Keep in mind that regardless of the presence or absence of an building fire 
alarm system, if the system requires an exterior water flow signal that the 
signal needs to be just that.? Many fire alarm designers want to connect a 
24VDC signal (bell, horn/strobe, etc) on the exterior of the building tied to 
the FACP and call it a waterflow signal.? This can present numerous problems.? 
First, if it is tied to the general alarm contacts, it will sound regardless of 
the initiating device, in other words, it will sound from a smoke detector, 
manual pull station, kitchen suppression system, or whatever initiating devices 
are connected to the fire alarm system.?This defeats the entire purpose of an 
exterior water flow signal (obviously to alert responding fire companies that 
water is actually flowing on their arrival.)? If the signaling device can be 
programmed to only sound when the sprinkler initiating device (pressure 
switch/flow switch) is actuated, this activation is normally latc
 hing (stays activated until manually reset from the panel.)? Again, this 
defeats the purpose of the exterior waterflow signal in the event it is 
activated by a temporary situation, such as a water surge.? (Once the pressure 
returns to normal, or the water flow from the surge clears, the exterior signal 
would still be sounding when fire companies arrive, giving a false indication 
that there is a water flow.)? For those non-fire department operations types 
out there, the normal SOP for fire companies arriving at sprinklered properties 
is that if the exterior waterflow signal is sounding it assumed that water is 
actually flowing and?hose is layed and connected to the FDC to support the 
operating system.? If the signal is not sounding, companies investigate first.? 
If water is then found to be flowing, there is a time delay in supporting the 
system.

The need for a dedicated and properly identified circuit for the 120VAC 
exterior waterflow signal then becomes vital.? As Craig said, your wouldn't 
want someone shutting down a breaker for a toaster circuit and killing the 
exterior signal, especially since there is no battery backup.? While it is true 
that the electrical issue is not directly the sprinkler contractors concern, if 
NFPA 13 requires an exterior waterflow signal, and the electrician does not 
connect it properly, most AHJs will not approve the final, and the customer 
will not have an approved sprinkler system.? I think it is in our best interest 
to follow through and make sure the system meets the code and passes the 
acceptance test.? It is not our function to fix the problem, only to identify 
the problem to the customer so he can address the electrical contractor 
properly.?(Besides, who does the customer yell at anyway?if he can't get his 
CO?? LOL)??


-----Original Message-----
From: [EMAIL PROTECTED]
To: [email protected]
Sent: Wed, 18 Jul 2007 10:02 am
Subject: RE: Alarm Circuit



Your alarm devices (water flow, tamper, water pressure, alarm bells)
should be 24vdc or whatever is required to match the fire alarm system.
Most are 24vdc, (power limited fire alarm (PLFA) circuits) and the power
to each device comes through the fire alarm panel.   You can find some
120vAC alarm bells and tamper & flow switches but I've only come across
them where the building wasn't equipped with a fire alarm system.  If
that's what you've got then they should be on a separate circuit of
their own.

The alarm panel connection to the building power grid is really not the
sprinkler contractors concern.  That's the responsibility of the
Electrical contractor so I wouldn't worry about it.  

There is considerable verbiage in NFPA 70, article 760 as well as other
places (national electrical code) concerning rules for wiring,
conductors and on and on and on for fire alarm systems.  That is
primarily where they get their direction from. 

The fire alarm system should be on a dedicated circuit as stated in NFPA
72, 4.4.1.4.1 as you found.   You wouldn't want someone pulling a
breaker to shut off a toaster and kill the fire alarm system too,
(although they do have battery backup but power interruption would
render a trouble or supervisory alarm).

   



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregory
Lindholm
Sent: Wednesday, July 18, 2007 9:31 AM
To: SprinklerFORUM
Subject: Alarm Circuit

We have always told the electricians on projects that the wiring for the
sprinkler alarms had to be on a dedicated circuit on the panel.

Is this right, and if so, where is it stated? 

I looked in the 2002 edition of NFPA #72, and the closest thing that I
found is 4.4.1.4.1, but not sure if that is correct.

Greg Lindholm
Metro Fire Protection, Inc.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


________________________________________________________________________
AOL now offers free email to everyone.  Find out more about what's free from 
AOL at AOL.com.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to