One thing that hasn't been mentioned, centrifugal fire pumps have to operate
with positive suction head. So if you are going to use the pool as a water
source the suction flange on the pump has to be at or below the intake level
in the pool. With a typical in ground pool that means at least 8' below the
water level of the pool. So your looking at a basement or pump pit
arrangement which is another cost to consider.
Richard L. Mote
Designer
Rowe Sprinkler Systems, Inc
----- Original Message -----
From: "Rod DiBona" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, July 11, 2007 10:31 AM
Subject: RE: pool as water source
Thanks for the comment Ken it is a good point that I had not thought of.
Rod
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
Sent: Wednesday, July 11, 2007 7:36 AM
To: [email protected]
Subject: RE: pool as water source
Sorry Rod I thought I read hotel somewhere. In any case the draining of
the pool for maintenance would constitute no sprinkler protection.
Best Regards,
Ken Holsopple
Design Manager
Rowe Sprinkler Systems, Inc.
570-837-7647
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)