Re: Domestic Demands 13R

2020-11-12 Thread BRUCE VERHEI via Sprinklerforum
This is why I hate calling one point on a flow test curve Static. It’s really Background or Normal Usage or something similar. The domestic flow only really matters when have a joint water supply connection for the domestic and spk system. Out at the main someone else is doing fire flow calc’

RE: Domestic Demands 13R

2020-11-12 Thread Jim Davidson via Sprinklerforum
On Behalf Of J H via Sprinklerforum Sent: Thursday, November 12, 2020 3:06 PM To: sprinklerforum@lists.firesprinkler.org Cc: J H Subject: Re: Domestic Demands 13R If the AHJ digs in there is always the route of using automatic domestic shutoff valves.. <https://www.avast.com/sig-em

Re: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
** From: Sprinklerforum on behalf of Matt Grise via Sprinklerforum Sent: Thursday, November 12, 2020 1:16:17 PM To: sprinklerforum@lists.firesprinkler.org Cc: Matt Grise Subject: RE: Domestic Demands 13R What if you just brought in a separate fire line? Then you

RE: Domestic Demands 13R

2020-11-12 Thread Matt Grise via Sprinklerforum
Behalf Of Ed Kramer via Sprinklerforum Sent: Thursday, November 12, 2020 2:14 PM To: sprinklerforum@lists.firesprinkler.org Cc: e...@bamfordfire.com Subject: RE: Domestic Demands 13R Section 9.6 (2016) says "Domestic demand FOR THE BUILDING BEING CALCULATED shall be included . . ."

RE: Domestic Demands 13R

2020-11-12 Thread Ed Kramer via Sprinklerforum
..@pyebarkerfire.com; sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com Subject: RE: Domestic Demands 13R Correct. However, they may be expected to have domestic demands. That is the plan reviewer rationale in one particular case. Travis Mack, CFPS, CWBSP, RME-G, SET Engineerin

Re: Domestic Demands 13R

2020-11-12 Thread J H via Sprinklerforum
If the AHJ digs in there is always the route of using automatic domestic shutoff valves.. Virus-free. www.avast.com

Re: Domestic Demands 13R

2020-11-12 Thread John Denhardt via Sprinklerforum
er.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003 > or > http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003** > > From: Sprinklerforum On > Behalf Of

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
half Of Bob Knight via Sprinklerforum Sent: Thursday, November 12, 2020 11:27 AM To: sprinklerforum@lists.firesprinkler.org Cc: Bob Knight Subject: RE: Domestic Demands 13R "However, they may be expected to have domestic demands. That is the plan reviewer rationale in one particular case." Do

RE: Domestic Demands 13R

2020-11-12 Thread Bob Knight via Sprinklerforum
- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack via Sprinklerforum Sent: Thursday, November 12, 2020 9:53 AM To: philli...@pyebarkerfire.com; sprinklerforum@lists.firesprinkler.org Cc: travis.m...@mfpdesign.com Subject: RE: Domestic Demands 13R Correct

RE: Domestic Demands 13R

2020-11-12 Thread Hinson, Ryan via Sprinklerforum
f Ron Greenman via Sprinklerforum Sent: Thursday, November 12, 2020 11:19 AM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: Re: Domestic Demands 13R My understanding of this is that the complex would have had a total fire flow and domestic flow calculated into the main

Re: Domestic Demands 13R

2020-11-12 Thread Skyler Bilbo via Sprinklerforum
to your favorite ferguson.com features. > http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003 > or > http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
rforum On Behalf Of Ron Greenman via Sprinklerforum Sent: Thursday, November 12, 2020 10:19 AM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: Re: Domestic Demands 13R My understanding of this is that the complex would have had a total fire flow and domestic flow calcula

RE: Domestic Demands 13R

2020-11-12 Thread Matt Grise via Sprinklerforum
ber 12, 2020 11:19 AM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: Re: Domestic Demands 13R My understanding of this is that the complex would have had a total fire flow and domestic flow calculated into the main loop by the Civil Engineer (his job) and the complex loop is tied into the

Re: Domestic Demands 13R

2020-11-12 Thread Ron Greenman via Sprinklerforum
ures. > http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003 > or > http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003** > > From: Hinson, Ryan > Sen

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
517003** From: Hinson, Ryan Sent: Thursday, November 12, 2020 9:59 AM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack Subject: RE: Domestic Demands 13R Is this entire complex brand new or existing? Your answer will determine mine: 1. Taking a water flow test on an existing looped

RE: Domestic Demands 13R

2020-11-12 Thread Hinson, Ryan via Sprinklerforum
Is this entire complex brand new or existing? Your answer will determine mine: 1. Taking a water flow test on an existing looped water main supplying both FW and domestic demands already accounts for the domestic demands of the other buildings, no? On the single main feeding all the way in

RE: Domestic Demands 13R

2020-11-12 Thread Sean.VanGaal via Sprinklerforum
rsday, November 12, 2020 9:51 AM To: sprinklerforum@lists.firesprinkler.org; travis.m...@mfpdesign.com Cc: Mark Phillips Subject: [EXTERNAL] Re: Domestic Demands 13R From a practical perspective all of the apartment building would not be expected to be on fire at once. That was how a plan reviewer

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
inklerforum@lists.firesprinkler.org; Travis Mack Subject: Re: Domestic Demands 13R From a practical perspective all of the apartment building would not be expected to be on fire at once. That was how a plan reviewer once explained it to me. Sent from my mobile device Please excuse spelling, gra

Re: Domestic Demands 13R

2020-11-12 Thread Mark Phillips via Sprinklerforum
Phillips via Sprinklerforum Sent: Thursday, November 12, 2020 11:46:23 AM To: travis.m...@mfpdesign.com ; sprinklerforum@lists.firesprinkler.org Cc: Mark Phillips Subject: Re: Domestic Demands 13R [EXTERNAL] Sorry if I was not clear only the demand of the building or buildings that share the 4

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
ay, November 12, 2020 9:45 AM To: sprinklerforum@lists.firesprinkler.org Cc: Sean.VanGaal Subject: RE: Domestic Demands 13R I understand you said you are designed per 13R, but since you have a large lead-in of 4" have you tried to use "the more stringent 13 standard" that essent

Re: Domestic Demands 13R

2020-11-12 Thread Mark Phillips via Sprinklerforum
; sprinklerforum@lists.firesprinkler.org Subject: RE: Domestic Demands 13R [EXTERNAL] So in this case, you would be adding a total demand of 2500 gpm (20 buildings at 125 gpm each) to your sprinkler calc? And yes, it would be included at the point of each 4” connection to the 8” main. Seems

RE: Domestic Demands 13R

2020-11-12 Thread Sean.VanGaal via Sprinklerforum
I understand you said you are designed per 13R, but since you have a large lead-in of 4" have you tried to use "the more stringent 13 standard" that essentially says UG mains less than 4" that are for fire/domestic you have to calculate both unless you have a way to automatically isolate the non

RE: Domestic Demands 13R

2020-11-12 Thread Travis Mack via Sprinklerforum
amp;p=2591775&t=517003  or  http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003** From: Mark Phillips Sent: Thursday, November 12, 2020 9:41 AM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack Subject: Re: Domest

Re: Domestic Demands 13R

2020-11-12 Thread Mark Phillips via Sprinklerforum
Assuming the 8 inch supply loops the complex Add the domestic demand at the 4” point on the loop for each building Sent from my mobile device Please excuse spelling, grammar, and auto correction. Mark Phillips Branch Manager Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Ala

RE: Domestic Demands 13R

2020-11-12 Thread Matthew J Willis via Sprinklerforum
If I remember correctly, I treated each calc as its own. In other words the 125 for each building. I do not recall adding all domestic flows to the U/G serving both. Seems the same for not having to flow more than 1 calc area when inside the same building. R/ Matt -Original Message- F