Sorry about all the question marks in the last post.? Not sure where they came from.? They weren't in the original.
Ray -----Original Message----- From: [EMAIL PROTECTED] To: [email protected] Sent: Sun, 22 Jul 2007 6:15 am Subject: Re: Alarm Circuit Keep in mind that regardless of the presence or absence of an building fire alarm system, if the system requires an exterior water flow signal that the signal needs to be just that.? Many fire alarm designers want to connect a 24VDC signal (bell, horn/strobe, etc) on the exterior of the building tied to the FACP and call it a waterflow signal.? This can present numerous problems.? First, if it is tied to the general alarm contacts, it will sound regardless of the initiating device, in other words, it will sound from a smoke detector, manual pull station, kitchen suppression system, or whatever initiating devices are connected to the fire alarm system.?This defeats the entire purpose of an exterior water flow signal (obviously to alert responding fire companies that water is actually flowing on their arrival.)? If the signaling device can be programmed to only sound when the sprinkler initiating device (pressure switch/flow switch) is actuated, this activation is normally latc hing (stays activated until manually reset from the panel.)? Again, this defeats the purpose of the exterior waterflow signal in the event it is activated by a temporary situation, such as a water surge.? (Once the pressure returns to normal, or the water flow from the surge clears, the exterior signal would still be sounding when fire companies arrive, giving a false indication that there is a water flow.)? For those non-fire department operations types out there, the normal SOP for fire companies arriving at sprinklered properties is that if the exterior waterflow signal is sounding it assumed that water is actually flowing and?hose is layed and connected to the FDC to support the operating system.? If the signal is not sounding, companies investigate first.? If water is then found to be flowing, there is a time delay in supporting the system. The need for a dedicated and properly identified circuit for the 120VAC exterior waterflow signal then becomes vital.? As Craig said, your wouldn't want someone shutting down a breaker for a toaster circuit and killing the exterior signal, especially since there is no battery backup.? While it is true that the electrical issue is not directly the sprinkler contractors concern, if NFPA 13 requires an exterior waterflow signal, and the electrician does not connect it properly, most AHJs will not approve the final, and the customer will not have an approved sprinkler system.? I think it is in our best interest to follow through and make sure the system meets the code and passes the acceptance test.? It is not our function to fix the problem, only to identify the problem to the customer so he can address the electrical contractor properly.?(Besides, who does the customer yell at anyway?if he can't get his CO?? LOL)?? -----Original Message----- From: [EMAIL PROTECTED] To: [email protected] Sent: Wed, 18 Jul 2007 10:02 am Subject: RE: Alarm Circuit Your alarm devices (water flow, tamper, water pressure, alarm bells) should be 24vdc or whatever is required to match the fire alarm system. Most are 24vdc, (power limited fire alarm (PLFA) circuits) and the power to each device comes through the fire alarm panel. You can find some 120vAC alarm bells and tamper & flow switches but I've only come across them where the building wasn't equipped with a fire alarm system. If that's what you've got then they should be on a separate circuit of their own. The alarm panel connection to the building power grid is really not the sprinkler contractors concern. That's the responsibility of the Electrical contractor so I wouldn't worry about it. There is considerable verbiage in NFPA 70, article 760 as well as other places (national electrical code) concerning rules for wiring, conductors and on and on and on for fire alarm systems. That is primarily where they get their direction from. The fire alarm system should be on a dedicated circuit as stated in NFPA 72, 4.4.1.4.1 as you found. You wouldn't want someone pulling a breaker to shut off a toaster and kill the fire alarm system too, (although they do have battery backup but power interruption would render a trouble or supervisory alarm). Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregory Lindholm Sent: Wednesday, July 18, 2007 9:31 AM To: SprinklerFORUM Subject: Alarm Circuit We have always told the electricians on projects that the wiring for the sprinkler alarms had to be on a dedicated circuit on the panel. Is this right, and if so, where is it stated? I looked in the 2002 edition of NFPA #72, and the closest thing that I found is 4.4.1.4.1, but not sure if that is correct. Greg Lindholm Metro Fire Protection, Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ________________________________________________________________________ AOL now offers free email to everyone. Find out more about what's free from AOL at AOL.com. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ________________________________________________________________________ AOL now offers free email to everyone. Find out more about what's free from AOL at AOL.com. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)