Where's Peter Cottontail?  I believe some have ventured down a rabbit
trail......................

This was NOT a question about the origination and execution of the water
flow signal.  It was about a dedicated power circuit for the alarm
panel.  That question was asked and answered.

We can discuss the methods of alarm design but I'm not sure the
Sprinkler forum is the best place.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Sunday, July 22, 2007 11:03 AM
To: [email protected]
Subject: Re: Alarm Circuit

Ray,

I also felt Craig's answer missed the mark a bit. You're comments
intrigued me because they made perfect sense but we are dealing with
NFPA here. Regarding this matter 13 does direct you to 72 when an alarm
system is present. I don't have a 72 here so my question then is does 72
support your arguements? (Question mark intentional:-})

On 7/22/07, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:> Keep in mind
that regardless of the presence or absence of an building fire alarm
system, if the system requires an exterior water flow signal that the
signal needs to be just that.? Many fire alarm designers want to connect
a 24VDC signal (bell, horn/strobe, etc) on the exterior of the building
tied to the FACP and call it a waterflow signal.? This can present
numerous problems.? First, if it is tied to the general alarm contacts,
it will sound regardless of the initiating device, in other words, it
will sound from a smoke detector, manual pull station, kitchen
suppression system, or whatever initiating devices are connected to the
fire alarm system.?This defeats the entire purpose of an exterior water
flow signal (obviously to alert responding fire companies that water is
actually flowing on their arrival.)? If the signaling device can be
programmed to only sound when the sprinkler initiating device (pressure
switch/flow switch) is actuated, this activation is normally latc
>  hing (stays activated until manually reset from the panel.)? Again,
this defeats the purpose of the exterior waterflow signal in the event
it is activated by a temporary situation, such as a water surge.? (Once
the pressure returns to normal, or the water flow from the surge clears,
the exterior signal would still be sounding when fire companies arrive,
giving a false indication that there is a water flow.)? For those
non-fire department operations types out there, the normal SOP for fire
companies arriving at sprinklered properties is that if the exterior
waterflow signal is sounding it assumed that water is actually flowing
and?hose is layed and connected to the FDC to support the operating
system.? If the signal is not sounding, companies investigate first.? If
water is then found to be flowing, there is a time delay in supporting
the system.
>
> The need for a dedicated and properly identified circuit for the
120VAC exterior waterflow signal then becomes vital.? As Craig said,
your wouldn't want someone shutting down a breaker for a toaster circuit
and killing the exterior signal, especially since there is no battery
backup.? While it is true that the electrical issue is not directly the
sprinkler contractors concern, if NFPA 13 requires an exterior waterflow
signal, and the electrician does not connect it properly, most AHJs will
not approve the final, and the customer will not have an approved
sprinkler system.? I think it is in our best interest to follow through
and make sure the system meets the code and passes the acceptance test.?
It is not our function to fix the problem, only to identify the problem
to the customer so he can address the electrical contractor
properly.?(Besides, who does the customer yell at anyway?if he can't get
his CO?? LOL)??
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> To: [email protected]
> Sent: Wed, 18 Jul 2007 10:02 am
> Subject: RE: Alarm Circuit
>
>
>
> Your alarm devices (water flow, tamper, water pressure, alarm bells) 
> should be 24vdc or whatever is required to match the fire alarm
system.
> Most are 24vdc, (power limited fire alarm (PLFA) circuits) and the
power
> to each device comes through the fire alarm panel.   You can find some
> 120vAC alarm bells and tamper & flow switches but I've only come 
> across them where the building wasn't equipped with a fire alarm 
> system.  If that's what you've got then they should be on a separate 
> circuit of their own.
>
> The alarm panel connection to the building power grid is really not 
> the sprinkler contractors concern.  That's the responsibility of the 
> Electrical contractor so I wouldn't worry about it.
>
> There is considerable verbiage in NFPA 70, article 760 as well as 
> other places (national electrical code) concerning rules for wiring, 
> conductors and on and on and on for fire alarm systems.  That is 
> primarily where they get their direction from.
>
> The fire alarm system should be on a dedicated circuit as stated in
NFPA
> 72, 4.4.1.4.1 as you found.   You wouldn't want someone pulling a
> breaker to shut off a toaster and kill the fire alarm system too, 
> (although they do have battery backup but power interruption would 
> render a trouble or supervisory alarm).
>
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Gregory

> Lindholm
> Sent: Wednesday, July 18, 2007 9:31 AM
> To: SprinklerFORUM
> Subject: Alarm Circuit
>
> We have always told the electricians on projects that the wiring for 
> the sprinkler alarms had to be on a dedicated circuit on the panel.
>
> Is this right, and if so, where is it stated?
>
> I looked in the 2002 edition of NFPA #72, and the closest thing that I

> found is 4.4.1.4.1, but not sure if that is correct.
>
> Greg Lindholm
> Metro Fire Protection, Inc.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
> ______________________________________________________________________
> __ AOL now offers free email to everyone.  Find out more about what's 
> free from AOL at AOL.com.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)