:* Re: [RE-wrenches] Cable tray Bill: I have to disagree with you on this one. We can not abandoned a tried and true practice just because some practitioners don't do it right. I don't know how one can justify saying that encapsulating high voltage conductors in a conduit

Re: [RE-wrenches] Cable tray

2013-03-28 Thread Chris Mason
: 530.277.4894 ** ** *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Allan Sindelar *Sent:* Wednesday, March 27, 2013 8:51 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Cable tray ** ** Andrew, We have used

Re: [RE-wrenches] Cable tray

2013-03-28 Thread Allan Sindelar
hes-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Tuesday, March 26, 2013 9:49 PM To: RE-wrenches Subject: Re: [RE-

Re: [RE-wrenches] Cable tray

2013-03-27 Thread Andrew Truitt
-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Tuesday, March 26, 2013 9:49 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray Bill: I have to disagree with you on this one. We can not abandoned a tried and true practice just because some practitioners

Re: [RE-wrenches] Cable tray

2013-03-27 Thread Allan Sindelar
rch 26, 2013 9:49 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray Bill: I have to disagree with you on this one. We can not abandoned a tried and true practi

Re: [RE-wrenches] Cable tray

2013-03-27 Thread John Berdner
] On Behalf Of Allan Sindelar Sent: Wednesday, March 27, 2013 8:51 AM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray Andrew, We have used #10 USE-2 for about 16 years, and our high-elevation New Mexico sun is quite intense. I have yet to see any degradation exceeding fading discoloration on any

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Mark Richardson
-wrenches' Subject: Re: [RE-wrenches] Cable tray All, Here is the language that has been accepted into the 2014 NEC: 690.31(C)(2) (2) Cable Trays. PV source circuits and PV output circuits using single-conductor cable listed and labeled as Photovoltaic (PV) wire of all sizes with or without

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Glenn Burt
). Too bad we are still on the 2008 code cycle here. Thanks Glenn Burt From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Monday, March 25, 2013 10:54 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Cable tray

Re: [RE-wrenches] Cable tray

2013-03-26 Thread David Brearley
-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Monday, March 25, 2013 10:54 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Cable tray All, Here is the language that has been accepted into the 2014 NEC: 690.31(C)(2

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Chris Mason
I don't understand how it can be permissible to string the PV wire over the rails, under the modules, and in the rail channels, but not permissible to put it in purpose made cable trays. Makes no sense. ___ List sponsored by Home Power magazine List

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Glenn Burt
. The devil is in the details. From: David Brearley [mailto:david.brear...@solarprofessional.com] Sent: Tuesday, March 26, 2013 12:51 PM To: glenn.b...@glbcc.com; RE-wrenches Subject: Re: [RE-wrenches] Cable tray Not at all. Type USE cable was added to the Permitted Uses of Cable Tray

Re: [RE-wrenches] Cable tray

2013-03-26 Thread William Miller
, March 25, 2013 9:30 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray David: Of course, I understand that you are not saying we can willfully disregard the Code in anticipation of future clarification. I was just extrapolating on your idea. If we want an exception based on a predicted

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Bill Brooks
: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Tuesday, March 26, 2013 9:49 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray Bill: I have to disagree with you on this one. We can not abandoned a tried

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Mark Richardson
-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Mason Sent: Sunday, March 24, 2013 8:24 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray We use Cablofil but at $10/ft, it's OK for the inverter area but for large roofs, it is expensive. On Sun, Mar 24, 2013 at 3

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Glenn Burt
: Friday, March 22, 2013 3:08 PM To: RE-wrenches Subject: [RE-wrenches] Cable tray I'm looking for flat roof cable tray system that is cost effective. We previously used Cablofil and Cablo-port FSL 12 tray but it is very expensive for our current application due to the size of the roof. We need

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Chris Mason
** ** *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason *Sent:* Friday, March 22, 2013 3:08 PM *To:* RE-wrenches *Subject:* [RE-wrenches] Cable tray ** ** I'm looking for flat roof cable tray system that is cost

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Glenn Burt
392.3(B)1 This was also pointed out in a recent article in Solar Pro talking about Wire Management issues. From: Chris Mason [mailto:cometenergysyst...@gmail.com] Sent: Monday, March 25, 2013 6:17 PM To: glenn.b...@glbcc.com; RE-wrenches Subject: Re: [RE-wrenches] Cable tray What part

Re: [RE-wrenches] Cable tray

2013-03-25 Thread David Brearley
-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Mason Sent: Friday, March 22, 2013 3:08 PM To: RE-wrenches Subject: [RE-wrenches] Cable tray I'm looking for flat roof cable tray system that is cost effective. We previously used

Re: [RE-wrenches] Cable tray

2013-03-25 Thread William Miller
David: This is great news. Now, whenever I want to do something that is prohibited by code, I can just say that the Code Making Panel is gonna correct that pesky code section (insert your problem citation here) any day now, so I might as well be allowed to do whatever it was I was fixin' to

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Chris Mason
] *On Behalf Of *Chris Mason *Sent:* Friday, March 22, 2013 3:08 PM *To:* RE-wrenches *Subject:* [RE-wrenches] Cable tray ** ** I'm looking for flat roof cable tray system that is cost effective. We previously used Cablofil and Cablo-port FSL 12 tray but it is very expensive for our current

Re: [RE-wrenches] Cable tray

2013-03-25 Thread David Brearley
Ouch. I promise I'm not advocating for anything like that. What I may be missing is the Code reference that says no cable tray on roofs or similar. There is so much room for improvement in wire management practices, that being able to use cable tray seems like a step forward. I understand some

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Bill Brooks
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley Sent: Monday, March 25, 2013 6:01 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable tray Ouch. I promise I'm not advocating for anything like that. What I may be missing is the Code reference that says no cable tray on roofs

Re: [RE-wrenches] Cable tray

2013-03-25 Thread David Brearley
1.4m (4.5’). I hope this helps. It is a very big deal. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley Sent: Monday, March 25, 2013 6:01 PM To: RE-wrenches Subject: Re: [RE-wrenches] Cable

Re: [RE-wrenches] Cable tray

2013-03-25 Thread William Miller
David: Of course, I understand that you are not saying we can willfully disregard the Code in anticipation of future clarification. I was just extrapolating on your idea. If we want an exception based on a predicted update in the code, we are at the mercy of the AHJ who may or may not be

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Bill Brooks
-wrenches Subject: Re: [RE-wrenches] Cable tray David: Of course, I understand that you are not saying we can willfully disregard the Code in anticipation of future clarification. I was just extrapolating on your idea. If we want an exception based on a predicted update in the code, we

Re: [RE-wrenches] Cable tray

2013-03-24 Thread Chris Mason
Generation -- *From:* Chris Mason cometenergysyst...@gmail.com *To:* RE-wrenches re-wrenches@lists.re-wrenches.org *Sent:* Friday, March 22, 2013 12:07 PM *Subject:* [RE-wrenches] Cable tray I'm looking for flat roof cable tray system that is cost effective. We

Re: [RE-wrenches] Cable tray

2013-03-24 Thread Kirk
Engineer SEE Systems 1048 Irvine Ave Suite 217 Newport Beach, Ca. 92660 760-403-6810 Building a Better Future For The Next Generation From: Chris Mason cometenergysyst...@gmail.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Friday, March 22, 2013 12:07 PM Subject: [RE-wrenches

Re: [RE-wrenches] Cable tray

2013-03-24 Thread Chris Mason
-- *From:* Chris Mason cometenergysyst...@gmail.com *To:* RE-wrenches re-wrenches@lists.re-wrenches.org *Sent:* Friday, March 22, 2013 12:07 PM *Subject:* [RE-wrenches] Cable tray I'm looking for flat roof cable tray system that is cost effective. We previously

Re: [RE-wrenches] Cable tray

2013-03-23 Thread Max Balchowsky
: [RE-wrenches] Cable tray I'm looking for flat roof cable tray system that is cost effective. We previously used Cablofil and Cablo-port FSL 12 tray but it is very expensive for our current application due to the size of the roof. We need to install about 200' of tray and Cablofil galvanized

Re: [RE-wrenches] Cable tray versus RMC

2011-02-16 Thread Carl Adams
Larry, We do have the option of no roof penetrations and that is the course being taken. We will have 90 source circuits in the array and 5 Jboxes on the roof and these will then be routed to a vertical wall on the west end of the array. The strings will carry through the wall horizontally and