RE: ESFR obstruction in non-storage

2015-06-11 Thread RFletcher
We deal with this all the time. Lacking any direction in 13 it just comes down to what the AHJ will accept? It's ridiculous to not allow standard SSP obstruction rules for ESFR's if there is no storage but that is my opinion as a contractor. We are just completing a demo and retrofit of a

RE: Light or Ordinary Hazard

2015-05-08 Thread RFletcher
Wouldn't 8.3.2.1 ('13) apply? It allows ordinary and intermediate temperature to be used throughout buildings. Doesn't 8.3.2.1 make it okay to use intermediate temperature throughout the nursing home? Ron F -Original Message- From: Sprinklerforum

RE: Light or Ordinary Hazard

2015-05-08 Thread RFletcher
New in the 2010 Edition. It's explained very clearly in the 2010 Handbook. the standard now groups ordinary and intermediate temperature sprinklers together and allows intermediate temperature sprinklers throughout the building, reducing the need for multiple types of sprinklers. Ron F

Re: Heat Tracing

2015-04-22 Thread RFletcher
Heat trace? Florida? Ron fletcher Sent from my iPhone On Apr 22, 2015, at 12:37 PM, Pete Schwab pe...@waynefire.com wrote: I am searching for an installer of heat tracing (Listed for fire protection) in Florida If you have a contact you can share it is greatly appreciated. Thanks

RE: NFPA 409 2011 6.1., 6.1.2, 7.2

2015-04-17 Thread RFletcher
My hard copy of 409-2011 edition is the same as Greg quoted. 6.1.2 Group I aircraft hangar storage and service area shall be provided with protection in accordance with 6.1.1 or with automatic sprinkler protection as specified in Section 7.2 and 7.8. When I pull up 409 go on line 6.1.2 is as

Re: Bottom of elevator shaft protection

2015-04-01 Thread RFletcher
Just curious, do you have a code reference for mech rooms as OH1? Ron fletcher Sent from my iPhone On Apr 1, 2015, at 6:35 AM, Matthew J Willis ma...@rapidfireinc.com wrote: I had the 10 in parenthesis, my apologies Also I forgot to add.., OH1 because it is a mechanical room after all.

RE: Large pumping capacity

2015-03-26 Thread RFletcher
With 3 pumps, 2 needed and one backup the suction and discharge header should be sized for 2 pumps. 16 pipe would result in a suction velocity of less than 10 fps, I believe that is the recommended limit in NFPA 20. All common pipe subject to the full flow of two pumps should be sized

RE: ESFR Sprinkler Heads

2015-03-19 Thread RFletcher
We always split the systems where the K factor changes. However, if the addition is small the total area is under 40k sqft you would probably have to change all the heads on that system to K17. Ron F -Original Message- From: Sprinklerforum

Re: Underground Piping Under Slab

2015-02-20 Thread RFletcher
Makes it more fun proving to a contractor that it's a NEW change. Ron fletcher Sent from my iPhone On Feb 20, 2015, at 3:01 PM, Roland Huggins rhugg...@firesprinkler.org wrote: NFPA has at least temporarily stopped flagging the sections that have changed. Not sure how long this will

RE: Underground Piping Under Slab

2015-02-13 Thread RFletcher
10.6.3.1* (13 Ed.) The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire service mains enter under the building no more than 10 ft (3 m) as measured from the outside edge of the building to the center of the vertical pipe. Ron F -Original Message- From: Sprinklerforum

RE: NFPA 13 FM Mix

2015-02-12 Thread RFletcher
Many times we have done two submittals. One to the AHJ with all NFPA requirements and another to FM with their requirements. One example is the local AHJ may require a 10% reduction to the flow test and .2/1500 for OH2. FM does not mandate any reduction to the flow test but will require .2/2500

Re: Relocate sprinklers with drops RETORT

2015-02-06 Thread RFletcher
Like shipping, unpacking and installation only applies the proper and necessary stress for the sprinkler to operate as intended. Or maybe the engineering is so precise that the sprinkler can only stand the rigors of being threaded into a fitting once and then it's useless. Or maybe there are

RE: foam delivery times

2015-01-30 Thread RFletcher
I have always just done cowboy math to give them a rough idea of delivery time. Volume of system piping/demand gpm=approximate time (500 gallon volume/1000 gpm demand = .5x60=30 seconds) to get water to the last generator. There will typically be at least one timed discharge test with just

RE: Hot box or other types of exterior fire riser enclosures

2015-01-27 Thread RFletcher
We build what we call a pump in a box 10'X18' but it could be made smaller to house only risers. They are structurally designed for the conditions at the intended location, all metal siding and roof with a structural steel base. Pre-piped, insulated, heated, lighting, fire alarm conduit and an

RE: Bracing for Pipe on Pipe Stands

2015-01-08 Thread RFletcher
We have started running the bypass line on the floor instead of over the pump as usual so that it can be braced to the floor. Sometimes there isn't anything around a pump to brace to other than the floor. We also brace the legs of the fuel tank to the wall or floor. Ron F -Original

Re: Pressure Relief Valve on Wet Pipe System

2015-01-07 Thread RFletcher
Things are a pain. They have to be plugged for the 200# test. Then drain the system to reconnect. We put a ball valve before the relief so we can test and reconnect without draining. Ron fletcher Sent from my iPhone On Jan 7, 2015, at 12:05 PM, Aaron Peck amp...@me.com wrote: I wonder if

Re: Conveyor equipment in storage occupancies

2015-01-05 Thread RFletcher
What edition of 13 are you using? Ron fletcher Sent from my iPhone On Jan 5, 2015, at 12:16 PM, Steve Leyton st...@protectiondesign.com wrote: So ... I get hired to write a tech report on an S-1 occupancy and it's pretty straightforward since the existing (brand new and never occupied)

RE: A Poll of the Experienced

2014-12-09 Thread RFletcher
I did the flow test. S-170 R-155, 3950 gpm through a 4 diffuser. The best part was at a meeting when the Fire Marshall said that they may reject our plans because required fire flow is 4,000 gpm and the flow test was 50 gpm short. I am not kidding. Luckily we they approved our plans despite the

Re: transverse flue space clarification

2014-12-09 Thread RFletcher
If there are rack uprights with horizontal and diagonal bracing but no permanent fixed solid shelving I would say that you have transverse flue spaces. My 2 cents. Ron fletcher Sent from my iPhone On Dec 9, 2014, at 5:25 PM, Greg McGahan g...@livingwaterfp.com wrote: Storage of non-typical

RE: A Poll of the Experienced

2014-12-08 Thread RFletcher
Absolutely agree with you about the non-value of extrapolating the flow test beyond the observed flow. The part I'm not so sure I would agree with is requiring the 20 psi minimum at the onsite hydrants. The IFC commentary notes that the 20 psi is used because it is the recommended minimum

RE: Balancing In-Rack Sprinklers

2014-12-04 Thread RFletcher
Sounds like you are K'ing the overhead system into the racks, if should the other way around. K the racks into the overhead system. Personally I would revisit the calc's and make them balance. A 15 psi difference is too far apart. Ron F -Original Message- From: Sprinklerforum

RE: Contradiction if FDC codes? NFPA 13 2013

2014-11-25 Thread RFletcher
noun: supplement; plural noun: supplements - something that completes or enhances something else when added to it. How can the possibly pressure be supplemented? Using enough pressure to open the FDC check valve will close the valve in the riser. The rule should be changed to either calculated

CA Title 8

2014-11-11 Thread RFletcher
We have been working in CA for some years now and it seems like something new and counterintuitive comes up every time we start a new project. A GC is telling us we have to get a CA Department of Industrail Relations, Division of Occupational Safety Health (CAL/OSHA) safety permit. It is

RE: FM Global requirements

2014-11-10 Thread RFletcher
If your contract requires you to meet both I would double check everything you do against the FM Global data sheets. We have come across some differences that are, let's say counterintuitive. For instance FM no longer seems to recognize concrete twin tee construction like NFPA does. FM limits

RE: Expansion Joint vs. Seismic Expansion Joint

2014-10-22 Thread RFletcher
I have always thought every USACoE project required seismic bracing no matter the location. I believe (going by memory) that a coupling is required within 2 ft. of an expansion joint and the 6 elbow thing at a seismic joint. Ron F -Original Message- From: Sprinklerforum

RE: Shadowed area behind built in cabinet and in widow sill

2014-10-06 Thread RFletcher
1.7 New Technology Nothing in this standard shall be intended to restrict new technologies or alternate arrangements... Based on the recently discussed conservative committee actions I would think that anything in the later editions of 13 should be allowed as an alternate arrangement. Say

RE: Shadowed area behind built in cabinet and in widow sill

2014-10-06 Thread RFletcher
I will more than likely be admonished for this, again. But it's more likely the hole occupied by an uniformed, unqualified or unreasonable AHJ. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bill Brooks Sent: Monday,

RE: Pressure Limiting Drivers

2014-10-02 Thread RFletcher
Very effective, we use them all the time. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Hairfield Sent: Thursday, October 02, 2014 10:48 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Pressure Limiting

RE: Pressure Limiting Drivers

2014-10-02 Thread RFletcher
They add $3-5k to the price of a pump. Depending on static versus residual they can really payoff in usable pressure without having to be concerned with the churn pressure. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf

RE: No Longitudinal Bracing

2014-09-19 Thread RFletcher
If it is in a seismic zone. We do 4 ways at the top of risers only even though Phoenix is not in a seismic zone. Maybe that is what he saw. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Friday,

RE: Water Velocity

2014-09-16 Thread RFletcher
Ironic that the ETL also requires surge tanks. Belt and suspenders or ignorance? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reed A. Roisum, C.E.T. Sent: Tuesday, September 16, 2014 10:32 AM To:

RE: flex-coupling at water tank

2014-09-12 Thread RFletcher
I have seen a gimbal type arrangement used above ground outside. I guess if freezing is an issue a hot box or putting it in a vault would be an option. I have some pictures if that would help. Sorry I don't have any manufacturer or model information. They were used on a COE job on an Army base.

RE: fume hood / dust collector - sprinklers in?

2014-09-08 Thread RFletcher
Battlefield earth? -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Monday, September 08, 2014 9:42 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: fume hood / dust collector - sprinklers in?

RE: Seismic bracing

2014-09-05 Thread RFletcher
Some jurisdictions around here require what we call feel good bracing. They don't require calculations, or that the building be designed to any seismic standard, they just want the minimum bracing. If we want a green tag we have to put it in. I guess in this case the question would be if the

RE: Seismic bracing

2014-09-05 Thread RFletcher
If I did I would have a pile of hold harmless up to the ceiling. We call them piping alignment braces, you know to help keep the piping in a straight line. Where's the liability in installing too many supports? Ron F -Original Message- From: Sprinklerforum

RE: Seismic bracing

2014-09-05 Thread RFletcher
Seems to me the AHJ's need the education more than the contractors. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of wmens...@comcast.net Sent: Friday, September 05, 2014 8:58 AM To: sprinklerforum Subject: Re: Seismic

RE: Seismic bracing

2014-09-05 Thread RFletcher
Since it is an existing building I doubt any of the things you have listed will be done. I guess I look at getting it done without doing any harm so the owner can use the building. The alternative appears to be telling the owner it's not their responsibility and that he has to get an architect,

RE: ESFR Table 17.2.3.1 NFPA 13 2013

2014-08-22 Thread RFletcher
I disagree. S-1 occupancies have roof slopes less than 2/12 so they are considered flat and I have seen many ceilings that are sloped greater than 2/12. Also there are warehouses with a couple high bays of 50-60' with the rest of the building at 40'-36'. Applying NFPA's interpretation would

RE: ESFR Table 17.2.3.1 NFPA 13 2013

2014-08-21 Thread RFletcher
I would say the maximum height is meant to apply the area of storage and not the maximum height of the entire building. A.17.2.3 Storage in single-story or multistory buildings can be permitted, provided the maximum ceiling/roof height as specified in chapter 12 is satisfied for each storage

Re: ESFR Table 17.2.3.1 NFPA 13 2013

2014-08-21 Thread RFletcher
Wouldn't be the first time I thought the NFPA interp was wrong and I think that again now. Ron fletcher Sent from my iPhone On Aug 21, 2014, at 4:34 PM, Steven P. Biship sbis...@pacificfireeng.com wrote: I actually called NFPA a couple weeks ago for an unofficial interpretation for this

Re: ESFR Sprinkler in Racks.

2014-08-14 Thread RFletcher
It was an unusual condition. 8 ft deep ssingle rack against a wall, no flues, plywood barrier fit tight to the wall. Mattresses below and cartooned stge above. Added to existing ESFR Whse Ron fletcher Sent from my iPhone On Aug 14, 2014, at 7:24 AM, Roland Huggins rhugg...@firesprinkler.org

Re: ESFR Sprinkler in Racks.

2014-08-13 Thread RFletcher
Last time we did one we called the solid shelf a mezzanine and put the correct density under with ESFR at roof. Ron fletcher Sent from my iPhone On Aug 13, 2014, at 3:34 PM, Roland Huggins rhugg...@firesprinkler.org wrote: open ___

RE: Texas code set

2014-07-29 Thread RFletcher
Too funny. I once saw a set of plans reviewed by Andy that said Rejected - Do Not Resubmit until redrawn by an experienced designer. Or something to that effect. I went to his office one time, there were plans everywhere. Ron F -Original Message- From: Sprinklerforum

RE: Segue to AHJ's from CPVC Underground

2014-07-21 Thread RFletcher
Anything would be better than here's your badge and unlimited authority. One the biggest problems I find is that the higher up the chain of command we go the less they know about codes and plan review. The Chief tries to hire experienced people and is reluctant to overrule them because he/she

RE: Segue to AHJ's from CPVC Underground

2014-07-21 Thread RFletcher
To show how futile it is here is word for word the letter they wrote minus the names and places. Per our discussion on 7/14/2014 regarding the Fire Pumps at Blah Blah Parkway, Project Blah Blah, within Blah Blah industrial center, Blah Blah Blah Fire Protection District is exercising its right

RE: Motor operated valve controller

2014-07-21 Thread RFletcher
Can you rig up something that uses whatever level sensing devices the tank already has? Otherwise they now make a sonic sensor that can mount to the inside top of the tank. You should be able to get a signal from it to operate a valve. Ron F -Original Message- From: Sprinklerforum

Re: Blazemaster CPVC Underground

2014-07-21 Thread RFletcher
I feel your pain. Ron F Ron fletcher Sent from my iPhone On Jul 21, 2014, at 12:10 PM, Tony Liddic tony.lid...@mrhsprinklerdesign.com wrote: AHJ has spoken with Mfr Rep directly and has basically decided to forgo common sense. The only way he will approve it is if NFPA 13R includes

Re: Segue to AHJ's from CPVC Underground

2014-07-20 Thread RFletcher
I am filing an appeal, for all the good it will do. Have to get CofO then I can fight the the good but futile fight. Ron fletcher Sent from my iPhone On Jul 20, 2014, at 5:10 PM, John Drucker - Home john.druc...@verizon.net wrote: Actually you get a notice of violation, order to pay

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
The stance of the AHJ is that their unwritten policy is pumps can only be used at 100%. They also believe that 1500 gpm pumps will only produce 1500 gpm, and we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think pressure is even a factor. Ron fletcher Sent from my iPhone On Jul

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
It's a mystery. An AHJ in a different jurisdiction but in same metro area said she didn't know if she would accept our flow test for the sprinkler Sys because we only flowed 3871 gpm and that they require 4000. The civil engineer had already modeled 4000 gpm for there drawings. Must be

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
The AHJ told me I don't care what the codes say. Do it my way or no CofO. I am appealing to the State FM while arranging to change the pumps to 2000 gpm. We have a written notice from the GC to get our plans approved. The GC has tried to reason with the badge. That's when he was told they would

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
Wouldn't say the GC is sitting with the badge. He took a run at, found it to be futile and is now rightly concerned about turning the bldg over on time. I'm sure at this point that we will change the pumps to 2000's and wait for the badge to go away before going back. We don't want lose money

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
Had a FPE registered in the state call the badge. They talked for an hour and the FPE thought he was making some headway. Badge said he would email something outlining their unpublished policies. 15 minutes later he called back and said the chief told him not put a anything in writing. End of

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
That's what I've been doing. The worst part besides the money is the wasted time and resources. I should be doing something productive, instead I'm trying to fix stupid. Ron fletcher Sent from my iPhone On Jul 19, 2014, at 9:51 AM, Rod DiBona r...@rapidfireinc.com wrote: As I have watched

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
Certainly it has occurred to me but I would hope that isn't the case. There are some union and some non in the area. While some may not like that we are in their backyard I prefer to think that this issue is just a lack of sophistication on ths part of the badge. Ron fletcher Sent from my

RE: Blazemaster CPVC Underground

2014-07-18 Thread RFletcher
That's a good one. I'll add that to my so you think you have heard everything list. Like saying it's approved below a valve but not above. Does he have a code reference or is this it just their opinion? Can you have someone from the manufacturer call them? Ron F -Original Message-

RE: Blazemaster CPVC Underground

2014-07-18 Thread RFletcher
I wish there was a way to deal with abusive AHJ's. It seems like every time we go into a new jurisdiction we have to waste time and money proving what we already know to be a fact. Then their ego gets hurt and they get stubborn. Ron F -Original Message- From: Sprinklerforum

Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
It's Friday so I figured I'd whine on the forum. To set the stage, prior to the letter I am referring to we had approved permitted drawings from the AHJ. The following is a quote from a letter we received from that same AHJ. At this time , Blah Blah Blah Fire Protection District is denying

RE: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
Yikes, that isn't very encouraging. The chief told us to go to the State FM is we wanted to appeal so there might be some hope. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Friday, July 18, 2014

RE: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
I told him that IFC didn't give him the power to do what he thinks. That's when he gave me the ultimatum. Can you believe he wrote a letter saying that we have to EXCEED the adopted codes? Ron F -Original Message- From: Sprinklerforum

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
All too true and I really enjoyed your metaphor with compost. I am trying give the badge what he wants. Schedule is the biggest issue. I just found out thAt I can buy two new pump cases keeping the same engines and have them re- labeled as 2000 gpm. Cost without labor $20-25k. The badge did

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
How about everything is per code except we have two pumps rather than one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most ignorant thing I have ever seen. Just found out the chief told plan reviewer no more written correspondence. I guess because they don't want a written

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
Can't say how much this pisses me off. Ron fletcher Sent from my iPhone On Jul 18, 2014, at 7:19 PM, Brad Casterline bcasterl...@fsc-inc.com wrote: You're alright like most of us the psychology part of sprinkler work just makes you want to throw up in your mouth a little bit , right?

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
Okay you explain the $40-50k hit to the bottom line Ron fletcher Sent from my iPhone On Jul 18, 2014, at 7:32 PM, Brad Casterline bcasterl...@fsc-inc.com wrote: Best not to dwell on any one project too much On Jul 18, 2014, at 9:28 PM, rfletc...@aerofire.com wrote: Can't say how much

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
I call ittroglydite infeztation Ron fletcher Sent from my iPhone On Jul 18, 2014, at 7:56 PM, Todd - Work t...@fpdc.com wrote: My favorite is home rule (aka we can make up whatever the heck we want) places like Texas. Did a small job for a company in a place around Houston. Was supposed

RE: FM Approved 8.0 K spray nozzle

2014-07-10 Thread RFletcher
8K spray nozzle is pretty odd device if you can't use standard spray sprinklers. Tyco D3's only go to 7.2K. I would talk to the FM rep about an alternative. I don't see why they would object If you can prove the impingement at the required density with smaller K Factor nozzles. Especially if

Re: Cooler Calc

2014-06-28 Thread RFletcher
We did a 45' high 40k sq ft beer cooler with ESFR's. After it was up and running we put temp recorders in front of reefer units. 30' up, 15' up and on floor. Recorded every 30 minutes for 5 days. Nothing varied more than one degree. Some one told me that the reefer units could not produce the

Re: Cooler Calc

2014-06-28 Thread RFletcher
38F. Yes an ESFR wet with 2 drops through the deck. Ron fletcher Sent from my iPhone On Jun 28, 2014, at 3:21 PM, Bobby Gillett bo...@livingwaterfp.com wrote: What temp was your beer cooler? You put a wet system in with ESFR's? Thank you, Bobby Gillett Living Water Fire Protection

RE: Cooler Calc

2014-06-27 Thread RFletcher
A couple questions. If it is a cooler why do you need dry pendent heads? And if it has to be dry heads and they are on a wet system the RA could still be reduced couldn't it? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On

RE: Cooler Calc

2014-06-27 Thread RFletcher
Exactly, we do 38F coolers with ESFR's. Never had a ..., I better not say that might jinx it. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Denhardt Sent: Friday, June 27, 2014 11:49 AM To:

RE: Underground Piping

2014-06-25 Thread RFletcher
In the friction loss formula found in 13-23.4.2.1.1 (13 Ed) I would use Q squared rather than Q to 1.85. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Rahe Loftin - 7PMC Sent: Wednesday, June 25, 2014 3:50 PM To:

Re: Location of Flow Test in Calc's

2014-06-19 Thread RFletcher
We do completely different drawings for the install crews. They don't need the hyd nodes or remote areas. Submittal plans have lots of info that isn't needed for installation. Ron fletcher Sent from my iPhone On Jun 19, 2014, at 6:38 AM, craig.pr...@ch2m.com craig.pr...@ch2m.com wrote:

RE: High Pressure ESFR

2014-06-16 Thread RFletcher
I have not heard one. Be great if there was though. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Monday, June 16, 2014 6:23 AM To: sprinklerforum@lists.firesprinkler.org Subject: High Pressure ESFR

RE: DRY HUMOR from NFPA

2014-05-30 Thread RFletcher
I can hear it now, the book says, shall be internally galvanized so there can't be any galvanizing on the outside of the pipe. The stuff we get is coated on the outside as well. How would an inspector tell if it was only galvanized on the inside? Maybe the next edition of 13 they can add a

RE: telecom rooms

2014-05-29 Thread RFletcher
I'd tell the engineer to site the code section that prohibits the pipe passing through. It's ridiculous but I have seen AHJ's interpret the thing about no unnecessary equipment to mean the pipe can enter but not leave an electrical equipment room. I don't think there is any code at all about

RE: Mixing EC-QR and SC-QR sprinklers in the same area

2014-05-28 Thread RFletcher
Yes, they can be mixed. We do it all the time. SC in entry and EC in sleeping room. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Pete Schwab Sent: Wednesday, May 28, 2014 8:49 AM To:

RE: Sheet Metal Pipe Sleeves

2014-05-19 Thread RFletcher
Have you tried Grainger? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Monday, May 19, 2014 11:14 AM To: sprinklerforum@lists.firesprinkler.org Subject: Sheet Metal Pipe Sleeves Someone missed the

RE: Thermal Barrier for Bathrooms

2014-05-16 Thread RFletcher
Seems like something that makes sense for wood frame buildings but not so much for noncombustible construction. The runaway shower enclosure fire had never occurred to me, guess I lack the imagination. Ron F -Original Message- From: Sprinklerforum

RE: Test Header Calc

2014-05-15 Thread RFletcher
Why not just read the gauges on the pump? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian Harris Sent: Thursday, May 15, 2014 8:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: Test Header Calc I'm running

RE: Test Header Calc

2014-05-15 Thread RFletcher
Okay, what am I missing? There are gauges on the suction and discharge sides of the pump, right? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tim Stone Sent: Thursday, May 15, 2014 8:36 AM To:

RE: Test Header Calc

2014-05-15 Thread RFletcher
Tim, So based on 47 psi at one test valve and just a flow on the rest, what was the pressure on the suction flange of the pump? Can't you just plot 1500 gpm on flow test curve and subtract the friction and elevation losses between the supply and pump? Brian, Pitot the discharge for each

RE: Thermal Barrier for Bathrooms

2014-05-15 Thread RFletcher
I just ran this very thing by the forum. The consensus was the barrier has to isolate the shower enclosure from the wall cavity so the sheet rock would have to be on both sides of the stud. Ron F -Original Message- From: Sprinklerforum

RE: Can a hydrant flow from the pumper connection be used for the hydraulic calculations ?

2014-05-14 Thread RFletcher
2012 IFC - APPENDIX B: B201.1 Definitions FIRE-FLOW. The flow rate of a water supply, measured at 20 PSI residual pressure that is available for fire-fighting. Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John

RE: Can a hydrant flow from the pumper connection be used for the hydraulic calculations ?

2014-05-13 Thread RFletcher
We use the 4 pumper connections for flow tests all the time. In Phoenix we have to calculate the 4,000 gpm fire flow onto the site and out of the private hydrants and I don't like doing hydraulic calc's out to 4,000 gpm using a graph from a 1,300 gpm flow test. The city water supply tends to

8.15.8.1.1 Bathrooms (2013)

2014-04-30 Thread RFletcher
States in part a 15 minute thermal barrier rating, including the walls and ceilings behind any shower enclosure or tub. Questions is, can there be a steel stud between the shower enclosure and the 15 minute barrier? Ron F ___ Sprinklerforum mailing

CA Title 19 Chapter 5

2014-04-18 Thread RFletcher
Anyone know if California Title 19 requires an inspector to write up spacing and placement issues or is it just for operation of the system per NFPA 25? Ron F ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org

Re: CA Title 19 Chapter 5

2014-04-18 Thread RFletcher
Thanks Steve. Thought you would know. Ron f Sent from my iPhone On Apr 18, 2014, at 4:43 PM, Steve Leyton st...@protectiondesign.com wrote: Many local AHJs want you to inform, but the state did not amend the NFPA 25 separation of design deficiencies from the ITM tasks. Steve

Obstructions against wall EC's

2014-04-11 Thread RFletcher
Just noticed Figure 8.8..1.2(c), 2013, it's new. It is also added for standard and residential heads. I tried to look up the ROP/ROC's but I lost my link and I can never find them through the menu system. The figure indicates a minimum depth of 18 for an obstruction (soffit) against a wall.

RE: Obstructions against wall EC's Fig. 8.8.5.2.2(c)

2014-04-11 Thread RFletcher
Glad you have submitted the comment. It will make more sense with those changes. Ron F -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Larry Keeping Sent: Friday, April 11, 2014 9:26 AM To:

Re: Diesel fuel tank

2014-04-09 Thread RFletcher
Is there.no exception in 20 if A double wall uL 142 tank. Ron f Sent from my iPhone On Apr 9, 2014, at 7:27 AM, Richard Mote rich...@rowesprinkler.com wrote: We had the builder layup 3 or 4 courses of 8 CMU block and had them coat the inside with a fuel proof coating. On one job they

Re: pump test header valves

2014-04-09 Thread RFletcher
Or, if possible keep headed in the pump room without valves, run hoses out to a truck mounted test rack with hose gates on the rack. This way the person reading the pitot can adjust the valves, Sent from my iPhone3200 USA Parkway McCarran‎ NV‎ 89434 United States On Apr 9, 2014, at 12:49 PM,

RE: heat collector vs heat director

2014-03-25 Thread RFletcher
Love engineer humor. Ron f From: sprinklerforum-boun...@lists.firesprinkler.org [sprinklerforum-boun...@lists.firesprinkler.org] on behalf of Todd - Work [t...@fpdc.com] Sent: Tuesday, March 25, 2014 9:40 AM To: sprinklerforum@lists.firesprinkler.org

Re:

2014-03-25 Thread RFletcher
We use intermediate for everything unless specifically forbiden. Have to watch out cuz some heads not available in intermediate. - Original Message - From: Jim Adams [mailto:tfscolor...@aol.com] Sent: Tuesday, March 25, 2014 01:11 PM To: sprinklerforum@lists.firesprinkler.org

RE: 1978 NFPA 13 question

2014-03-24 Thread RFletcher
NFPA #13, 1978, A-1-7.3.3 Warehouses having moderate to higher combustibility of content, such as household furniture , paint, general, a=storage, whisky etc. Ron F -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

P-A System Pendent Sprks

2014-03-13 Thread RFletcher
Here is a new one, for me anyway. Had a designer ask if it was okay to use exposed pendents on a pre-action system. He had it designed with uprights but due to field conditions the pipe was installed higher than designed and the foreman changed the heads to pendent. 13 says pendents have to be

RE: P-A System Pendent Sprks

2014-03-13 Thread RFletcher
No drops just a 1/2 head in a threaded tee or elbow. We are not us nitrogen. Ron F -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise Sent: Thursday, March 13, 2014 9:03 AM To:

RE: occupancy classification vs occupancy hazard

2014-03-12 Thread RFletcher
The interchangeable one I like most is expansion joint and seismic joint. Can't tell you how many times I have had AHJ's and EOR's write us up for not having a seismic joint in our pipe where it crossed an expansion joint. Actually had a structural engineer tell me there was no difference

RE: occupancy classification vs occupancy hazard

2014-03-12 Thread RFletcher
Nor do we usually receive the bid package early enough to ask questions and get answers. Ron F -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven Cook Sent: Wednesday, March 12, 2014 10:11

RE: Diesel Pump Generic Questions

2014-03-07 Thread RFletcher
I have never heard of a soft start diesel. I guess they could put a damper on the governor to prevent the throttle from opening quickly but I don't know what good it would do. Any pressure surge would be negligible unless there was a big air pocket in the system somewhere. For me it depends on

RE: Modifying sprinklers

2014-03-05 Thread RFletcher
It's done all the time. Do the hydro test then knock out the links. Ron F -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Wednesday, March 05, 2014 7:25 AM To: