That's the way I was taught, but if you look at A.8.6.3.2.4 (b,c,d) it looks
like you can only be 6'-0" off the wall if your 9'-0" in the same direction.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Tuesday, March 13, 2007 4:53 PM
To: [email protected]
Subject: RE: Small Room Rule

You can be 9' off any ONE wall and 7'-6 max. off any other 3 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Tuesday, March 13, 2007 4:38 PM
To: [email protected]
Subject: RE: Small Room Rule

Ed,
Thanks, obviously there can be any combination of sizes that equal up to 800
sq.ft. so those dim's can vary accordingly. One other question, why when
there's only one head can you be up to 9' off one wall and still be 7'6 off
the other (16'6" direction) but when there's 2 or more heads the max you can
be is 9'-0" & 6'-0"?


              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tambini, Ed
Sent: Tuesday, March 13, 2007 4:17 PM
To: [email protected]
Subject: RE: Small Room Rule

30' x 26'-8 = 800 sq ft max size for small room It's what's left over from
the 2 7'-6 dims

Ed
Aero
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Tuesday, March 13, 2007 12:42 PM
To: [email protected]
Subject: Small Room Rule

Figure A.8.6.3.2.4.(d) shows an example of the small room rule with (4)
heads, where exactly does the 11'-8" between rows come from?

 

           Regards,

              Brian Harris
First Defense Fire Protection
        Design Engineer

    <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax



 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to