Your alarm devices (water flow, tamper, water pressure, alarm bells) should be 24vdc or whatever is required to match the fire alarm system. Most are 24vdc, (power limited fire alarm (PLFA) circuits) and the power to each device comes through the fire alarm panel. You can find some 120vAC alarm bells and tamper & flow switches but I've only come across them where the building wasn't equipped with a fire alarm system. If that's what you've got then they should be on a separate circuit of their own.
The alarm panel connection to the building power grid is really not the sprinkler contractors concern. That's the responsibility of the Electrical contractor so I wouldn't worry about it. There is considerable verbiage in NFPA 70, article 760 as well as other places (national electrical code) concerning rules for wiring, conductors and on and on and on for fire alarm systems. That is primarily where they get their direction from. The fire alarm system should be on a dedicated circuit as stated in NFPA 72, 4.4.1.4.1 as you found. You wouldn't want someone pulling a breaker to shut off a toaster and kill the fire alarm system too, (although they do have battery backup but power interruption would render a trouble or supervisory alarm). Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregory Lindholm Sent: Wednesday, July 18, 2007 9:31 AM To: SprinklerFORUM Subject: Alarm Circuit We have always told the electricians on projects that the wiring for the sprinkler alarms had to be on a dedicated circuit on the panel. Is this right, and if so, where is it stated? I looked in the 2002 edition of NFPA #72, and the closest thing that I found is 4.4.1.4.1, but not sure if that is correct. Greg Lindholm Metro Fire Protection, Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)