One thing that hasn't been mentioned, centrifugal fire pumps have to operate with positive suction head. So if you are going to use the pool as a water source the suction flange on the pump has to be at or below the intake level in the pool. With a typical in ground pool that means at least 8' below the water level of the pool. So your looking at a basement or pump pit arrangement which is another cost to consider.


Richard L. Mote
Designer
Rowe Sprinkler Systems, Inc






----- Original Message ----- From: "Rod DiBona" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, July 11, 2007 10:31 AM
Subject: RE: pool as water source


Thanks for the comment Ken it is a good point that I had not thought of.
Rod

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
Sent: Wednesday, July 11, 2007 7:36 AM
To: [email protected]
Subject: RE: pool as water source

Sorry Rod I thought I read hotel somewhere. In any case the draining of
the pool for maintenance would constitute no sprinkler protection.

Best Regards,
Ken Holsopple
Design Manager
Rowe Sprinkler Systems, Inc.
570-837-7647


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to