RE: Distilled spirits

2022-03-07 Thread Bob Caputo via Sprinklerforum
Steve, I suggest looking at the FM Guidelines on distilled spirits, I have a copy somewhere if you need it or any help drinking the evidence Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Steve Leyton via Sprinklerforum Sent: Monday, March 7, 2022 3:23 PM To:

RE: INDOOR SPORTS FACILITY FIELD HOUSE

2022-02-07 Thread Bob Caputo via Sprinklerforum
Not in my opinion. We should always look at the definitions for each occupancy classification as opposed to the list in the annex. These facilities have a lot of plastics and combustibles that exceed the definition of light hazard and they are of heights exceeding 8 ft so OH1 is probably not

RE: swimming pool

2022-02-07 Thread Bob Caputo via Sprinklerforum
For what its worth, in the 2013 code cycle of NFPA 13, I submitted two proposed changes related to this topic. The first was to eliminate sprinklers directly above the water where indoor swimming pools were present. This was rejected by the committee with the statement that indoor pools are not

Re: UNUSED ATTIC DEFINITION

2022-01-15 Thread Bob Caputo via Sprinklerforum
Tim, In defense of the committee and its members, NFPA standards state clearly that where terms are not specifically defined in chapter 3, Mirriam Webster Collegiate Dictionary, 11th edition definitions shall be used. Unused mean no storage in this context and the standard does provide

Re: Airing of Grievances

2021-12-29 Thread Bob Caputo via Sprinklerforum
Scot, Thank you for your commentary on this subject and for sharing your opinion on the subject of open discussion related to money however, as I stated earlier, this is not the place for it. As president of the AFSA, it is my responsibility to ensure we deliver on out mission statement for

Re: Airing of Grievances

2021-12-28 Thread Bob Caputo via Sprinklerforum
Mr. Leyton, While I agree with you in spirit and in practice, please refrain from discussing specific pricing models within the forum or and AFSA venue or medium. Doing so may be considered a form of price fixing which is both frowned upon and illegal. AFSA is a non profit trade

RE: Purpose of Subdividing Dry Systems?

2021-12-21 Thread Bob Caputo via Sprinklerforum
As noted in the NFPA 13, 2013 edition handbook, "Prior to the 2010 edition, 7.2.3.9 conflicted with the requirement in 7.4.4.1 that combined dry pipe and preaction systems be subdivided as well as contradictory to the requirement in 7.9.2.8.4(5) for separate indicating control valves and check

Re: Sprinkler protection in a freezer warehouse - with plastics

2021-12-14 Thread Bob Caputo via Sprinklerforum
Craig, As you know, the commodity classification is based on the product, the packaging and the pallet type. As such, your foam trays have to be taken into account by weight or by volume. NFPA 13, Fig 20.4.3.3(a) and (b) and I don’t have a book with me but pretty sure frozen food on polystyrene

Re: NFPA #30 Containment

2021-12-14 Thread Bob Caputo via Sprinklerforum
I am out of the country (without my books) but from recollection, the time frame is based on the H occupancy classification form the IFC/IBC, where H9 has a longer duration than H3. Not sure its in NFPA 30. It’s definitely sprinkler discharge rate plus the volume of the largest vessel though. I

Re: Mechanical roll-grooved fittings for fire pipe

2021-12-14 Thread Bob Caputo via Sprinklerforum
NFPA 13 does provide rules for grooved piping. These rules are copied from the 2016 edition, so the current edition section numbers will be different. 6.5.3.1* Pipe, fittings, valves, and devices to be joined with grooved couplings shall contain cut, rolled, or cast grooves that are

RE: Paint Booth Duct Protection

2021-12-03 Thread Bob Caputo via Sprinklerforum
@lists.firesprinkler.org Cc: Dennis Wilson Subject: RE: Paint Booth Duct Protection Only the exhaust duct is normally sprinklered. -Original Message- From: Sprinklerforum On Behalf Of Bob Caputo via Sprinklerforum Sent: Thursday, December 2, 2021 12:23 PM To: sprinklerforum@lists.firesprinkler.org

Re: Paint Booth Duct Protection

2021-12-02 Thread Bob Caputo via Sprinklerforum
Generally, if the exhaust duct Carrie’s flammable or combustible vapors it does On Thu, Dec 2, 2021 at 9:49 AM Jerry Van Kolken via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > I have a paint booth with a intake and exhaust duct systems. > > When I look at NFPA 33-9.5.1.6

RE: theft of FDC inlets

2021-10-15 Thread Bob Caputo via Sprinklerforum
There are ways to replace the FDC swivels - here are a few links. AFSA does not endorse specific manufacturers or suppliers - this is simply offering potential solutions for FDC repair.

RE: Attic protection over a storage occupancy

2021-10-06 Thread Bob Caputo via Sprinklerforum
NFPA 13, 2019 edition section A.4.3.2(16) lists unused attics as light hazard. That said, it's always better to consider the definition of the hazard as opposed to automatically applying the lists from the annex. Section 4.3.2 defines LH as spaces with low quantity and combustibility of contents.

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Bob Caputo via Sprinklerforum
NFPA 20 is clear that the pump room is to be protected per EH2. By definition of EH2, the presence of the diesel fuel makes it EH2. See 4.14.1.3 Bob Caputo, CFPS President American Fire Sprinkler Association -Original Message- From: Sprinklerforum On Behalf Of James Crawford via

RE: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread Bob Caputo via Sprinklerforum
Not to mention it’s a horrible practice in my opinion Bob Caputo, President American Fire Sprinkler Association -Original Message- From: Prahl, Craig/GVL Sent: Thursday, August 19, 2021 5:07 PM To: Bob Caputo ; sprinklerforum@lists.firesprinkler.org Cc: John Denhardt Subject: RE:

RE: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread Bob Caputo via Sprinklerforum
The prior editions of NFPA 24 do not restrict the use of non-metallic spigot pieces (riser coming up through the floor from the underground piping) I discovered this fact a few years ago, while responding to the question when doing Advisory Service for NFPA. I was surprised and concerned for all

RE: Material Prices !!

2021-08-05 Thread Bob Caputo via Sprinklerforum
The AFSA Forum is intended to be used for the sharing of ideas and technical questions or issues. We do not allow, or condone any conversations related to pricing on any level. Please take this topic off line. It is not appropriate for this forum and will be deleted by the administrator. Thank

Re: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
The committee discussion on this change was the in a 400 cubic foot enclosure, it doesn’t matter where the sprinkler is relative to the shelf. Think about in rack sprinklers and the product loads…. I agree there should be concern for bumping the sprinkler but no one is loading the closet with

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
Pete, You are correct. Where the closet is less than 400 ft3, no clearance is required below the deflector Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To:

RE: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-05-19 Thread Bob Caputo via Sprinklerforum
demands need to be added together. Just if a fire pump supplies both per > NFPA 13 11.1.5.3, then fire pump gpm has to be able to meet both not just > the greater of the two. > > Thanks, > Gregg Fontes > Cen-Cal Fire Systems, Inc. > 209-334-9119 > > -----Original Mess

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Bob Caputo via Sprinklerforum
 On Fri, May 7, 2021 at 11:23 AM Michael Hill via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > There goes my logic, right out the window..again. > > Mike Hill > > -Original Message- > From: Sprinklerforum On > Behalf Of Bob Caput

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Bob Caputo via Sprinklerforum
No, you are not permitted to use elevation pressure from a gravity tank. You do not know the elevation of the water in the tank which is depleted during the operation of the systems in fighting the fire. You are permitted to use the pumps productive curve at 150% of rated flow and 65% of rated

Re: Hydrant barrel loss

2021-04-26 Thread Bob Caputo via Sprinklerforum
Sincerely you’re measuring the flow and pressure at the hydrant in the first place, why would you need to know that? Just curious... Reverse engineering the water supply in the water main below? On Mon, Apr 26, 2021 at 3:57 PM Steve Leyton via Sprinklerforum <

Re: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-04-23 Thread Bob Caputo via Sprinklerforum
e if site and fire sprinkler > demands need to be added together. Just if a fire pump supplies both per > NFPA 13 11.1.5.3, then fire pump gpm has to be able to meet both not just the > greater of the two. > > Thanks, > Gregg Fontes > Cen-Cal Fire Systems, Inc. > 209-334-9

Re: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-04-23 Thread Bob Caputo via Sprinklerforum
Lots of great responses to this question, the best of which is that it is really up to the local AHJ to determine what will be required. That said, in the context of NFPA 13 (2016 edition) we should note two specific applicable sections in consideration of the issue: First, section 3.8.2.1.3

Re: Old sprinklers

2021-04-08 Thread Bob Caputo via Sprinklerforum
This may have been approved by the local AHJ, which would be the appropriate assumption based on NFPA 25. We are not doing a design analysis. On Thu, Apr 8, 2021 at 9:34 AM Dale Wingard via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Sounds like the intent was to protect

Re: Different Levels of protection open to each other in the same hazard

2021-03-19 Thread Bob Caputo via Sprinklerforum
BTW, I probably should have included in my comments, the requirements for floor control valve assemblies in NFPA 13, 2019 edition section 16.9.11, which might be applicable to Jerry’s situation. Again, I may have missed the point of the original question…. But I’m old so I have an excuse!

Re: Different Levels of protection open to each other in the same hazard

2021-03-19 Thread Bob Caputo via Sprinklerforum
Jerry, NFPA 13 is clear that it is the designers responsibility to design the system and chose the design method. It is the AHJs (reviewer’s) responsibility to review the submitted design for acceptance to adopted codes and standards. Unless the reviewer in your case is the owner’s

Re: Question about a drop pipe size

2021-03-18 Thread Bob Caputo via Sprinklerforum
Henry, I’m not sure why the forum site would have disallowed your question but I will inquire with our IT people. To your specific question, NFPA 13, 2019 edition was reorganized (as you know) and all existing system modification requirements were moved to Chapter 29. The use of a 4”

Re: leaving abandoned sprinkler piping in place

2021-03-17 Thread Bob Caputo via Sprinklerforum
NFPA 13, 2019 edition actually addresses this in section 29.2 Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org

Re: Fire Retardant Coating used in Combustible concealed spaces

2021-02-10 Thread Bob Caputo via Sprinklerforum
Actually, the coating would be allowed under the equivalency clause with approval of the AHJ. With AHJ approval, the 3000 sq ft rule could also be ignored. Some years ago, I made the mistake of saying no to this question while doing interpretations for NFPA as a consultant and almost got them

Re: Distilled Spirits

2021-02-03 Thread Bob Caputo via Sprinklerforum
FM Global has a standard for this specifically. I recommend downloading it from their website. Great information that might provide guidance for you. Bob Caputo, CFPS President American Fire Sprinkler Association p: 214-349-5965 ext124 w: firesprinkler.org

Re: schedule 7 pipe?

2021-01-20 Thread Bob Caputo via Sprinklerforum
Jeff Normand is correct in terms of the 1st exposed thread at the fitting having less depth of material than a schedule 10 roll groove, however most corrosion we see is related to oxidation as opposed to MIC. The problem with roll grooves tends to be water trapped between the grooves sitting

Re: Merry Christmas,

2020-12-25 Thread Bob Caputo via Sprinklerforum
Thank youSame to you and yours On Fri, Dec 25, 2020 at 10:38 AM Mario Berrios via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Merry Christmas, > mario berrios > ___ > Sprinklerforum mailing list >

Re: potential freezing in ESFR system

2020-12-22 Thread Bob Caputo via Sprinklerforum
Matt, Not sure many people are lurking around the forum this week, so I’ll offer my 2 cents worth…. 1st and foremost, I would get the GC to sign off on a letter stating that you are not responsible for any freeze damage resulting from their request to perform the hydro prior to having heat in