Allan,

That pretty much answers my question. Out this way (former UBC land)
the standard method was to treat the waterflow as just another
annuciating device on the fitre alarm system if said system was
required. Otherwise a 120VAC bell or motor gong was supplied. Whether
a dedicated 120VAC on the former was used was a crap shoot. I'd say
from your answer, and I'll believe you without quoting chapter and
verse, the waterflow alarm ELECTRIC BELL or MECHANICAL GONG, or for
that matter steam driven air raid siren, needs to operate essentially
as a water motor gong would, making noise during actual flow and
shutting down if said flow should cease. That would then be an IBC
call, 13 would then simply agree and also state that if an alarm
system were present then water flow INITIATION would need to be
transmitted to FAP, and that the methods for sending that signal would
need to conform to 72, but how that signal is processed, i.e., send
signal to an acceptable monitoring station as determined by the type
of premise and/or notify occupants, would be per 72 also but, in the
case of when the waterflow signaling device actually sounds, would be
determined by IBC. I hope that wasn't too convoluted. I was trying to
get this straight so kind of thinking out loud. Thanks for the
insight.

On 7/22/07, Allan Seidel <[EMAIL PROTECTED]> wrote:
I do not know the answer to the original question asking for the
chapter and verse about whether or not a dedicated 110 circuit is
required. The circuit requirement ought be the same as per NFPA 72
for the power circuit to a fire alarm panel.

The way I understand this from our helpful fire alarm contractor,
unlike older BOCA, IBC requires the outside waterflow signal with no
exceptions and it states so with language that this is not part of
the fire alarm system. The explicit inclusion in IBC would supersede
NFPA 13, though I do not think 13 points to NFPA 72 for this item.
Making this function part of the fire alarm system is considerably
more expensive than the locally accepted method of providing a
dedicated 110 v circuit, that has a locking breaker, through the
second set of contacts on the flow switch to a 110 v exterior device.
The expense of doing this through the fire alarm system requires
amongst other items: a special output module, a supervised power
circuit, some fancy programming to make the alarm sound only on water
flow instead of general alarm, and possibly a fire alarm panel that
is a grade higher than the lowest end panel.

Allan Seidel
St. Louis, MO

On Jul 22, 2007, at 10:02 AM, Ron Greenman wrote:

> Ray,
>
> I also felt Craig's answer missed the mark a bit. You're comments
> intrigued me because they made perfect sense but we are dealing with
> NFPA here. Regarding this matter 13 does direct you to 72 when an
> alarm system is present. I don't have a 72 here so my question then is
> does 72 support your arguements? (Question mark intentional:-})
>
> On 7/22/07, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:> Keep in mind
> that regardless of the presence or absence of an building fire alarm
> system, if the system requires an exterior water flow signal that the
> signal needs to be just that.? Many fire alarm designers want to
> connect a 24VDC signal (bell, horn/strobe, etc) on the exterior of the
> building tied to the FACP and call it a waterflow signal.? This can
> present numerous problems.? First, if it is tied to the general alarm
> contacts, it will sound regardless of the initiating device, in other
> words, it will sound from a smoke detector, manual pull station,
> kitchen suppression system, or whatever initiating devices are
> connected to the fire alarm system.?This defeats the entire purpose of
> an exterior water flow signal (obviously to alert responding fire
> companies that water is actually flowing on their arrival.)? If the
> signaling device can be programmed to only sound when the sprinkler
> initiating device (pressure switch/flow switch) is actuated, this
> activation is normally latc
>>  hing (stays activated until manually reset from the panel.)?
>> Again, this defeats the purpose of the exterior waterflow signal
>> in the event it is activated by a temporary situation, such as a
>> water surge.? (Once the pressure returns to normal, or the water
>> flow from the surge clears, the exterior signal would still be
>> sounding when fire companies arrive, giving a false indication
>> that there is a water flow.)? For those non-fire department
>> operations types out there, the normal SOP for fire companies
>> arriving at sprinklered properties is that if the exterior
>> waterflow signal is sounding it assumed that water is actually
>> flowing and?hose is layed and connected to the FDC to support the
>> operating system.? If the signal is not sounding, companies
>> investigate first.? If water is then found to be flowing, there is
>> a time delay in supporting the system.
>>
>> The need for a dedicated and properly identified circuit for the
>> 120VAC exterior waterflow signal then becomes vital.? As Craig
>> said, your wouldn't want someone shutting down a breaker for a
>> toaster circuit and killing the exterior signal, especially since
>> there is no battery backup.? While it is true that the electrical
>> issue is not directly the sprinkler contractors concern, if NFPA
>> 13 requires an exterior waterflow signal, and the electrician does
>> not connect it properly, most AHJs will not approve the final, and
>> the customer will not have an approved sprinkler system.? I think
>> it is in our best interest to follow through and make sure the
>> system meets the code and passes the acceptance test.? It is not
>> our function to fix the problem, only to identify the problem to
>> the customer so he can address the electrical contractor properly.?
>> (Besides, who does the customer yell at anyway?if he can't get his
>> CO?? LOL)??
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> To: [email protected]
>> Sent: Wed, 18 Jul 2007 10:02 am
>> Subject: RE: Alarm Circuit
>>
>>
>>
>> Your alarm devices (water flow, tamper, water pressure, alarm bells)
>> should be 24vdc or whatever is required to match the fire alarm
>> system.
>> Most are 24vdc, (power limited fire alarm (PLFA) circuits) and the
>> power
>> to each device comes through the fire alarm panel.   You can find
>> some
>> 120vAC alarm bells and tamper & flow switches but I've only come
>> across
>> them where the building wasn't equipped with a fire alarm system.  If
>> that's what you've got then they should be on a separate circuit of
>> their own.
>>
>> The alarm panel connection to the building power grid is really
>> not the
>> sprinkler contractors concern.  That's the responsibility of the
>> Electrical contractor so I wouldn't worry about it.
>>
>> There is considerable verbiage in NFPA 70, article 760 as well as
>> other
>> places (national electrical code) concerning rules for wiring,
>> conductors and on and on and on for fire alarm systems.  That is
>> primarily where they get their direction from.
>>
>> The fire alarm system should be on a dedicated circuit as stated
>> in NFPA
>> 72, 4.4.1.4.1 as you found.   You wouldn't want someone pulling a
>> breaker to shut off a toaster and kill the fire alarm system too,
>> (although they do have battery backup but power interruption would
>> render a trouble or supervisory alarm).
>>
>>
>>
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Group
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [EMAIL PROTECTED]
>> http://www.lg.com
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of
>> Gregory
>> Lindholm
>> Sent: Wednesday, July 18, 2007 9:31 AM
>> To: SprinklerFORUM
>> Subject: Alarm Circuit
>>
>> We have always told the electricians on projects that the wiring
>> for the
>> sprinkler alarms had to be on a dedicated circuit on the panel.
>>
>> Is this right, and if so, where is it stated?
>>
>> I looked in the 2002 edition of NFPA #72, and the closest thing
>> that I
>> found is 4.4.1.4.1, but not sure if that is correct.
>>
>> Greg Lindholm
>> Metro Fire Protection, Inc.
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> _____________________________________________________________________
>> ___
>> AOL now offers free email to everyone.  Find out more about what's
>> free from AOL at AOL.com.
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to