[Sprinklerforum] Re: [External]Re: Jump Park

2024-11-13 Thread Fpdcdesign
Several years ago I did a large indoor playground (4000+ sqft). They had some larger pieces of equipment both wood and plastic. There were a couple of spaces that were actually storage rooms. The rooms got sprinklers. A lot of the unenclosed spaces didn’t because they were places kid

[Sprinklerforum] Re: Metal manufacturing

2024-10-28 Thread Fpdcdesign
com) > > > > > > > > > > > > > > > > > > > > From: Craig Hanson mailto:cra...@wc-3.com)> > > Sent: Thursday, October 24, 2024 12:48 PM > > To: Discussion list on issues relating to automatic fire s

[Sprinklerforum] Re: Metal manufacturing

2024-10-25 Thread Fpdcdesign
+1 for Tim Stone. Too often the contractor or their estimator are asked to figure out design criteria. That should fall upon the FPE. Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Oct 24, 2024 a

[Sprinklerforum] Re: Metal manufacturing

2024-10-24 Thread Fpdcdesign
n FPE and in accordance with IFC 104.7.2 and NFPA 13: 4.2(2022). The AHJ > should have requested that information also. These are tricky operations as > dissimilar metals create a deflagration issue. the design may also be outside > the scope of the NFPA 13 due to the process involved. Their insurance > compa

[Sprinklerforum] Duramax panels

2024-09-25 Thread Fpdcdesign
Does anyone have experience with Duramax ceiling panels? Per their specs, they are 100% pvc but have a flame spread rating of 10. Is that reasonable? It would put them in the category of Limited Combustible. Trying to figure protection requirements Todd G Williams, PE Fire Prot

[Sprinklerforum] Re: Draft hydrant

2024-09-16 Thread Fpdcdesign
nager| Bamford Fire Sprinkler Co., Inc. > P: 913.432.6688 > F: 913.432.5294 > M: 785.766.4894 > A: 5134 Merriam Dr.Shawnee Mission KS66203 > > > > > > > > > > > > > > > >

[Sprinklerforum] Draft hydrant

2024-09-13 Thread Fpdcdesign
I have been asked to design a 6” draft hydrant taking suction from a brackish river. I have the items in NFPA 24 section 5.8 addressed, but it does not mention materials. The contractor wants to use regular PVC but I need to confirm that something special is not required. Any though

[Sprinklerforum] Re: [External]Re: main drain test

2024-09-11 Thread Fpdcdesign
> > From:Ben Hill > Sent: Wednesday, September 11, 2024 11:45 AM > To: Discussion list on issues relating to automatic fire sprinklers > > Subject: [Sprinklerforum] Re: [External]Re: main drain test > > > > > > > > > >

[Sprinklerforum] Re: [External]Re: main drain test

2024-09-11 Thread Fpdcdesign
Has there even been a generally accepted correlation of a main drain test to a hydrant flow test? (Except static pressure). Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054

[Sprinklerforum] Re: Green points

2024-09-03 Thread Fpdcdesign
Tom, good to hear you are still out there. There are a lot of variables (like how long they do each flow, etc) that will impact how much water is saved or used. I don’t think there is enough consistency to make it viable. You would have to pick a time of flow and meter the

[Sprinklerforum] Re: Interstitial or Attic

2024-08-28 Thread Fpdcdesign
I’ve done a bunch of these. If the flat area meets the criteria for concealed space sprinklers, use them. In the sloped areas, I try to use single direction attic sprinklers if possible. The one thing this detail doesn’t show is where the insulation is located in the sloped r

[Sprinklerforum] Re: Storage Unit Inspections

2024-08-14 Thread Fpdcdesign
So Ron, this sounds like they have to remove sheet rock ceilings and ductwork before the inspector show up. Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Aug 14, 2024 at 2:51 PM, mailto:rongree

[Sprinklerforum] Re: Mattress Storage Classification

2024-08-08 Thread Fpdcdesign
What Steve said. I did a large project with a foam mattress manufacturer a while back. We pretty much dismissed the flammability standards argument right away. it may slow it down a little but it’s still a foamed plastic. Todd Williams Fire Protection Design/Co

[Sprinklerforum] Re: Old pipe Schedule system

2024-07-31 Thread Fpdcdesign
If they did a calculation on the existing system with the 1/2” sprinklers and achieved that density, I do not believe they have to upgrade anything. I think the 0.2 restriction is for new or upgraded systems only. The other consideration is that the placard could be total BS

[Sprinklerforum] Re: Dock System / Stand pipe

2024-07-30 Thread Fpdcdesign
Far am I to challenge Mr Layton on a standpipe question. However, my first reaction was why not. Pumps and underground are shared between buildings, why not between a building and a marina? Connected to a 1000 gpm pump, it would most likely end up automatic wet instead of manual dry.

[Sprinklerforum] Re: Missing Hydraulic Design riser tags

2024-07-30 Thread Fpdcdesign
One of the things that I see, living in an area with 80+ year old systems, is that the newer inspectors are asking for calc signs on pipe schedule systems. Hydraulically calculatingpipe schedule system can be a disaster. They are 2 separate and individual system designs. A system

[Sprinklerforum] Re: NFPA 13R - Multifamily with attic access

2024-07-28 Thread Fpdcdesign
As far as access, attic access could be allowed unless prohibited by Building Code or other restriction (ie zoning approval). However, since it is accessible for living space or storage, it would need to be appropriately protected. Even then, it could be considered 4 stories inst

[Sprinklerforum] Re: Gym Hazard Classification

2024-07-22 Thread Fpdcdesign
Would the same apply to platforms in churches if they are doing any sort of production? Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Jul 22, 2024 at 1:11 PM, (mailto:st...@protectiondesign.com)>

[Sprinklerforum] Re: Gym Hazard Classification

2024-07-20 Thread Fpdcdesign
to partner once we explain what we need and why we > need it. > > > > > > > > > Steve Leyton > > > > (Sent from my smartphone; please excuse typos and voice-to-text corruptions.) > > > > > > &

[Sprinklerforum] Re: Gym Hazard Classification

2024-07-19 Thread Fpdcdesign
“Articulate owner’s certificate”? LMFAO Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Jul 19, 2024 at 7:52 PM, (mailto:st...@protectiondesign.com)> wrote: > > > > > > Is it ju

[Sprinklerforum] Re: [External]Re: Water Tank for Standpipe

2024-07-01 Thread Fpdcdesign
> think it’s the building owner’s responsibility to solve the City’s issue. > > > > > > > > > > > > > > > > > > Cliff Whitfield, SET > > > > > > > > President > > > > > > > >

[Sprinklerforum] Re: Water Tank for Standpipe

2024-07-01 Thread Fpdcdesign
; Todd- > > > > Yes, it’s a manual wet standpipe. Problem is the city supply has dropped a > fair amount and now the standpipe test won’t pass. > > > > > > > > > Thank you, > > > > > > > > Brian Har

[Sprinklerforum] Re: Water Tank for Standpipe

2024-07-01 Thread Fpdcdesign
Isn’t this a 4 story building? Below the high rise threshold, I assume. Can it be a manual wet standpipe? Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Jul 1, 2024 at 9:09 AM, m

[Sprinklerforum] Re: Water Tank for Standpipe

2024-07-01 Thread Fpdcdesign
Isn’t this a 4 story building? Below the high rise threshold, I assume. Can it be a manual wet standpipe? Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 > > On Jul 1, 2024 at 9:09 AM, mailto:pkim...@as

[Sprinklerforum] Re: Reducing dry system area

2024-06-24 Thread Fpdcdesign
t; wrote: > > > > > > Have a rated wall or walls installed between sections and use room design > method? > > > > Ed K > > > > > > > > > > > > > > > > From: Fpdcdesign > Sent: Mo

[Sprinklerforum] Reducing dry system area

2024-06-24 Thread Fpdcdesign
I am working on a building with a unique facad where I am trying to figure out the calcs. Each end of the building has a 24x24 “tower” where the roof slope on 4 sides to a peak. The center of the building over the entry has a 24x17 inverted V sloped roof. Connecting each of these is

[Sprinklerforum] Obstruction below sidewall sprinkler

2024-05-15 Thread Fpdcdesign
I am working on a system with extended coverage sidewall sprinklers, allegedly protecting an LH occupancy. The space is a high ceiling area where the elevation distance between the high and low ceilings is 22”. The low ceiling is protected by pendants. 4” below the center

[Sprinklerforum] Re: Cannabis growing

2024-05-13 Thread Fpdcdesign
Spencer Tomlinson, PE > > > > Owner, Fire Protection Engineer > > > > > > > > > > > > Cell: 620-955-7293 > > > > > > > > > > > From: Fpdcdesign > Sent: Monday, May 13, 2024 9:32 AM > To: Discussion list on

[Sprinklerforum] Re: Cannabis growing

2024-05-13 Thread Fpdcdesign
m (http://www.mepcad.com/) | m: 480.547.9348 > > > > > > > > AutoSPRINK|AutoSPRINK FAB|AutoSPRINK RVT|AlarmCAD > > > > > > > > Book appointment time in my calendar > > > > https://calendly.com/t

[Sprinklerforum] Re: Cannabis growing

2024-05-13 Thread Fpdcdesign
royo Grande Blvd. #105 I Henderson, NV 89074 > > > > www.mepcad.com (http://www.mepcad.com/) | m: 480.547.9348| Whatspp: > +14805479348 > > > > Email: t.m...@mepcad.com > > > > > > > > AutoSPRINK|AutoSPRINK FA

[Sprinklerforum] Cannabis growing

2024-05-13 Thread Fpdcdesign
I know that NFPA 420 is coming but I believe has not been issued yet. I have been asked to look at a new growing facility. NFPA 13 calls out agriculture facilities os OH2, which make sense for this occupancy. My question comes from the tables. The tables are portable so sprinklers are

[Sprinklerforum] Re: Water Supply

2024-05-06 Thread Fpdcdesign
nting out the obvious fact > that I missed about the static pressure. > > > > > Thank you, > Bob Knight, CET III > Fire by Knight, LLC > 208-318-3057 > > On 5/6/2024 3:18 PM, Fpdcdesign wrote: > > > > > There is n

[Sprinklerforum] Re: Water Supply

2024-05-06 Thread Fpdcdesign
There is no friction loss at 0 gpm. The static at the riser will be your churn pressure plus the elevation gain. In my opinion, you should include the mains as you describe them as part of the calculation. Todd Williams Fire Protection Design/Consulting Stoning

[Sprinklerforum] Re: Plastisol liquid PVC

2024-04-12 Thread Fpdcdesign
Steve, a quick search found a couple of different MSDS. The older ones showed as you said but some newer ones called it a IIIB flammable liquid. I would suggest contact the supplier and get the latest MSDS. Todd Williams Fire Protection Design/Consulting Sto

[Sprinklerforum] Re: Main floor hose valve location.

2024-04-11 Thread Fpdcdesign
Yes, Todd.Back in the Boston District Office, some 40-plus years ago. > > > > Regards, > > > > Dwight Havens > > Pre-planning Engineer > > Round Lake Fire Department > > > > Still volunteering, now in Malta, NY. > &g

[Sprinklerforum] Re: Standpipe Calculations

2024-04-03 Thread Fpdcdesign
13R buildings are not considered to be fully sprinklered. > > On Apr 3, 2024 at 9:45 AM, mailto:shawn.f...@gmail.com)> wrote: > > > > Why would you do 1250 if it’s a fully sprinklered building? > > > > > > > > >

[Sprinklerforum] Re: Main floor hose valve location.

2024-03-29 Thread Fpdcdesign
Dwight, That is pretty much what I have said. I am proposing adding a hose valve in a common area and submit to the AHJ to add this arrangement in their fire planning. From a practical standpoint, the FD would fight a firein the main occupied areas from the hydrant acros

[Sprinklerforum] Re: BFP Forward flow test design

2024-03-28 Thread Fpdcdesign
Design Manager > > > > Fire FoeCorp. > > > > 999 Trumbull Ave. > > > > Girard, OH 44420 > > > > P: 330-759-9834 x112 > > > > F: 330-759-8949 > > > > E: t...@firefoe.com (mailto:t...@fi

[Sprinklerforum] BFP Forward flow test design

2024-03-28 Thread Fpdcdesign
I am working on a re-design of a system where I need to include a provision for doing a forward flow test for the backflow preventer (4”). Due to space issues, I would like to do a by-pass around the check valve to the FDC. Is there a problem with this due to the clappers in the

[Sprinklerforum] Main floor hose valve location.

2024-03-27 Thread Fpdcdesign
I am working on a small 4 story building where we are required to install a standpipe (as well as a full 13 sprinkler system). The first floor consists of a conference area, office space and various mechanical and storage rooms. The conference space and office area have direct access

[Sprinklerforum] Multiple sprinkler spacings

2024-03-21 Thread Fpdcdesign
I am working on a project which is a retail store being renovated for a new tenant. The previous retail tenant had been in the space for at least 20 years. The existing sprinklers below the ceiling (to remain) are spaced at 10 ft in one direction and alternate 10 ft and 14 ft (10-14

[Sprinklerforum] Mixed antifreeze types

2024-03-21 Thread Fpdcdesign
I have a client with a rather large (330 gallon) antifreeze system that is looking to upgrade to an approved solution. There are approximately 100 pendent sprinklers on either straight drops or swing joints. The contractor has proposed pulling a few drops and using a Dropmaster to try

[Sprinklerforum] Re: NWD file

2024-03-19 Thread Fpdcdesign
I think this is another part of the evolution. I can see a time where all you get is access to a Revit-NWD hybrid file through something like Procore. Everything is on the drawing and you have to do your design simultaneously with everyone else with real time clash detection. Nothing

[Sprinklerforum] Re: Sidewalls on curved walls

2024-03-11 Thread Fpdcdesign
leep with > > thirteen EC sprinklers in this area. > > > > > > AJ > > > > > > > > > > > > > > > > > > > > Virus-free.www.avg.com > > (http://www.avg.com/email-signature?utm_medium=

[Sprinklerforum] Re: Sidewalls on curved walls

2024-03-08 Thread Fpdcdesign
. > > On Mar 8, 2024 at 3:41 PM, mailto:rongreen...@gmail.com)> > wrote: > > > > > I'm thinking this may be one of those occasions where that PE after your name > may need to be summoned, Todd. > > > > > On Fri, Ma

[Sprinklerforum] Re: Sidewalls on curved walls

2024-03-08 Thread Fpdcdesign
Light Hazard. Waiting room > > On Mar 8, 2024 at 2:18 PM, mailto:rick26...@gmail.com)> > wrote: > > > > > > What’s the occupancy of the space? > > Rick Matsuda > > > > &

[Sprinklerforum] Sidewalls on curved walls

2024-03-08 Thread Fpdcdesign
I am working on a project that has a 40 ft diameter circular ceiling at an elevation of 10 ft that is surrounded by an 8 ft ceiling. The existing protection to the high areis provided by 18 extended coverage sidewall sprinklers around the perimeter. They are renovating the space and

[Sprinklerforum] Re: Apartment used as an office

2024-03-05 Thread Fpdcdesign
y services as a consultant to help them get out of the > situation.Like you, I passed and am not sure how it resolved. > > > > > > > > Steve L. > > > > > > > > > > From: Fpdcdesign > Sent: Tuesday, March 05

[Sprinklerforum] Apartment used as an office

2024-03-05 Thread Fpdcdesign
I was in an apartment building yesterday and the apartment on the 3rd floor had been rented and was being used as an office. I believe the system design is NFPA 13R (not sure but it looks like it). My guess this is under the radar of the local authorities. Has anyone else run into this

[Sprinklerforum] Re: Polybutylene pipe

2024-03-04 Thread Fpdcdesign
s an option under specially listed > pipe, NFPA 13- section: 6.3.6.1, and NFPA 13R-section: 5.2.2.2. > > > > > > > > Hope this helps! > > > > > > > > Sincerely, > > > > Eric Rieve, SET > > > > Rieve Fire P

[Sprinklerforum] Polybutylene pipe

2024-03-04 Thread Fpdcdesign
Was polybutylene pipe ever listed for NFPA 13 or 13R systems? I looked at a system with PB pipe this morning but have no other information on the system (placard only had the static water pressure). Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-53

[Sprinklerforum] Re: 13R water supply question

2024-02-28 Thread Fpdcdesign
Steve and Ken made very knowledgeable and professional posts, as they always do. However, now it is my turn. If you are required to pull multiple permits for the same installation, this should be written somewhere, along with an explanation of who is to do what. This should

[Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof

2024-02-24 Thread Fpdcdesign
stairway extends to the roof, then a hose valve is required at the top > landing or on the roof. > > > > > > > > > > > > If there is no roof access from the stairway, then no hose valve is required. > > > > > > > > > >

[Sprinklerforum] Re: Modified 13D System per FD

2024-02-21 Thread Fpdcdesign
As I keep trying to beat into people’s brains, Codes are a minimum. If the project is not design-build, then you need to look to see if there is a spec that asks for more. This phenomenon is not restricted to the west coast. > > On Feb 21, 2024 at 9:0

[Sprinklerforum] Re: Small ESFR system

2024-02-08 Thread Fpdcdesign
Why can’t you use a K16.8 CMSA instead of an ESFR? Controls mode design might be a little more friendly than extinguishing mode. > > On Feb 8, 2024 at 12:42 PM, (mailto:k...@parsleyconsulting.com)> wrote: > > > I'm a bit late to this discuss

[Sprinklerforum] Re: Return Plenum

2024-02-05 Thread Fpdcdesign
Steel or CPVC? > > On Feb 5, 2024 at 4:56 PM, mailto:bhar...@bvssystemsinc.com)> > wrote: > > > > > > Is there anywhere in code that says sprinkler pipe is not allowed in a space > above a ceiling being used as a return air plenum? I

[Sprinklerforum] Re: Fire Pump testing procedures

2024-01-29 Thread Fpdcdesign
I would think you would need to do both, at least initially. Individually to find out that each pump is working correctly itself and both to verify that the full demand can be met. For a future testing program, probably something specialized would be needed. Make sure it is

[Sprinklerforum] Re: Hose Valves in Townhome Apartments

2024-01-23 Thread Fpdcdesign
It is worth noting that the EOR (assumed in this case to be the specifying engineer) can request things that are beyond what the Code requires. Codes are a minimum, not an absolute. That being said, you should be able to get the “permit review comments”. Not sure who did th

[Sprinklerforum] Re: Concealed Spaces Not Requiring Sprinkler Protection

2024-01-16 Thread Fpdcdesign
What is the floor structure about the joists? Wood or metal? What is the spacing of the joists? I have been told that the definition of “limited combustible” is purposely vague. I can’t define it but I know what it is when I see it. Top and bottom wood members every 16” would

[Sprinklerforum] Re: Backflow In Stairwell

2024-01-16 Thread Fpdcdesign
Ditto to Greg. A couple of years ago I saw a pump and backflow under a stair. Usually on the ground floor out of the way or any travel path. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (te

[Sprinklerforum] Re: Proprietary Product

2024-01-09 Thread Fpdcdesign
These are the type oof questions I don’t like to answer on the Forum. Too much you don’t know. This is the type of thing the Owner should have an FPE review and have them develop a design spec. Not a design build project. Todd G Williams, PE Fire Protection Design/Consu

[Sprinklerforum] Re: LIGHT-WALL SCH 7 NFPA

2024-01-08 Thread Fpdcdesign
If I recall, I believe Sch 7 pipe became popular for use in Press-Fit systems. And I think that was galvanized, nit black. Outside of that I haven’t seen a situation where it gives you any significant advantage over sch 10. However, if it is listed for fire service, it is would be a

[Sprinklerforum] Re: Dry System Aux. Drain

2024-01-03 Thread Fpdcdesign
Brian, what I have seen is a chart with the location of the low points mounted near the riser. Also bright orange tags on the drain valves themselves to make them a little easier to spot. Best you can do it say that they exist and here is where they are. I’

[Sprinklerforum] Re: Dry System Aux. Drain

2024-01-03 Thread Fpdcdesign
Brian, what I have seen is a chart with the location of the low points mounted near the riser. Also bright orange tags on the drain valves themselves to make them a little easier to spot. Best you can do it say that they exist and here is where they are. I’m not sure what

[Sprinklerforum] Re: Sprinkler is spray both intake ducts.

2023-12-27 Thread Fpdcdesign
duct needs to be protected. > > > > 7. Air monitoring is required. > > > > 8. All filters need to be changed regularly and disposed properly. > > > > 9. Numerous other requirements. > > > > &

[Sprinklerforum] Sprinkler is spray both intake ducts.

2023-12-26 Thread Fpdcdesign
I am working on a project where a company acquired a used paint spray booth that they are adapting to their operation. It is a little unique in that the air intake is through the floor and the exhaust is through the ceiling. The previous dry chemical system has been removed and the

[Sprinklerforum] Re: Painted Heads

2023-12-22 Thread Fpdcdesign
Charlie, typically you only have to replace the sprinkler(s) that have been painted. Any local contractor could take a look at the existing sprinkler and find a current replacement. Some residential sprinklers and sizes have been discontinued but there are some allowances in the reside

[Sprinklerforum] Re: Sprinkler system area determination

2023-12-19 Thread Fpdcdesign
What size are the equipment platforms? You might also need to look at 4.5.2.2 and 4.5.2.3. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:

[Sprinklerforum] Re: Braded Flex Drops

2023-12-18 Thread Fpdcdesign
I have seen all varieties but some of it may be dictated by the EOR. They have their own ideas about flex drops. One engineer specified that they be replaced with hard pipe if moved from the original location. > > On Dec 18, 2023 at 8:51 AM, mailto:jamie.se...@gm

[Sprinklerforum] Re: Definitions

2023-12-11 Thread Fpdcdesign
It sounds to me like the definition of “unused attic” is purposely vague (and note it is in the Appendix and not main Standard). The main definition of Light Hazard is “spaces of low quantity and combustibility of contents”. That is the question you need to answer. Does the presen

[Sprinklerforum] Re: Commodity Classification questions

2023-11-09 Thread Fpdcdesign
I did one of these a while back. There is no good information in the Standards about this (unless there is something new). The problem is this could end up as a deep seated fire and the only real way to extinguish it is to pull all of the stuff out, look for hot spots and hit them w

[Sprinklerforum] Antifreeze volume limitations.

2023-11-08 Thread Fpdcdesign
I am working on an existing gridded system that was converted from wet to anti-freeze several years ago. The system protects a Light Hazard occupancy and and has a volume around 375 gallons. We are in the process of trying to replace the existing glycerine mixture with a listed soluti

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Fpdcdesign
rsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1) > > On 10/9/2023 10:49 AM, Fpdcdesign wrote: > > > > > Is there a check valve on the floor control assem

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Fpdcdesign
Is there a check valve on the floor control assembly? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Oct 9,

[Sprinklerforum] Re: [EXTERNAL] Distance to fire pump suction

2023-10-09 Thread Fpdcdesign
gt; > > > 1041 East Butler Road Greenville, South Carolina29606 > > > > CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS > > > > > > > > > > > > > > > From: Fpdcdesign > Sent: Saturday, October 7

[Sprinklerforum] Re: Distance to fire pump suction

2023-10-07 Thread Fpdcdesign
> > > Fire Protection Sprinkler Design > > > > and Consulting Services > > > > > > > > 117 Old Stage Rd. - Essex Jct., VT. 05452 > > > > CELL: (802) 373-0638 > > > >

[Sprinklerforum] Distance to fire pump suction

2023-10-07 Thread Fpdcdesign
I have a system with a 6” backflow preventer, which reduces to 4” immediately after. There is approximately 48” of 4” pipe to the suction flange on a 4 x 3 pump. All elbows are turning correctly. Is this sufficient? Does the 10x rule apply to the size of the backflow preventer or th

[Sprinklerforum] Re: Maurice Pillette

2023-10-06 Thread Fpdcdesign
> On Fri, Oct 6, 2023 at 1:52 PM Fpdcdesign (mailto:fpdcdes...@gmail.com)> wrote: > > > > > > > > > > > Who was the other? > > > > > > > > Todd G Williams, PE > > Fire Protection Design/Consulting > &g

[Sprinklerforum] Re: Maurice Pillette

2023-10-06 Thread Fpdcdesign
Who was the other? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Oct 6, 2023 at 1:48 PM,

[Sprinklerforum] Re: Maurice Pillette

2023-10-06 Thread Fpdcdesign
There is a name I haven’t heard in a few years. Sorry to hear he passed. > > On Oct 6, 2023 at 1:41 PM, mailto:tduro...@comcast.net)> wrote: > > > > > > To those fortunate enough to know this man, I’m sorry to announce his passing >

[Sprinklerforum] Irregular concealed space sprinkler spacing

2023-10-04 Thread Fpdcdesign
I am working on a project in a wood frame building where they have ceilings at varying heights. In the high ceiling areas (about 50% of the space), there is 5” between the ceiling and the bottom of the joists. These do not require sprinklers per 9.1.2.5. In the low ceiling areas, th

[Sprinklerforum] Re: Spray Foam Insulation

2023-09-29 Thread Fpdcdesign
One of the problem is that insulation installers are not consistent. Some may stop at the joists, others may just let it flow. It is almost impossible to properly install sprinks until after the insulation is in, but then it is difficult to hang the pipe. On one job I was w

[Sprinklerforum] Re: NONEXPANDED GROUP A PLASTICS

2023-09-20 Thread Fpdcdesign
Without any further info, it sounds like exposed. > > On Sep 20, 2023 at 8:03 PM, (mailto:danielbobadil...@gmail.com)> wrote: > > > > > Hello Guys, hoping you're good. > > > > I need to protect electronic voter identification machin

[Sprinklerforum] Metric

2023-09-20 Thread Fpdcdesign
Those of you who use the metric system, do you typically use mm/min or L/min/m**2 to describe density? I realize they are the same but am interested in how it is expressed. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080)

[Sprinklerforum] Re: Last OH 3 edition

2023-09-11 Thread Fpdcdesign
No OH3 in 1991 > > On Sep 11, 2023 at 3:01 PM, mailto:cl...@fire-design.com)> wrote: > > > > > > Steve, > > > > > > > > It was still in there in the 89 edition.I think it changed in 91 but I > can’t lay my hands on mine.

[Sprinklerforum] Re: Roof Drain / Sprinkler Drain

2023-08-23 Thread Fpdcdesign
A lot of good responses. Another consideration might be if you would be required to do a drain test from this connection. That would be under pressure and a higher volume that a straight drain. It might need to be considered in the roof drain design. > > On Aug 2

[Sprinklerforum] Re: Standpipe Hydraulic Information Sign

2023-08-09 Thread Fpdcdesign
Unfortunately the only signs available are the ones for sprinklers from the 1980s. I have done some custom stuff for specific applications. Maybe that should be my retirement business > > On Aug 9, 2023 at 9:12 AM, mailto:da...@bamfordfire.com)> wro

[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread Fpdcdesign
Tim, Craig pretty much nailed it. This is not a sprinkler issue. The HVAC crowd needs to solve this. My concern is why is this a wet system to begin with? Somewhere there is a chiller that is pumping out air a lot colder then 40 degrees to maintain that temperature; probably at roof

[Sprinklerforum] Re: [EXTERNAL] Re: Sprinklers in column enclosures

2023-08-08 Thread Fpdcdesign
sources of ignition present. > > > > scratching my head to understand this one, > > > > > Ken Wagoner, SET > Parsley Consulting > 500 West Mechanic Street > Harrisonville, Missouri 64701-2235 > Phone: (760) 745-6181 &g

[Sprinklerforum] Re: Sprinklers in column enclosures

2023-08-08 Thread Fpdcdesign
Mechanic Street > Harrisonville, Missouri 64701-2235 > Phone: (760) 745-6181 >Visit the website > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZ

[Sprinklerforum] Re: Sprinklers in column enclosures

2023-08-08 Thread Fpdcdesign
; > Ken Wagoner, SET > Parsley Consulting > 500 West Mechanic Street > Harrisonville, Missouri 64701-2235 > Phone: (760) 745-6181 >Visit the website > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE

[Sprinklerforum] Sprinklers in column enclosures

2023-08-07 Thread Fpdcdesign
I am working on a wood framed residential building, with some steel columns, that has a full 13 system (Type V-B construction). The steel columns are 4” diameter and are enclosed in wood framing leaving an interior space of roughly 12” x 10”. The Building Inspector is asking for spr

[Sprinklerforum] Re: Attic Sprinkler spacing

2023-07-20 Thread Fpdcdesign
I looked in my 1991 handbook and there was no restriction on distance between sprinklers for roof pitch > > On Jul 20, 2023 at 3:37 PM, mailto:bobby.we...@koorsen.com)> > wrote: > > > > > > I have ran across an attic dry system that h

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Fpdcdesign
> > > > > > Hope this helps, > > > > Eric Rieve > > > > Rieve Fire Protection > > > > > > > > > > From: Fpdcdesign > Sent: Friday, July 14, 2023 12:37 PM > To: Sprinklerforum > Subje

[Sprinklerforum] Elbows in pump suction

2023-07-14 Thread Fpdcdesign
I am working on a pump house that has a 1500 gpm pump with an 8” suction line (no reducer). There is an elbow in the suction line parallel to the pump shaft with a piece of pipe that is 38” from the suction flange and there is a problem with the test. We have to add

[Sprinklerforum] Re: Forward Flow testing valve arrangements

2023-07-12 Thread Fpdcdesign
Pretty good supply if you can flow 1800 gpm at a good pressure without a pump. > > On Jul 12, 2023 at 4:37 PM, mailto:craig.pr...@jacobs.com)> > wrote: > > > > > > Providing an array of 2.5” hose valves as a test header for testing

[Sprinklerforum] Re: Old Pipe Scheduled Systems

2023-07-12 Thread Fpdcdesign
I see these all the time. 1. There is a section in 13 about water supplies for pipe schedule systems. That won’t give you something for a placard but it would tell you if there is sufficient water for it. 2. Placards are only required for hydraulically calculated

[Sprinklerforum] Powder coating oven

2023-07-11 Thread Fpdcdesign
This is my first time doing a powder coating operation. This is a continuous batch system where the product is suspended from a chain system that transports it through the process. As part of the process, it is run through a 400 degree F (max) curing oven, which is about 20’ x 30’.

[Sprinklerforum] Re: Spray On Insulation

2023-07-10 Thread Fpdcdesign
Also be concerned about any sprinklers in the space that may have insulation on them. Side story. I designed a project a few years ago where the insulation guy buried a row of attic sprinklers under 2+ feet of expanded foam. He was supposed to install 8” but got a little ov

[Sprinklerforum] Re: Optional sprinkler protection in garage without sprinklers elsewhere

2023-07-05 Thread Fpdcdesign
Ken, you are way too eloquent. My thought was a hydraulic alarm actuation system. I recently did a project at a facility with rack storage of Li batteries. I had to go through all of the data and research to try and figure where to start. Given what I learned, even a proper