Craig pretty much summed up my thoughts. But to add to that, if you are 
dealing with molten materials for 3D printing, which could be in the thousands 
of degrees, how would sprinkler water react with that?   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Oct 24, 2024 at 5:29 PM,  <Craig Prahl (mailto:[email protected])>  
> wrote:
>   
>   
>           
>   
>
> Well then, the option is to dive into something beyond one’s level of 
> experience and expertise and hope your liability insurance is all paid up.
>
>   
>
>   
>
>   
>
> NFPA 13 is not the end all when it come to design.    If you haven’t looked 
> at the building code and then the fire code (local and/or state) and then the 
> applicable NFPA Standard which sometimes isn’t NFPA 13, you’ve not done 
> anyone a real service.
>
>   
>
>   
>
>   
>
> And sometimes it might be better to let the guy down the road have it.   
>
>   
>
>   
>
>   
>
> In our business lives are at stake. Be sure you can whole heartedly defend 
> every note, every decision and every word without hesitation because one day 
> you might have to do so.
>
>   
>
>   
>
>   
>
> Oh and be sure to find out the temp of the extruder head, sometimes they can 
> be real hot and those 155°F sprinklers just aren’t going to cut it.   
>
>   
>
>   
>
>   
>
> And y’all be careful now, ya hear.   
>
>   
>
>   
>
>   
>   
>
>  Craig Prahl    |Jacobs     | Fire Protection SME – EV, AM, DC, Special 
> Hazards
>
>   
>
>  [email protected] (mailto:[email protected])|www.jacobs.com 
> (https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$)
>
>   
>
> 1041 East Butler Road      Greenville, South Carolina    29606     
>
>   
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>   
>
>   
>
>   
>   
>
>   
>
>   
>   
>   
>
> From:   [email protected]  <[email protected]>
>   Sent:  Thursday, October 24, 2024 4:50 PM
>   To:  [email protected]
>   Subject:  [EXTERNAL] [Sprinklerforum] Re: Metal manufacturing
>
>   
>   
>   
>
>   
>
>   
>   
>
> I love all you guys. I really do. (Even you Todd)
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> But, Hire an Engineer, or Should be provided by an Engineer, just does not 
> work out here in the trenches.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> The answer is there in 13. Even "extruding" by a 3-D printer is extruding. I 
> had to do Metal Working for folks cutting 4x8 sheets of aluminum.
>
>   
>   
>   
>
> There is not a distinction. Some AHJ's see that and live by it.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
>   IS it the intent? Probably not.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> But it IS what the book says.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> Which is the only thing we have in most cases.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> I really wish we could kick it back. But more times than not, they just go to 
> the next person in line.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> Just saying. Those are not really answers to the questions.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> Rant over..
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> R/
>
>   
>   
>   
>
> Matt
>
>   
>   
>   
>   
>
>   
>
>   
>   
>   
>
>   
>
>   
>   
>
>  Matthew J. Willis, CWBSP, C.E.T.
>
>   
>
>  Ferguson Fire Design, LLC
>
>   
>
>  D:   (602) 337-0721 ((602)%20337-0721)    C:   (307) 236-8249 
> ((307)%20236-8249)
>
>   
>
>   [email protected] (mailto:[email protected])
>
>   
>
>   
>
>   
>   
>   
>   
>   
>
>  From:    Craig Hanson  <[email protected] (mailto:[email protected])>
>   Sent:  Thursday, October 24, 2024 12:48 PM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] Re: Metal manufacturing
>
>   
>   
>
>   
>
>   
>   
>   
>   
>   
>   
>
> Caution:    This email originated from outside of the organization.    DO NOT 
> click links or open attachments unless you recognize and trust the sender.   
>
>   
>     
>   
>   
>
> They need to provide for you the hazard analysis   that should have been done 
> by an FPE and in accordance with IFC 104.7.2 and NFPA 13: 4.2(2022). The AHJ 
> should have requested that information also. These are tricky operations as 
> dissimilar metals create a deflagration issue. the design may also be outside 
> the scope of the NFPA 13 due to the process   involved. Their insurance 
> company should also be requiring   a hazard analysis.   
>
>
>   
>   
>   
>   
>
>   
>
>   
>   
>
>   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>   
>   
>   
>
>   
>   
>   
>   
>
>  Craig D. Hanson, CFPS
>
>   
>   
>   
>   
>   
>
>  Fire Division Manager
>
>   
>   
>   
>   
>   
>
>  West Coast Code Consultants, Inc. (WC³)
>
>   
>   
>   
>   
>   
>
>  Meridian Satellite Office
>
>   
>   
>   
>   
>   
>
>  C:   253.225.9977 |   E:   [email protected] (mailto:[email protected])  |   
> www.WC-3.com 
> (https://urldefense.com/v3/__https:/www.wc-3.com/__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S35sekTmA$)
>
>   
>   
>   
>   
>   
>
>  Teaming With Your Community to Make a Difference
>
>   
>   
>   
>   
>   
>   
>   
>   
>   
>
>   
>
>   
>   
>
>   
>
>   
>   
>   
>
> On Thu, Oct 24, 2024 at 12:21 PM Fpdcdesign  <[email protected] 
> (mailto:[email protected])>  wrote:
>
>   
>   
> >   
> >   
> >   
> >
> > +1 for Tim Stone. Too often the contractor or their estimator are asked to 
> > figure out design criteria. That should fall upon the FPE.   
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >
> > Todd Williams   
> >
> >   
> >   
> >
> > Fire Protection Design/Consulting
> >
> >   
> >   
> >   
> >
> > Stonington, CT
> >
> >   
> >   
> >   
> >
> > 860-608-4559
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >
> >   
> >   
> >
> >
> >   
> > >   
> > >   
> > >
> > > On Oct 24, 2024 at 1:04 PM,  <Tstone52 (mailto:[email protected])>  
> > > wrote:
> > >
> > >   
> > >   
> > >   
> > >   
> > >
> > > It should be recommended that an “Architect” or “Engineer of Record” 
> > > should provide you with a Code Review.
> > >
> > >   
> > >
> > > Or hire a “Fire Protection Engineer” to assist you.
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >
> > > Regards,
> > >
> > >   
> > >
> > >  G. Tim Stone
> > >
> > >   
> > >
> > >     
> > >
> > >   
> > >
> > >  G. Tim Stone Consulting, LLC
> > >
> > >   
> > >
> > >  NICET Level III Engineering Technician
> > >
> > >   
> > >
> > >  Fire Protection Sprinkler Design
> > >
> > >   
> > >
> > >  and Consulting Services
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > >       117 Old Stage Rd. - Essex Jct., VT. 05452
> > >
> > >   
> > >
> > >                                  CELL: (802) 373-0638     
> > >
> > >   
> > >
> > >                             [email protected] 
> > > (mailto:[email protected])
> > >
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >
> > > From:  Bobby Welch  <[email protected] 
> > > (mailto:[email protected])>
> > >   Sent:  Thursday, October 24, 2024 12:57 PM
> > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > <[email protected] 
> > > (mailto:[email protected])>
> > >   Subject:  [Sprinklerforum] Metal manufacturing
> > >
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > > I have a building were they are making metal products by multiple 
> > > processes including Metal Casting of steel, Metal Forging, Additive 
> > > Manufacturing and hot rolling. Most of the building is open warehouse 
> > > where they are producing metal products with 3D printers.    NFPA has 
> > > metal workings listed as ordinary hazard but also has Die Casting and 
> > > Metal extruding under Extra hazard group 1. Does anyone know where I 
> > > would start to figure out what hazard is required for this building?
> > >
> > >   
> > >
> > >  Bobby Welch   |    Sprinkler Systems Designer
> > > KOORSEN FIRE  &  SECURITY
> > >   8090 N Dixie Dr, Dayton, OH 45414
> > >  P 937.641.8403    |    Ext. 0318   |    M 937.594.8457
> > >   [email protected] (mailto:[email protected])   
> > > |www.koorsen.com 
> > > (https://urldefense.com/v3/__http:/www.koorsen.com__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S1HA_wFmw$)
> > >      
> > >
> > >   
> > >
> > >  24x7x365 Service: 937.660.7050   |[email protected] 
> > > (mailto:[email protected])         
> > >
> > >   
> > >   
> > >
> > >  _________________________________________________________ SprinklerForum 
> > > mailing list:  
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >  
> > > (https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S32DM4r9A$)
> > >   To unsubscribe send an email to  
> > > [email protected] 
> > > (mailto:[email protected])
> > >
> > >   
> > >   
> >   
> >   
> >   
> >   
> >
> >
> >  _________________________________________________________
> >  SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > (https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S32DM4r9A$)
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])
> >
> >   
>   
>   
>   
>   
>     
>  NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to